Anyone Installed Startco Earth Detection SE 704 for a 4160V 3-Phase Motor?

  • Thread starter Thread starter dorymill
  • Start date Start date
  • Tags Tags
    Detection Earth
Click For Summary
SUMMARY

The discussion focuses on the installation of the Startco Earth Detection SE 704 system for a 4160V 3-phase, 1900 HP motor with a detection level of 100 mA. Participants address issues related to nuisance tripping during motor startup and inquire about the KVA code for the motor. Key considerations include verifying the starting current against the specifications of the Startco current transformers (CTs) and the implications of a Wye connection, particularly regarding third harmonic currents. Recommendations include examining the CT output with an oscilloscope to identify potential anomalies during startup.

PREREQUISITES
  • Understanding of Startco Earth Detection SE 704 system
  • Knowledge of 4160V 3-phase motor specifications
  • Familiarity with current transformers (CTs) and their applications
  • Basic principles of harmonic analysis in electrical systems
NEXT STEPS
  • Investigate the specifications and installation guidelines for Startco Earth Detection SE 704
  • Learn about the KVA code and its relevance to motor performance
  • Examine techniques for analyzing CT output using an oscilloscope
  • Research the effects of third harmonic currents in Wye-connected systems
USEFUL FOR

Electrical engineers, motor control specialists, and technicians involved in the installation and troubleshooting of high-voltage motor systems.

dorymill
Messages
1
Reaction score
0
Anyone ever install SE 704 Earth Detection (ground fault system)?
4160V 3 phase
1900 HP motor
detection level 100 Ma
resistance grounded supply max fault current 1 amp.

Nuisance tripping when starting the motor.
 
Engineering news on Phys.org
what's KVA code on motor?

is starting current within spec of that Startco gizmo's CTs?

Wye connection? remember third harmonic all returns through neutral...CT needs to wrap it too.
any idea of motor windings' capacitance to earth?

examine CT output with a scope during a start, if it's 180 hz you have an interesting situation.

just guesses

old jim
 

Similar threads

Replies
7
Views
3K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 38 ·
2
Replies
38
Views
8K
Replies
23
Views
7K
  • · Replies 16 ·
Replies
16
Views
4K
  • · Replies 26 ·
Replies
26
Views
4K
  • · Replies 4 ·
Replies
4
Views
17K
  • · Replies 1 ·
Replies
1
Views
7K
Replies
4
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K