Earthing Transformer: Wye vs Zigzag Connection

Click For Summary

Discussion Overview

The discussion revolves around the use of wye versus zigzag connections in earthing transformers, particularly in medium voltage applications. Participants explore the implications of each connection type, including cost, safety, and operational considerations.

Discussion Character

  • Debate/contested
  • Technical explanation

Main Points Raised

  • One participant expresses concern that using a direct wye connection may require sufficient reactance for exciting voltage, which could increase construction costs and pose safety risks in case of shorts.
  • Another participant indicates confusion regarding the initial post and questions the clarity of the argument presented.
  • A different participant notes that zigzag transformers are commonly used for earthing globally and suggests that the choice between zigzag and wye connections may depend on cost considerations, especially when multiple star-connected transformers are involved.
  • This participant also points out that if all incomers on a bus are star connected and can be earthed at the star-point, a separate earthing transformer may not be necessary.
  • It is mentioned that earthing transformers can be configured in various ways, including zigzag and star-delta configurations, with the latter allowing for different uses of the delta connection.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the superiority of wye versus zigzag connections, with multiple competing views and considerations remaining unresolved.

Contextual Notes

Participants express varying levels of understanding regarding the technical details of transformer configurations, and there are indications of missing assumptions about the operational contexts in which these configurations are applied.

jacquisdelumen
Messages
1
Reaction score
0
:rolleyes: I'm curious if we use a direct wye connection instead of zigzag in case of earthing transformer.. i know that by merely looking if we use wye connection in earthing specially in medium voltage you have to have enough reactance for your exciting voltage.which will cost more in construction.also should there be shorts you directly ground the system which is very dangerous.does my opinion correct? any opinion might help..thanks
 
Engineering news on Phys.org
I am thoroughly confused by the above.
 
jacquisdelumen said:
:rolleyes: I'm curious if we use a direct wye connection instead of zigzag in case of earthing transformer.. i know that by merely looking if we use wye connection in earthing specially in medium voltage you have to have enough reactance for your exciting voltage.which will cost more in construction.also should there be shorts you directly ground the system which is very dangerous.does my opinion correct? any opinion might help..thanks

If you are describing a three phase transformer, we in the USA usually refer to them as a WYE or Delta configuration. I’m not familiar with “zigzag”. Your post is hard to understand.
 
Folks,

Zigzag transformers are used all over the world for earthing (grounding) and unearthed bus, and in voltage ranges from LV to MV. I think the original question is along the lines "why would you bother earthing a bus with a separate zigzag when star-points (wye-point) are available?" I think it mainly comes down to cost - if there is a need to Earth a bus via several separate star-connected transformers, each with associated neutral bushing and full voltage insulation at the netra end, the lower cost with a single zigzag transformer comes into consideration. I have seen them on a set of 33 kV busses where one of the incomers was delta, so there was a possibility of an ungrounded bus if that incomer was in service with all other star-connected feeders and incomers out of service - a dedicated earthing transformer then makes sense and zigzag construction is a very cost-effective way of achieving that. If all incomers on a bus were star connected and are able to be earthed at tehe star-point, then there is no need for a separate earthing transformer.

Earthing transformers do not have to be zigzag - it is just one method - they can also be a more normal star delta with the star-point earthed and the delta either used for aux power or not used.
 

Similar threads

Replies
9
Views
3K
  • · Replies 1 ·
Replies
1
Views
4K
Replies
4
Views
4K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 17 ·
Replies
17
Views
6K
  • · Replies 6 ·
Replies
6
Views
4K
Replies
4
Views
4K