    Drawing 3-Phase Voltage Waveforms

    Homework Statement Draw and label the 3-phase voltage waveforms where VAN= 347∠0° Vrms, VAB= 600∠30° Vrms, Frequency: 50Hz, Volts/Division 200, Time/Division: 2 ms 2. The attempt at a solution Im really not sure how to tackle this one. My prof hardly went over this in lecture, but gave this...
  2. J

    Engineering 3 PHASE CIRCUIT PROBLEM - Haaalllppp

    http://1-media-cdn.foolz.us/ffuuka/board/wsg/image/1339/18/1339188551986.gif
  3. J

    Engineering 3 PHASE CIRCUIT PROBLEM - Haaalllppp

    Homework Statement Three load each having a resistance of 16 ohms and an inductive reactance of 12 ohms are wye connected to a 240V three phase supply. Determine: a) the impedance per phase b) the current per phase c) the kVA total d) the Power Factor e) the kW total Homework...
  4. J

    Engineering P= 1.732 X 230V X 42A X 0.85 = 10,731.06 W or 10.73 kW

    Yeah my prof likes to throw us off with his wording heh. Thanks again for your help. I have 3 more questions to go. Ill post them in this thread If I am stuck.
  5. J

    Engineering P= 1.732 X 230V X 42A X 0.85 = 10,731.06 W or 10.73 kW

    Ok, so "per terminal" refers to "Line-to-Line"? so Id go with these: kVA= 1.732 X 230V X 40A kVA= 16kVA P= 1.732 X 230V X 40A X 0.85 P= 13.5kW Also, the 15HP (11kW) stated in the original question. Would that be the motors rated power, while the 13.5kW calculated would be its input power?
  6. J

    Engineering P= 1.732 X 230V X 42A X 0.85 = 10,731.06 W or 10.73 kW

    A) Wye: kVA= 1.732 X 230V X 40A kVA= 16kVA Delta: kVA= 1.732 X 230V X 69A kVA= 27kVA B) Wye: P= 1.732 X 230V X 40A X 0.85 P= 13.5kW Delta: P= 1.732 X 230V X 69A X 0.85 P= 23.4kWHow do these look?
  7. J

    Engineering P= 1.732 X 230V X 42A X 0.85 = 10,731.06 W or 10.73 kW

    3 PHASE INDUCTION MOTOR A 15 hp/230V, three phase induction motor has a full load current of 42A per terminal. 15HP= 11kW find: a) Full load kVA input b) If the full load power factor is lagging 0.85, what is the kW input. My question: How do I know whether its connected Wye or Delta?a) kVA=...
  8. J

    Engineering How Do You Calculate Line Voltage and Current in Delta Connections?

    Ok, A) According to textbook: VLoad=VPhase=VLine (Delta) Therefore VLine in this case = 240V B) According to textbook: ILine=IPhase X 1.732 (Delta) IPhase=100A (Would you agree)? Therefore ILine= 173.2A c) kVA= kW/PF kVA= 43/0.6 kVA=...
  9. J

    Engineering How Do You Calculate Line Voltage and Current in Delta Connections?

    each phase of a three phase delta connected generator supplies a full load current of 100A The Windings? 100A per phase/winding
  10. J

    Engineering How Do You Calculate Line Voltage and Current in Delta Connections?

    No answers provided. You say for b), that the line current is 100A. Does this mean that the Load current=Line current for delta connections? Also for question a), If I am not mistaken, the phase voltage is calculated Vload/1.732 which comes out to 138.5V. So shouldn't VLine be 138.5V?
  11. J

    Engineering How Do You Calculate Line Voltage and Current in Delta Connections?

    ^ Yes. What I am unsure of is question c and d. I am not exactly sure which values to substitute into kVA= (1.732)(VL)(IL)/1000 and P= (1.732)(VL)(IL)(0.6). I used the line current and line voltage for both. Is this right? (assuming that the line current I calculated is correct to begin with.)
  12. J

    Engineering How Do You Calculate Line Voltage and Current in Delta Connections?

    Homework Statement each phase of a three phase delta connected generator supplies a full load current of 100A at a voltage of 240V and at a power factor of 0.6 lagging. Find: a) line voltage b) line current c) the kVA rating d) the KW 2. The attempt at a solution a) Line voltage = Phase...