News Florida Collapsed Condominium had been sinking since 1990s

  • Thread starter Thread starter Astronuc
  • Start date Start date
Click For Summary
The discussion centers on the potential for negligent homicide related to the collapse of a Florida condo, which had been identified as unstable in a 2020 study. Concerns are raised about why residents were not warned or why the building was not condemned despite ongoing recertification reviews. The conversation highlights the responsibility of both the building's management and the residents in maintaining safety, noting that signs of subsidence and structural issues were likely observable. Experts suggest that the building's condition was a long-term issue, raising questions about the adequacy of inspections and the actions taken by those responsible. The implications of this tragedy extend to legal accountability and the financial burdens on condo owners for necessary safety measures.
  • #31
I am looking at the paper of Fiaschi and Wdowinski. To be honest, I can't tell if the point in question is Champlain Towers South or immediately north.
  • Figure 3 is low resolution and blowing it up 800% proved unhelpful.
  • The data points obscure the geography
  • The most obvious landmark, the building to the immediate south, wasn't built until 2018, so it's harder to align the data and a map than I first thought.
 
Physics news on Phys.org
  • #32
I reread the paper in the clear light of day. The authors identify the point in question as a 12-story condominium, which suggests it is the collapsed building. However, immediately north is Champlain Towers East Condo. Figure 3 shows it northeast of a park, which suggests East, but the park seems not to be shaped as it is today, which opens the question up again.

I think the paper isn't really intended to pick out a single building.

Was this paper a warning? Not explicitly. It's more about flooding, and is more focused on the opposite end of the island, where historical flooding has happened. Larger subsidences are observed elsewhere on Miami Beach and much larger ones still near Norfolk.

I don't even think it's actionable. "Excuse me ma'am, but you have to evacuate right now, because we were just made aware of a re-analysis of 20-25 year old data that shows that this building has a subsidence rate of 5 microns per day, which causes it to rank #4 out of all spots on this island, and is almost one-third the rate of parts of Norfolk. No ma'am, no problems seen at Norfolk. No ma'am, we don't think you'll ever be able to return home - can't` be too careful."

Three other points I'd like to make. One is that there is actually no problem if the building sinks 8 cm (which seems to me kind of hard to miss, but...). The problem is if the building sinks non-uniformly: 8 cm here, but only 1 cm there. It shifts the loads, and worse, forces that were purely horizontal develop vertical components and vice versa. The 2mm/year number tells only a part of the story and not a very big part at that.

The second is that the swimming pool sits over a parking garage, and is not terribly close to the building.

Finally, concrete is about the most complex inorganic building material there is (and reinforced concrete just makes it worse). People use supercomputers to try and model its properties. It's also not as chemically inert as you might think. Even if inferior concrete was poured 40 years ago, it might be hard to prove that today.

Nothing has changed my viewpoint: I don't think we know if
  • The standards were followed but inadequate
  • The standards were adequate but not followed
and are unlikely to know on the timescale of days or weeks.
 
  • Like
Likes Twigg
  • #33
Salty winds and water aren't rebars' friends. It could have been simple rust.

Repairing concrete is not only expensive, it is also rather dirty, takes months and most of all it is very, very loud. I don't know whether these points were an issue at the owners' regular meetings, but I do know people.
 
  • Like
Likes mathwonk and Lnewqban
  • #34
A building next to my office has a metal post sunk into a concrete slab. After only a decade, the concrete looks like a chromatography experiment - browns, and yellows and greens...

I'm not sure if rust is simple. The concrete shouldn't be under tension, which is where the rust might cause the rebar to yield. However, in combination with other factors, such as forces in an unanticipated direction, absolutely.
 
  • #35
The report described failed waterproofing that caused "major structural damage" to the concrete below the pool deck and entrance drive, as well as "abundant cracking" in the concrete columns, beams, and walls of the parking garage.

It's unclear if any of those issues flagged in the 2018 report contributed to Thursday's collapse. Officials told reporters in a press conference Saturday that the cause of the collapse will be investigated after the search-and-rescue efforts finish.

