Do Cable Trays in Sydney Car Parks Require Individual Earthing?

Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
3 replies · 3K views
Futsal1st
Messages
14
Reaction score
0
I am looking at a building with a car park in Sydney. Electrical circuits are run on perforated cable trays at high level.

I understand that the trays require earthing, however, I'm trying to determine the extent.

The trays are made from galvanized sheet and come in 3 meter lengths and are butted to each other. Two short straps (around 100mm long), one on each side, are used to join the lengths together. 10mm bolts and nuts are used for the connection.

Should the trays be individually earthed or only one at each run end or some thing in between? I have been told by one contractor that one Earth per tray is adequate. I've been told by an electrical engineer that each 3m length of tray should be individually earthed.

Advice please ..

Thaks
 
Engineering news on Phys.org
In my opinion, Australia use IEC standards for electrical installations.
IEC 61537 Annex C Protective Earth [PE] function.
But -as far as I know- no Annex C is detailed still. It is "under consideration".

In U.S.A. NEMA VE 2-2013
3.8.1 Cable Tray Used as an Equipment Ground Conductor (EGC)
3.9 BONDING TO THE METAL FRAME OF THE BUILDING AND EARTH

Metallic cable trays are permitted to be bonded to the metal frame of the building and Earth for signal grounding (“noise” prevention). This may be desirable if the cable tray system is not inherently bonded (connected) to the metal frame of the building and Earth through metallic support systems.

NEMA VE-2 2001 Edition recommended all 60 feet .From 2006 there is not any recommendation of the bonding interval.

The grounding bonding methods are stated in NEC[2017] Art.250.8
250.8 Connection of Grounding and Bonding Equipment. (A) Permitted Methods.
 