Earth as return path for power transmission line?

In summary, power companies use the Earth as one of the wires in a power system. The Earth is a good conductor and it is huge, so it makes a good return path for electrons. "Ground" in the power distribution grid is literally "the ground" that's all around you when you are walking outside.
  • #1
damosuz
72
0
This is from How Stuff Works:

The power company essentially uses the Earth as one of the wires in the power system. The Earth is a pretty good conductor and it is huge, so it makes a good return path for electrons. "Ground" in the power distribution grid is literally "the ground" that's all around you when you are walking outside. It is the dirt, rocks, groundwater, etc., of the earth.


Is this true? If yes, can you do something similar with a DC circuit (connect - of source to the earth, connect + of source to a resistor and then connect the other side of the resistor to the earth)? It seems that no current would flow, since the resistance of the Earth is extremely large...
 
Physics news on Phys.org
  • #2
damosuz said:
This is from How Stuff Works:

The power company essentially uses the Earth as one of the wires in the power system. The Earth is a pretty good conductor and it is huge, so it makes a good return path for electrons. "Ground" in the power distribution grid is literally "the ground" that's all around you when you are walking outside. It is the dirt, rocks, groundwater, etc., of the earth.


Is this true? If yes, can you do something similar with a DC circuit (connect - of source to the earth, connect + of source to a resistor and then connect the other side of the resistor to the earth)? It seems that no current would flow, since the resistance of the Earth is extremely large...

A "pretty good conductor" does not have an "extremely large resistance".

But yes, it is true.

And you can do it with DC circuits.

I've heard (but have never seen nor tried) that you can make worms come out of their holes by electrifying the ground in this way.

For fishing of course.
 
  • #3
OmCheeto said:
A "pretty good conductor" does not have an "extremely large resistance".

Actually yes it does if it is 1000 km long...
 
  • #4
You can (and do) use the Earth itself as a "ground". But because of the very large resistance of the Earth compared to copper wire, it would be pointless to try and make a circuit using the Earth as a return.
 
  • #5
NEC standard is no more than 25 ohms resistance to ground. I realize this isn't the same as "resistance through the earth", which changes depending on moisture and mineral content along the path, but it at least gives you a starting point.

Like OmCheeto said, yes, you can do it with DC -- in fact they actually DO. Look up "High Voltage DC single wire Earth return". They key in both AC and DC "SWER" systems is the high voltage, which minimizes your losses to resistance.
 
  • #6
Having very poor conductivity, the Earth is BY NO MEANS an ideal circuit link.
It's just convenient and can handle large amperages.
 
  • #7
OmCheeto said:
A "pretty good conductor" does not have an "extremely large resistance".

But yes, it is true.

And you can do it with DC circuits.

I've heard (but have never seen nor tried) that you can make worms come out of their holes by electrifying the ground in this way.

For fishing of course.

Just this summer while cleaning out my father-in-laws garage I found his worm spike, it consisted of a 2ft long hollow wooden rod with a 120v AC cord running through it. One wire of the cord was connected to a 6in long spike. My wife recalls him plugging this into a wall socket then driving the spike into the ground, the worms would crawl out of their holes waiting to be picked up, yes, for fishing. Not sure how big of an area it would effect.

The device gave me the creeps, it just looked dangerous! I disassmebled it and trashed the pieces.
 
  • #8
An electrician friend told me that when electricity was first used in the U.K.the Earth was used as one of the wires.You had a possitive as one and the ground as another.
It soon became obviouse that there was a problem with this system as many users were being killed by electrocution.
So an extra wire was introduced to try to prevent this.
Never done any research on this but it does sound plausable.
 
Last edited:
  • #9
damosuz said:
This is from How Stuff Works:

The power company essentially uses the Earth as one of the wires in the power system.

No, they don´t. In a three phase system there is no return wire. And if they have 3+N (230/400V household systems in European countries) N is an extra wire.
http://en.wikipedia.org/wiki/3-phase_AC
Railways use the rails as return wire, but that´s iron.
 
  • #10
maimonides said:
No, they don´t. In a three phase system there is no return wire. And if they have 3+N (230/400V household systems in European countries) N is an extra wire.
http://en.wikipedia.org/wiki/3-phase_AC
Railways use the rails as return wire, but that´s iron.

Ummm... Yes they do, in the case of Single Wire Earth Return transmissions systems, which was the topic of this thread.
 