Morabito Consultants' statement noted that the 2018 report had "detailed significant cracks and breaks in the concrete, which required repairs to ensure the safety of the residents and the public."
https://www.yahoo.com/news/engineering-firm-found-structural-damage-031857075.html

Remedial work was necessary and identified in 2018. Three years later it hadn't been addressed.

From the video of the collapse, the central portion of the north wing collapsed and then the eastern portion collapsed (somewhat being pulled sideways and down). There was an entry point to the garage under the center section of the building. (See figure)

Concrete should be in compression and the rebar would take some tensile or bending load, and shear if present. Concrete is porous (unless specially designed and treated) meaning water can infiltrate, and salt water is particularly damaging to concrete and the rebar (corrosion). Even without saltwater, standing water can cause concrete to deteriorate.

It will take time to get to the foundation and collect forensic evidence as to the condition of the subsurface and concrete used in the foundation.

Some article on concrete and seawater.
https://theconstructor.org/concrete/concrete-seawater-effects-preventions/843/

https://www.concreteconstruction.net/_view-object?id=00000153-8bb0-dbf3-a177-9fb9d6200000 (link to pdf, save or open pdf)

http://onlinepubs.trb.org/Onlinepubs/hrr/1966/113/113-002.pdf

An interesting Nature article - Rare mineral is the key to long-lasting ancient concrete
https://www.nature.com/articles/nature.2017.22231
 

Attachments

  • Champlain_tower_south_88thStreetGarageEntrance.png
    Champlain_tower_south_88thStreetGarageEntrance.png
    170.8 KB · Views: 142
Last edited:
  • Like
Likes mathwonk, Twigg, Lnewqban and 1 other person
  • #36
The Washington Post had a story on the front page this morning which described a man whose wife was talking on the phone from her balcony when the collapse occurred. He said that she saw the pool collapse into the garage. After that, the building collapsed and her line went dead. :frown:
 
  • Sad
Likes Twigg and Astronuc
  • #37
Borg said:
The Washington Post had a story on the front page this morning which described a man whose wife was talking on the phone from her balcony when the collapse occurred. He said that she saw the pool collapse into the garage. After that, the building collapsed and her line went dead. :frown:
I heard a similar story. The area near the pool should be one of the least stressed/loaded areas. Also the garage floor to the west of the pool area collapsed, but it's not clear if it collapsed first or got hit by the building as it collapsed.

Furthermore, the section of the tower structure to the west of the pool is still standing, whereas the part that collapse was further away and diagonally opposite the corner with the pool. The central portion of the wing north of the pool collapsed, then the part at the eastern end, directly north of the pool collapsed (it seemed to get pulled down by the collapsed section). It may mean the ground became unstable, as in a sinkhole situation, or perhaps liquefaction. If that is the case, then all the high rise buildings are at risk, regardless of the concrete and reinforcement.

Someone listed an apartment next door for $1.375 M. It was purchased in October last year for just over $1M. The listing has since been pulled after negative comments. I should clarify that the apartment was in one of the other sister towers, not the Champlain Tower South that collapsed. I was expecting that the apartments in the CTS are probably on the order of $1M each, although the apartments on the lower floors are probably less.
 
Last edited:
  • Wow
Likes Greg Bernhardt
  • #38
  • Like
Likes CalcNerd and Lnewqban
  • #39
I think that Items I, J and K on pages 7, 8 and 9 look pretty threatening, and urgent, especially at the top of page 7, where MC indicates the failed waterproofing is causing major structural damage to the concrete structural slab below these areas, after indicating the waterproofing is beyond its useful life. Then it states, "failure to replace the waterproofing in the near future will cause the extent of the concrete deterioration to expand exponentially." That is a fairly dire warning. It should have been repaired during 2019!

Of course, MC only looked at the building, not under the building. I'm sure insurance companies will force highrise building owners to look under the buildings for unstable areas.
 
