Determine the amount of porcelain insulation

  • Thread starter Thread starter Ron_04
  • Start date Start date
  • Tags Tags
    Insulation
Click For Summary

Discussion Overview

The discussion revolves around determining the appropriate amount of porcelain insulation for electrical systems in substations, with a focus on issues related to creepage and insulation effectiveness in high voltage applications.

Discussion Character

  • Technical explanation
  • Debate/contested

Main Points Raised

  • Some participants emphasize the importance of creepage over dielectric strength in insulation design, noting that creepage is the current that travels across the surface of an insulator.
  • One participant mentions that the dielectric strength of good insulators is around 400V/mil, suggesting a conservative design of 150V/mil.
  • There is a question about the relationship between insulation in transformer bushings and creepage current, with some participants suggesting that surface conditions like dirt and moisture can promote creepage.
  • Another participant distinguishes between creepage and eddy currents, asserting that creepage occurs on the surface due to potential differences and is influenced by environmental factors.
  • Concerns are raised about how creepage current can flow, with clarifications that it does not penetrate the insulation but travels along its surface, often affected by contaminants.
  • Participants discuss the design of high voltage insulators, noting features like mushroom shapes that help prevent moisture accumulation and maintain insulation capability.
  • Real-life experiences are shared regarding the maintenance of insulators, including the effects of environmental conditions on their performance.

Areas of Agreement / Disagreement

Participants express multiple competing views regarding the mechanisms of creepage and its implications for insulation design. The discussion remains unresolved with no consensus on certain technical aspects.

Contextual Notes

Participants mention various factors that can influence creepage, such as humidity and surface contaminants, but do not reach a definitive conclusion on the best practices for insulation design in substations.

Ron_04
Messages
14
Reaction score
0
hi everyone...i want to know tht how we determine the amount of porcelain insulation to be done in any electrical systems situated in a substation? please help
 
Engineering news on Phys.org


For power line that is 60Hz, the important thing to worry is not the insulation strength first. Most problem is creepage. Creepage is the current conduct across the surface of an insulator. That's the reason you see the HV standoff on the power lines is not straight, they are shape such the diameter get bigger and then smaller and bigger and smaller along the length. This is to increase the length of the path from the HV point at the top to the anchor point at the base.

Back to your original question, dielectric strength of most good insulator is about 400V/mil give and take. If you design with 150V/mil, usually it is ok already. You want to be more conservative, lower the number. This is a very general statement, you need to look up the specific material you are using.

As I said before, unless you push the insulation thickness, most problem is the creepage. It is only when the frequency goes up, then the material make a big difference. That's where the whole topics of dielectric loss and loss tangent and all come in.
 
Last edited:


thank u very much for ur explanation...but i want to knw one thing tht is like in bushing of a transformer we do insulation to protect the transformer from surface current so why again creepage current...can u xplain me the creepage current please
 


Ron_04 said:
thank u very much for ur explanation...but i want to knw one thing tht is like in bushing of a transformer we do insulation to protect the transformer from surface current so why again creepage current...can u xplain me the creepage current please

I don't think that's creepage, sound more like eddy current. Creepage is conduction on the surface due to potential difference. Dirt, moisture on the surface promote creepage. The distance depends on humidity and other factors. I don't remember the ball part distance. But it is a lot larger than insulation thickness.

I remember when I designed for CE requirement, say if I have a HV wire connect to one point. I need to prevent any human from touching even the insulation of the HV cable 3" from the exposed junction. From my experience, arcing in HV system was mostly from creepage. We trouble shoot where the arc was by turning off all lights and induced arcing. You can actually the lighting shoot across the surface.
 


ok thanks for the xplanation...but one more foolish question is how can creepage current flow through insulation? i mean to say how can a insulator conduct a current?
 


Ron_04 said:
ok thanks for the xplanation...but one more foolish question is how can creepage current flow through insulation? i mean to say how can a insulator conduct a current?

Creepage don't go through insulation. It only travel on surface of the insulator. When I design HV pcb, I lot of time, I route groove to create a longer path of creepage on the FR4.

I really have not look into the detail theory of creepage, I just know by real life experience. I believe is the stuffs deposit on the surface that break down and conduct. For example, solder flux residue, finger print oil, moisture in air all degrade the performance. I believe people use Teflon material not because of the insulation strength, it is still about 400V/mil. It's the surface of Teflon, things don't stick on the teflon so it's better to handle the creepage.
 


I believe is the stuffs deposit on the surface that break down and conduct.



OP asked about electric utility insulators?

Yungman is exactly right.
The individual ceramic discs are mushroom shaped so that rain runs over top to edge and drips off leaving underside dry so it retains insulating capability.

Near the ocean or on a foggy morning inland you can hear high voltage insulators "sizzle" as the deposits absorb moisture and become conductive. A good rain will wash them clean.

search on 'insulator wash system'

there's some brave folks who wash them while energized..
http://www.wilorton.com/HotLineIns.htm
 
Last edited by a moderator:


jim hardy said:
OP asked about electric utility insulators?
That was my understanding, so it is likely to be 60Hz

Yungman is exactly right.
The individual ceramic discs are mushroom shaped so that rain runs over top to edge and drips off leaving underside dry so it retains insulating capability.

Near the ocean or on a foggy morning inland you can hear high voltage insulators "sizzle" as the deposits absorb moisture and become conductive. A good rain will wash them clean.

search on 'insulator wash system'

there's some brave folks who wash them while energized..

I can assure you I am not one of the brave one!:smile:
http://www.wilorton.com/HotLineIns.htm

I never look at an power line insulator close up, I hope they have smooth shinny surface so it is less susceptible to things sticking onto the surface.
 
Last edited by a moderator:


got it...thnx
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
8K
  • · Replies 1 ·
Replies
1
Views
1K
Replies
10
Views
3K
  • · Replies 19 ·
Replies
19
Views
4K
Replies
15
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 12 ·
Replies
12
Views
3K
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
1K
  • · Replies 10 ·
Replies
10
Views
4K