hi everyone...i want to know tht how we determine the amount of porcelain insulation to be done in any electrical systems situated in a substation? please help
The discussion revolves around determining the appropriate amount of porcelain insulation for electrical systems in substations, with a focus on issues related to creepage and insulation effectiveness in high voltage applications.
Participants express multiple competing views regarding the mechanisms of creepage and its implications for insulation design. The discussion remains unresolved with no consensus on certain technical aspects.
Participants mention various factors that can influence creepage, such as humidity and surface contaminants, but do not reach a definitive conclusion on the best practices for insulation design in substations.
Ron_04 said:thank u very much for ur explanation...but i want to knw one thing tht is like in bushing of a transformer we do insulation to protect the transformer from surface current so why again creepage current...can u xplain me the creepage current please
Ron_04 said:ok thanks for the xplanation...but one more foolish question is how can creepage current flow through insulation? i mean to say how can a insulator conduct a current?
I believe is the stuffs deposit on the surface that break down and conduct.
jim hardy said:OP asked about electric utility insulators?
That was my understanding, so it is likely to be 60Hz
Yungman is exactly right.
The individual ceramic discs are mushroom shaped so that rain runs over top to edge and drips off leaving underside dry so it retains insulating capability.
Near the ocean or on a foggy morning inland you can hear high voltage insulators "sizzle" as the deposits absorb moisture and become conductive. A good rain will wash them clean.
search on 'insulator wash system'
there's some brave folks who wash them while energized..
I can assure you I am not one of the brave one!
http://www.wilorton.com/HotLineIns.htm