Calculating the reactive power of a transmission line

Click For Summary

Discussion Overview

The discussion revolves around calculating the reactive power of a transmission line connected to an infinite bus, focusing on the impact of line resistance on reactive power calculations. Participants explore different methods and equations used to derive reactive power values, as well as the implications of their results.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant calculated reactive power without line resistance, obtaining a value of 35.24 kVAR, and with resistance, a value of -114.77 kVAR, questioning the significant difference.
  • Another participant confirmed a similar result using Excel, suggesting that the reactive power should be 114.7 kVAR and described it as capacitive.
  • Questions were raised about the inclusion of resistance in calculations and its impact on reactive power values.
  • Concerns were expressed regarding the interpretation of the negative reactive power value, with one participant clarifying that it indicates the generator is underexcited and absorbing reactive power from the grid.
  • Participants discussed the equations used for calculations, with one suggesting that symbolic solutions might clarify the conditions affecting reactive power.
  • Another participant provided a specific calculation for line reactive power based on a given current, leading to a value of 68.77 kVAR.

Areas of Agreement / Disagreement

Participants express differing views on the nature of the reactive power (whether it is capacitive or inductive) and the implications of negative values. There is no consensus on the interpretation of results or the calculations involved.

Contextual Notes

Participants rely on specific assumptions about voltage magnitudes and line characteristics, which may not be universally applicable. The discussion includes unresolved questions about the effects of resistance on reactive power calculations.

anon6912
Messages
21
Reaction score
3
I have a single machine connected to an infinite bus with the following parameters:

- Sending end power = 3.75MW
- RL=5.18 ohms
- XL=130 ohms
- VS (Generator bus)=161kV
- VR (Infinite bus)=161kV
- Sending end voltage angle (delta) = 0.01877 (Angle which allows 3.75MW to be transferred)
Using these I want to calculate the amount of reactive power sent by the sending end as well.

I calculated it first without factoring in the line resistance (RL=0) Then got the result for Q as : **35.24kVAR**

Next I calculated it with the line resistance factored in Then got the result for Q as: **-114.77kVAR**

When the line resistance is factored in, the answers for reactive power vary immensely. And when the resistance is factored in, the sign of Q is negative indicating the generator bus is absorbing VARS which doesn't seem to make sense.

Why are they so different? What am I doing wrong?

The equations I used are here

I derived these equations using Matlab to do the algebra, so it hopefully should be correct :)
 
Engineering news on Phys.org
I did the calculation using Microsoft.Excel 2010 and the result is close to your.

If you require abs(VS)=abs(VR) the reactive power has to be 114.7 kVAr only.

In my opinion it is capacitive.

In order to preserve P=3.75 MW delta has to be 0.018831
 
Did you include the resistance in your calculation or no?
 
@anon6912 -- is this for schoolwork? If so, I can move your thread to the schoolwork forums.
 
berkeman said:
@anon6912 -- is this for schoolwork? If so, I can move your thread to the schoolwork forums.
Hey yeah, could you move it if you don't mind :)
Thanks
 
Of course, I did it. The formulas in complex are as following:

VS=COMPLEX(161*cos(delta),161*sin(delta))

VR=COMPLEX(161,0)

Z=COMPLEX(5.18,130)

IS=IMDIV(IMSUB(VS,VR),Z)

S=VS*IMCONJUGATE(IS)

P=IMREAL(S)

Q=IMAGINARY(S)
 
Babadag said:
Of course, I did it. The formulas in complex are as following:

VS=COMPLEX(161*cos(delta),161*sin(delta))

VR=COMPLEX(161,0)

Z=COMPLEX(5.18,130)

IS=IMDIV(IMSUB(VS,VR),Z)

S=VS*IMCONJUGATE(IS)

P=IMREAL(S)

Q=IMAGINARY(S)
Ok but I am still confused:

a. Its an inductive line how can it be capacitive? (is it capacitive because the terminal voltage magnitudes are the same?)
b. and how/why does the effect of the resistance have such a huge impact on the value of Q?
b.1 Does the incusion of the resistance make it "capacitive" in a sense somehow?
 
If you are looking at the equations, then the answers to your questions are implicit in the equations.

If you are taking the data from #1 and putting them into a computer, then I recommend that you write and solve the equations sybolicly on paper instead.

Once you have the expression for Q, ask "what conditions other than line reactance can make Q negative?"
 
  • Like
Likes   Reactions: jim hardy
My mistake! It is not good to say capacitive. Since it is referred to the generator delivered power if it is negative that means the generator is underexcitated and gets reactive power from the Grid[Infinite].
The transmission line reactive power it is :
If Is=23 A then line reactive power it is [X*IS^2]=130*23^2=68.77 kVAr.
upload_2017-6-22_17-22-53.png
 
  • Like
Likes   Reactions: jim mcnamara and jim hardy
  • #10
Babadag said:
My mistake! It is not good to say capacitive. Since it is referred to the generator delivered power if it is negative that means the generator is underexcitated and gets reactive power from the Grid[Infinite].
The transmission line reactive power it is :
If Is=23 A then line reactive power it is [X*IS^2]=130*23^2=68.77 kVAr.
View attachment 205900

Thanks a lot. That vector diagram makes makes sense :)
 

Similar threads

  • · Replies 15 ·
Replies
15
Views
2K
Replies
8
Views
3K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 10 ·
Replies
10
Views
5K
Replies
11
Views
3K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
15
Views
2K
  • · Replies 39 ·
2
Replies
39
Views
9K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
6K