Calculating changes in Fan Power

  • Thread starter Thread starter StudYMA
  • Start date Start date
  • Tags Tags
    Fan Power
Click For Summary
SUMMARY

This discussion focuses on calculating changes in fan power due to airflow restrictions, specifically using fan affinity laws and differential pressure measurements. Brian, the original poster, seeks to understand how changes in pressure drop across components like filter banks affect fan speed and power in a variable speed fan system. Key equations discussed include the relationship between pressure drop and fan speed, as well as the power loss equation SP*CFM/(6356*%Eff)=HP. The consensus is that fan affinity laws provide a more accurate framework than Bernoulli's equation for this analysis.

PREREQUISITES
  • Understanding of fan affinity laws
  • Knowledge of differential pressure measurement using a magnehelic gauge
  • Familiarity with airflow concepts, specifically CFM (Cubic Feet per Minute)
  • Basic principles of fluid dynamics, particularly relating to pressure and power calculations
NEXT STEPS
  • Study the application of fan affinity laws in HVAC systems
  • Learn how to calculate CFM based on resistance changes in ductwork
  • Research the implications of static pressure loss on fan performance
  • Explore the conversion of power loss equations into SI units for broader applicability
USEFUL FOR

Mechanical engineers, HVAC professionals, and anyone involved in optimizing fan performance in air handling units (AHUs) will benefit from this discussion.

StudYMA
Messages
3
Reaction score
0
I have a question regarding the relationship between airflow restriction and fan power. If the pressure drop across an airflow restrictor (filter bank, heat exchanger coils, etc.) is known by measuring with a magnehelic differential pressure gage and that dP changes (filter replacement/removal, etc), how will that affect fan speed/fan power?

I am talking about a variable speed fan which aims to maintain a constant duct static pressure downstream of said obstructions, so I believe that the fan speed would decrease, but how do I calculate how much?

To find power reduction I initially used an extended bernoulli equation ignoring kinetic and potential energy factors which reduced to [(pressure reduction)*(mass flowrate)]/(air density), or (pressure reduction)*(CFM) but this is coming out lower than I expected.

I'm also aware than fan power varies with the cube of fan speed, so maybe I'm skipping an intermediate step?


Thanks in advance to anybody who can assist me!

-Brian
 
Engineering news on Phys.org
Use the fan affinity laws, not Bernoulli's equation. Have a look at them and let me know if you have trouble applying them to this situation - I do this exact problem several times a week.

Google them - I'm posting from a blackberry and can't give much help right now.
 
OK, I can see how fan affinity laws would be preferred. In fact, that's where I came up with fan power being proportional to the cube of fan speed. I see that head or pressure is proportional to the square of fan speed, so that will allow me to get from change in pressure to change in fan power.

The question I have is applying the change in pressure. I'm looking at a large hospital AHU whose duct static pressure setpoint is 2" wg. The final filter bank reads 0.7" wg drop across it. I am stuck here - the only next step I can see is using 2 and 1.3 for P1 and P2 and then calculating the change in fan speed, but that doesn't seem right...
 
The trick here is to split it into two problems. The basic affinity laws are good for changing one parameter at a time - but you are changing resistance and then fan speed to compensate. So calculate a new CFM due to the change in resistance, then the new rpm needed to get you back to the original CFM.

If you just want power loss due to the restriction, that's easier. The equation is just SP*CFM/(6356*%Eff)=HP
 
Also, supply static is just a control parameter. What matters is the typical operating CFM and the SP loss across the filter for energy loss or total static rise across the fan for total fan energy.
 
First off, thanks for your patience and assistance. I'm less than a year out of school working my first engineering job so applying the concepts learned in school is still a struggle. Much easier when a textbook tells you exactly the variables you need.

Here's what I found for fan affinity laws:

CFM 1 / CFM 2 = RPM 1 / RPM 2

Delta P 1 / Delta P 2 = [RPM 1 / RPM 2]^2

Power 1 / Power 2 = [RPM 1 / RPM 2]^3


Knowing anyone of the fractions will allow me to solve for any other. The equation that stands out to me is the second one since I'm dealing with a known pressure drop across a filter bank. However I believe this equation is relating pressure differential across a fan (or head across a pump) for two different settings, and then outputting the change in fan speed given those delta P's.

You say to calculate a new CFM based on resistance - what is this relationship? I was assuming that the CFM delivered by the fan would stay the same, it just would not have to work as hard to supply it.

Finally, the equation of power loss due to restriction SP*CFM/(6356*%Eff)=HP is essentially what I came up with so that is relieving. Would it also apply to removing airflow restrictors such as sound attenuators downstream of the fan in the ductwork? Also, is the 6356 just a coefficient to get power into units of HP based on inputting pressure in units of "h2o and flowrate in units of CFM?


Again, thanks so much
-Brian
 
How do you arrive to the equation SP*CFM/(6356*%Eff)=HP and how do we write this equation in SI units??
 

Similar threads

Replies
6
Views
5K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 22 ·
Replies
22
Views
4K
Replies
3
Views
2K
  • · Replies 12 ·
Replies
12
Views
5K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 3 ·
Replies
3
Views
7K
Replies
1
Views
2K
Replies
5
Views
3K
Replies
11
Views
3K