  • #12
damosuz said:
The power company essentially uses the Earth as one of the wires in the power system. The Earth is a pretty good conductor and it is huge, so it makes a good return path for electrons. "Ground" in the power distribution grid is literally "the ground" that's all around you when you are walking outside. It is the dirt, rocks, groundwater, etc., of the earth.
This is a little deceptive IMO. "The power company" does not do this. It is certainly possible to do as other posters have pointed out, but this would be hugely expensive in terms of loss of power, and a power company that did this would be out of business very soon. The return path for electrons in a typical three-phase power distribution grid is the other lines. The dirt only carries current in the event of some failure or load imbalance, and often not even then since there is usually another wire for that purpose.
 
  • #13
One-wire power transmission lines have been used extensively in a number of countries. I do not know how many are using them currently.

http://tdworld.com/mag/power_one_wire_enough/"

Early telegraph and telephone systems used one-wire systems with ground as the return.
 
Last edited by a moderator:
  • #14
maimonides said:
Sorry. There seem to be no SWERs around where I live, and I must admit I´d not realized the developments in monopolar HVDC transmission.
http://en.wikipedia.org/wiki/Single_wire_earth_return

One of my email communicants, an EE professor, related a communication he had with the Bonneville Power engineers. When Bonneville does maintenance on their +500,000 V and -500,000 V DC lines from Bonneville, OR to Los Angeles, they shut down the line they intend to do maintenance on and use Earth ground as the return for the one in service. The Bonneville engineers stated they have less resistance using the ground return than when they have used the second line (without the opposite DC potential) as the return.

All the mechanism(s) the contribute to Earth conductivity are not fully understood. With a little depth, the increased pressure and temperature change the rules.
 
  • #15
alphawolf50 said:
maimonides said:
damosuz; said:
This is from How Stuff Works: The power company essentially uses the Earth as one of the wires in the power system.
No, they don´t. In a three phase system there is no return wire. And if they have 3+N (230/400V household systems in European countries) N is an extra wire.
http://en.wikipedia.org/wiki/3-phase_AC
Railways use the rails as return wire, but that´s iron.
Ummm... Yes they do, in the case of Single Wire Earth Return transmissions systems, which was the topic of this thread.

Form what I remember there is no return in 3phase system only becouse at the both end of the line the Y star center is at the same potential 0 and is grounded, but only if the loading of the line is symmetric which is not always true. If you don't have a symmetric loading of the 3 phase, there is a return current through the neutral point. More than this, when you have a short circuit to ground of 1 phase or between 2 phases, the current path is through the earth.
 
  • #16
pallidin said:
Having very poor conductivity, the Earth is BY NO MEANS an ideal circuit link.
It's just convenient and can handle large amperages.

It has poor conductivity but there is so much of it, so does it have poor conductance?
 

Related to Earth as return path for power transmission line?

1. How does Earth serve as a return path for power transmission lines?

Earth acts as a return path for power transmission lines by providing a low resistance path for the flow of electricity. This is achieved through the use of grounding rods and conductive materials, such as copper, buried in the ground.

2. What is the purpose of using Earth as a return path for power transmission lines?

The primary purpose of using Earth as a return path for power transmission lines is to ensure the safety of individuals and equipment. By providing a low resistance path, Earth helps to prevent the buildup of excess voltage and reduces the risk of electrical shocks.

3. Are there any potential hazards associated with using Earth as a return path for power transmission lines?

While Earth can help to mitigate potential hazards by providing a return path for electricity, there are still some risks involved. Improper grounding or damage to grounding systems can result in high voltage levels and potential electrical hazards.

4. How is the effectiveness of Earth as a return path for power transmission lines measured?

The effectiveness of Earth as a return path for power transmission lines is measured by the resistance of the grounding system. A lower resistance indicates a more effective return path and better protection against electrical hazards.

5. Can Earth serve as a return path for all types of power transmission lines?

Yes, Earth can serve as a return path for all types of power transmission lines, including high voltage and direct current lines. However, the specific design and installation of the grounding system may vary depending on the type of power transmission line.

Similar threads

  • Electrical Engineering
Replies
2
Views
179
Replies
18
Views
2K
  • Electrical Engineering
Replies
2
Views
1K
Replies
6
Views
2K
  • Electrical Engineering
Replies
32
Views
2K
Replies
13
Views
4K
  • Electrical Engineering
Replies
5
Views
2K
  • Classical Physics
Replies
2
Views
693
  • Electrical Engineering
Replies
4
Views
1K
Back
Top