Exit flow rate in a Plate Heat Exchanger

Click For Summary
SUMMARY

The discussion focuses on calculating the volume flow rate and velocity of water at the outlet of a plate heat exchanger in a cascade system. The system involves a boiler supplying hot water at 65°C, which exits the first heat exchanger at 50°C, and is then used to heat another fluid from 10°C to 45°C. The volume flow rate is established at 5.0 m³/hr, and despite concerns about pressure loss (0.1 bar) affecting velocity, it is confirmed that there will be no significant change in mass flow rate or velocity at the outlet.

PREREQUISITES
  • Understanding of heat exchanger principles
  • Knowledge of fluid dynamics and flow rates
  • Familiarity with energy equilibrium calculations
  • Basic thermodynamics, specifically heat transfer equations
NEXT STEPS
  • Study the principles of plate heat exchangers and their applications
  • Learn about calculating pressure drops in heat exchangers
  • Research the impact of temperature differentials on heat transfer rates
  • Explore pump selection criteria for heat exchanger systems
USEFUL FOR

Engineers and technicians involved in thermal system design, HVAC professionals, and anyone working with heat exchangers in industrial applications.

harishree90
Messages
3
Reaction score
0
TL;DR
Calculation of Exit Mass flow rate in a Plate Heat Exchanger to design a Cascade Heating Network
Hello All,

I am working on a project with plate heat exchangers connected in a cascade system to heat up water connections in a huge system

The Problem Statement :

A boiler produces and circulates hot water at 65 degC to a Heat Exchanger and come out at 50 degC, where as the other fluid is also water which needs to be heated to 60 degC from 45 degC , The volume flow rate of hot water is at 5.0 m3/hr and the dia meter of the pipe is DN50

Using energy Equilibrium , Heat transfer rate in the first heat exchanger

Q = m X Cp X ΔT which come around 85KW
HX.jpg

now from the outlet of the Heat Exchange in the hot Side which is at 50 degC, I am connecting it as an Input to another heat Exchanger, which is also used to heat water from 10 degC to 45 degC and the hot water connected back to the Boiler which is at 15 degC

My question is, how can I calcuate the volume flow rate or mass flow rate or velocity of water at the outlet in the first heat exchanger which acts as an Input to second HX, so that I can calculate the heat transfer rate of the second HX to determine if need to have a pump in the circuit.

Thanks in Advance
If my question is not clear please let me know
 
Engineering news on Phys.org
Hello harishree, :welcome:

Your question is indeed unclear to me: if the volume flow is not 5 m3/h, where would the difference go ?

And the 5 m3/h, where does that come from, if not from a pump ?

Or:
With 'outlet' you mean the 60 C outlet ? Your heat exchange rate of 87 kW more or less dictates 5 m3/h too (with the given ##\Delta##T)
 
  • Like
Likes   Reactions: harishree90
BvU said:
Hello harishree, :welcome:

Your question is indeed unclear to me: if the volume flow is not 5 m3/h, where would the difference go ?

And the 5 m3/h, where does that come from, if not from a pump ?

Or:
With 'outlet' you mean the 60 C outlet ? Your heat exchange rate of 87 kW more or less dictates 5 m3/h too (with the given ##\Delta##T)

Thank you for the reply

The 5 m3/h volume flow at the inlet of the heat exchanger comes from a hot water boiler.

And by Outlet I mean the output with 50 C which acts as a input to the second heat exchanger.

My question is ...due to pressure loss in the heat exchanger (Considering 0,1 bar), will there be a change in velocity of the fluid at the exit (at 50 C) ?
 
harishree90 said:
Thank you for the reply

The 5 m3/h volume flow at the inlet of the heat exchanger comes from a hot water boiler.

And by Outlet I mean the output with 50 C which acts as a input to the second heat exchanger.

My question is ...due to pressure loss in the heat exchanger (Considering 0,1 bar), will there be a change in velocity of the fluid at the exit (at 50 C) ?
No significant change. And, of course, the mass flow rate won't change at all.
 
  • Like
Likes   Reactions: harishree90
Chestermiller said:
No significant change. And, of course, the mass flow rate won't change at all.

Thank you for the explanation Chestermiller and BvU

I was under the wrong idea that since there will be a pressure loss in the heat exchanger, it would affect the velocity and the flow rate also.
Now I understand
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
22
Views
4K
Replies
1
Views
1K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 6 ·
Replies
6
Views
14K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
7
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K