Can Transfer Air Effectively Cool a Small Server Room?

  • Thread starter Thread starter Samj008
  • Start date Start date
  • Tags Tags
    Cooling Server
Click For Summary

Discussion Overview

The discussion centers on the effectiveness of using transfer air versus air conditioning to cool a small server room. Participants explore the thermodynamic principles involved, the necessary airflow rates, and the economic implications of each cooling method.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant argues that an air conditioner is the most economical and efficient way to cool the server room, given the heat output of 5,000 BTU/hr.
  • Another participant suggests that the first law of thermodynamics can be applied to determine the mass flow rates of air needed to maintain a steady state temperature.
  • There is a proposal to compare the costs of using a fan and air conditioning unit, including power consumption and maintenance costs.
  • One participant questions the outside temperature and suggests that moving outside air may be more economical and environmentally friendly than cooling air.
  • Another participant mentions that optimizing airflow around the servers, such as avoiding direct airflow into walls, could improve cooling efficiency.
  • A later reply indicates that using transfer air could be cheaper if the temperature difference is not too low, providing a calculation for required airflow based on temperature limits.
  • However, it is noted that network closets typically require cooler air than occupied spaces, which may limit the feasibility of using transfer air.

Areas of Agreement / Disagreement

Participants express differing views on the best cooling method, with some advocating for air conditioning and others for transfer air. The discussion remains unresolved, with multiple competing perspectives on the effectiveness and efficiency of each approach.

Contextual Notes

Participants mention the need for specific calculations regarding airflow rates and costs, but do not provide definitive solutions or consensus on the best approach. The discussion is influenced by assumptions about outside temperatures and the layout of the server room.

Samj008
Messages
2
Reaction score
0
Hi there,

I need to prove to an architect that the most economical and efficient way to cool our server room will be with an Airconditioner.

At present we have a system which is supposed to recycle the warm air downstairs suring winter and Outside during summer, only it doesn't draw nearly enough air to keep the server room cool.

The room is 1.1M x 1.8M x 2.5M and the machinery inside is producing roughly 5,000 BTU P/hr. The room temperature at the moment is getting up to 30 plus degrees C on mild days with the door wide open (I Dare not close the door to test)

The architecht wants to drill a whole in the floor and allow the marginally cooler air in from below, possibly putting another fan in the floor to provide more flow.

My argument is that the amount of flow required to cool that room to what is necissary using fans and electricity is going to outway any supposed environmental benifit from not using Air Conditioning, however I need to prove that.

Is there a calculation for the amount of air needed to cool a room that size where that much heat is being produced??

Cheers for your help in advance.
Sam
 
Engineering news on Phys.org
It's a simple first law of thermodynamics problem. You basically have an open system where 5,000 BTU/hr of heat is being added and needs to be removed my a mass flow of air in order to reach a steady state temperature.

The first step is to determine the mass flow rates of air required to remove the heat from the server from both the hole in the floor and the air conditioner. The mass flow rate of the air from the AC will obviously be less than that coming from the hole in floor because its probably going to be at a lower temperature (peak efficiency).

Then its basically just comparing the electrical and capital costs of the fan and AC unit to see which one is cheaper. For this you will need to find the power consumption of the fan and the AC unit and probably include maintenance costs as well.

BTW, AC units are expensive and suck up a lot of juice, so don't be surprised if a hole in the floor with a fan is considerably cheaper.
 
Whats the outside temperature where you are?
It's a lot cheaper (economically and environmentally) to just move a lot of outside air than to cool it.
Then take a look at the layout of your systems and the airflow.
Do you have racks full of servers with fans blowing out of the back straight into a wall?
Adding ducting and fans to get the best airflow around the machines is better than just overcooling everything.
 
It is almost always cheaper to use transfer air than to cool air, if the required delta-T isn't too low. What you need to do is use the temperature requirements of the equipment to dictate the answer to the problem. If, for example, the air downstairs is at 75F and your maximum allowable temperature is 78F, then you need 5000/1.1/(78-75)= 1500 CFM.

That said, it is typical for network closets to require the air be cooler than occupied spaces, so using transfer air would be out of the question in that case.
 

Similar threads

  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 12 ·
Replies
12
Views
1K
  • · Replies 8 ·
Replies
8
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 3 ·
Replies
3
Views
5K
  • · Replies 6 ·
Replies
6
Views
9K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K