Calculate humidity from dry/Wet bulb temp

  • Thread starter Thread starter dhkdeoen
  • Start date Start date
  • Tags Tags
    Bulb Humidity
Click For Summary
SUMMARY

The discussion centers on calculating specific humidity, relative humidity, and specific enthalpy using dry-bulb temperature (46°C), wet-bulb temperature (34°C), and atmospheric pressure (101.3 kPa). The formulas used include specific humidity (w = 0.622 * Pv / Pa), relative humidity (φ = w * P / [(0.622 + w) * Pg]), and specific enthalpy (h = ha + w * hg). Initial calculations yielded incorrect results, prompting a reevaluation that led to more accurate values of approximately 38% relative humidity and 129 kJ/kg specific enthalpy.

PREREQUISITES
  • Understanding of psychrometric principles and charts
  • Familiarity with thermodynamic properties of air
  • Knowledge of specific humidity and relative humidity calculations
  • Ability to interpret temperature and pressure data in SI units
NEXT STEPS
  • Study the use of psychrometric charts for accurate humidity calculations
  • Learn about the properties of air at various temperatures and pressures
  • Explore the implications of wet-bulb and dry-bulb temperature measurements
  • Investigate the relationship between specific enthalpy and humidity in HVAC applications
USEFUL FOR

Students in thermodynamics, HVAC engineers, meteorologists, and anyone involved in environmental control systems will benefit from this discussion.

dhkdeoen
Messages
11
Reaction score
0

Homework Statement


Dry-bulb Temperature 46'C
Wet-bulb Temperature 34'C
P=101.3kPa

with these, I have to 'calculate' Specific Humidity(w), Relative humidity(φ), Specific Enthalpy(h)

Homework Equations



Specific Humidity
w=0.622*Pv/Pa
when Pa=P-Pv

Relative Humidity
φ=w*P/[(0.622+w)*Pg]

Specific Enthalpy
h=ha+w*hg

for this problem, I used approximated values based on temperature for ha.
so
ha=1.005[kJ/KgC]*T[C]
ha[kJ/KG]

The Attempt at a Solution


P is 101.3
T is 46'C

from Table A-4, Pv is 10.14kPa at 46'C

w=(0.622*10.14)/(101.3-10.14)=0.069
6.9%

φ=0.069*101.3/[(0.622+0.069)*10.14)=0.9976
99.76%
this is when I start to feel a bit weirdh=1.005*46+0.069*2584.18
=224.54kJ/kgThen I checked my Psychrometric Chart, and found out this makes no sense. Where did I go wrong? or am I reading the the chart wrong?
 
Physics news on Phys.org
Since your wet bulb temp is close to freezing the curves on the psychrometric chart are at one end so it's a bit hard to get accurate readings, but I got
rel humidity ~ 33%
enthalpy ~ 12.5 BTU per lb. dry air. Sorry these units are not SI.
humidity mass ratio ~ .004 moisture/dry air.
Don't know about your equations but I can tell from their simplicity that they are rough approximations to the chart numbers.
 
rude man said:
Since your wet bulb temp is close to freezing the curves on the psychrometric chart are at one end so it's a bit hard to get accurate readings, but I got
rel humidity ~ 33%
enthalpy ~ 12.5 BTU per lb. dry air. Sorry these units are not SI.
humidity mass ratio ~ .004 moisture/dry air.
Don't know about your equations but I can tell from their simplicity that they are rough approximations to the chart numbers.
Wet bulb temperature is 34° C. That's not close to freezing. In fact, it's rather balmy. I think you got your temperature units mixed up.
 
dhkdeoen said:

Homework Statement


Dry-bulb Temperature 46'C
Wet-bulb Temperature 34'C
P=101.3kPa

with these, I have to 'calculate' Specific Humidity(w), Relative humidity(φ), Specific Enthalpy(h)

Homework Equations



Specific Humidity
w=0.622*Pv/Pa
when Pa=P-Pv

Relative Humidity
φ=w*P/[(0.622+w)*Pg]

Specific Enthalpy
h=ha+w*hg

for this problem, I used approximated values based on temperature for ha.
so
ha=1.005[kJ/KgC]*T[C]
ha[kJ/KG]

The Attempt at a Solution


P is 101.3
T is 46'C

from Table A-4, Pv is 10.14kPa at 46'C

w=(0.622*10.14)/(101.3-10.14)=0.069
6.9%

φ=0.069*101.3/[(0.622+0.069)*10.14)=0.9976
99.76%
this is when I start to feel a bit weirdh=1.005*46+0.069*2584.18
=224.54kJ/kgThen I checked my Psychrometric Chart, and found out this makes no sense. Where did I go wrong? or am I reading the the chart wrong?

It's not clear what Table A-4 is. Can you link to it?

Here is a psychrometric chart in SI Units:

http://www.uigi.com/UIGI_SI.PDF

Your dry bulb/wet bulb temps are almost off this chart.

I would say the enthalpy is about 122 kJ/kg of dry air and the relative humidity is about 45%
 
SteamKing said:
Wet bulb temperature is 34° C. That's not close to freezing. In fact, it's rather balmy. I think you got your temperature units mixed up.
Well you're absolutely right. I'll take another shot at it soon.
 
With the correct temperatures I got about 38% rel. humidity, 0.025 kg moisture /kg dry air, and H ~ 56 BTU//lb dry air = 129 kJ/kg. On my chart I had to estimate enthalpy a bit.
 

Similar threads

  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 6 ·
Replies
6
Views
5K
  • · Replies 10 ·