The discussion centers on the operational duration of four 125 Ah deep cycle batteries powering a 6000 watt inverter with a 12 amp AC load. Given the inverter's no-load draw of 2 amps and an estimated efficiency of 80%, the batteries can sustain the load for approximately 90 minutes before reaching a 50% discharge level. Key recommendations include maintaining the inverter close to the batteries, using appropriate gauge cables, and ensuring batteries are of the same type and age to prevent premature aging. Regular recharging is emphasized to prolong battery life.

PREREQUISITES
  • Understanding of deep cycle battery specifications (e.g., 125 Ah capacity)
  • Knowledge of inverter efficiency calculations (e.g., 80% efficiency)
  • Familiarity with electrical load calculations (e.g., 12A * 120V = 1440W)
  • Basic principles of battery maintenance and charging practices
NEXT STEPS
  • Research "Inverter efficiency and load calculations" for better understanding of power requirements
  • Learn about "Battery maintenance techniques for lead acid batteries" to extend lifespan
  • Investigate "Proper cable sizing for inverter installations" to minimize voltage drop
  • Explore "Best practices for connecting batteries in parallel" to ensure balanced performance
USEFUL FOR

This discussion is beneficial for electrical engineers, renewable energy enthusiasts, and anyone involved in off-grid power systems who seeks to optimize battery performance and inverter efficiency.

ggpa
Messages
2
Reaction score
0
I have four 125 ah batteries powering a 6000 watt inverter. The inverter is supposed to have a no load draw of 2 amps. I have a 12 amp 120volt Ac load. How long should I be able to operate before drawing my batteries to 50%
 
Engineering news on Phys.org
By the way, the batteries are 12 volt deep cycle. They are connected in parallel
 
Using very rough numbers, about 2 kwh from those 4 batteries.

A better way to express it is to recharge whenever the loaded voltage drops below 12V, of 12.2V when rested and at no load.
 
ggpa said:
I have four 125 ah batteries powering a 6000 watt inverter. The inverter is supposed to have a no load draw of 2 amps. I have a 12 amp 120volt Ac load. How long should I be able to operate before drawing my batteries to 50%

The output of the inverter is..
12A * 120V = 1440W
If the inverter was 100% efficient then the input would also be 1440W but that's unlikely. Efficiencies of >80% are possible. Using 80% that gives an input power of

1440/0.8 = 1800W
At 12V that's a current of

1800/12 = 150A or 37.5A per battery.

You say they have a nominal capacity of 125AH but only want to use 50% so they can deliver that 37.5A for
125/(2*37.5) = 1.6 hours. Call it 90 mins.

Your mileage may vary! Check the actual efficiency of your inverter.

Put the inverter as close as possible to the batteries and use fat cables. At 80% efficiency the inverter dissipates 1800-1440 = 360W so allow for cooling air flow.

I used a lot of lead acid batteries in the 1980's amd 90's. I found the key to long life is never to leave them discharged for long, get them back on a charger as soon as possible, ideally within hours of use. I found if you regularly left one party discharged for a week they didn't last long, well under a year. Once I got into the habit of leaving them on a float charger all the time they started to live a lot longer.
 
Batteries connected in parallel should be of the same type and the same age or they will (very likely) 'age' prematurely. Charge and discharge currents will not be shared equally if you use different batteries and using four random batteries can be false economy even if you get them cheap. Your deep cycle choice was good. The only good thing about car start batteries is that they can give you hundreds of Amps when needed.
 
  • Like
Likes   Reactions: CWatters

Similar threads

Replies
6
Views
4K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
11
Views
2K
Replies
12
Views
3K
  • · Replies 14 ·
Replies
14
Views
3K
Replies
5
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 11 ·
Replies
11
Views
2K