  • Informative
Likes Twigg and berkeman
  • #40
Astronuc said:
failure to replace the waterproofing in the near future will cause the extent of the concrete deterioration to expand exponentially
And you might lose a parking garage.
 
  • #41
Vanadium 50 said:
And you might lose a parking garage.
I recall seeing a number like $9 million for repair, but I don't know the scope of that.

The town/city or whatever responsible entity will now have to check the stability of the ground on which that building and nearby high-rises sit. If indeed, there was some kind of sinking or subsidence, then all such structures are at risk. It will depend on the loading of the foot print.

Some of the other information indicates the garage was subgrade, or subsurface, to see if it was unstable. Also, in figures J1 and J2, it's not clear which entrance; there are two, one of 88th Street on the north side of the building and one near the southwest corner, which may be to the upper garage deck. I'm guessing from the slope, J2 is looking north up the ramp to 88th St.

Could street runoff travel down that ramp and pool in the garage? Could the water/rain and upper garage deck pool and drain to the lower garage level? If the waterproofing failed, the water could seep into the foundation and subsurface, where drainage may be poor, given that it is near sea level. Then if water pooled in the subsurface, the ground could become soft (and more easily flow), AND if there is saltwater intrusion into that formation, then the pooled freshwater would allow migration of the sea water into the formation, which might explain the corrosion of the rebar and concrete floor.

Inspections will have to look at the subsurface to see if there is seawater intrusion under the concrete flooring and footings of the building. Then they will probably have to rewrite the code to prohibit similar construction on the island. They should probably look for corrosion in Surfside's sewer/storm drain system.

I was looking for the wastewater treatment plant, but I cannot readily find it.
 
Last edited:
  • Like
Likes BillTre and Vanadium 50
  • #42
One thing that's not mentioned is geology. The whole thing sits on karst. Lots can happen with karst.
 
  • Like
  • Informative
Likes Twigg, BillTre and Astronuc
  • #43
Vanadium 50 said:
One thing that's not mentioned is geology. The whole thing sits on karst. Lots can happen with karst.
https://en.wikipedia.org/wiki/Karst

Maybe also Coquina, which is also porous, or perhaps a combination.
https://www.nps.gov/casa/learn/historyculture/coquina-the-rock-that-saved-st-augustine.htm
They did not have long to wait before the coquina walls were tested. In 1702, Governor James Moore of Charleston led his English forces against St. Augustine and the Castillo. He captured the town and set his cannon up amongst the houses to bombard the fortress. But a strange thing happened. Instead of shattering, the coquina stone merely compressed and absorbed the shock of the hit. The cannon balls just bounced off or sunk in a few inches. The shell rock worked!

I don't know the details of the geology in the Miami area, but I do know that local governments have expressed concern about infrastructure due to rising sea level and heavy flooding with high tides. There is a lot of infrastructure at risk, and the collapse of CTS in Surfside may the a warning to all the cities along the Atlantic and Gulf Coast, especially for older structures built during the early 80s and before.

https://news.yahoo.com/beach-residents-wondering-whether-building-150945957.html
 
  • Like
Likes BillTre
  • #44
If the building sat on karst, that (speculatively) explains a lot.

I took a look at this report on karst geology in Florida. In Fig 10 (page 22), you can see that Dade county is marked as "thinly covered karst". With the poor drainage, there was probably standing water that seeped deep into the ground and corroded the karst. That speculative hypothesis could explain the 2mm/yr subsidence rate that was seen in Wdowinski et al's data from 1992-1999.

Not suggesting that this subsidence was the cause of the collapse. It's just a complicating factor, and it's unclear to me how it might've fit in. The failed waterproofing and corroded foundation smells fishier to me.

Another question that bugs me is why the building pancaked. I saw in the engineering thread @Lnewqban linked that the walls are CMU. Is this kind of failure mechanism typical for that construction?

Still need to read the engineer's report.
 
  • #45
Twigg said:
Another question that bugs me is why the building pancaked. I saw in the engineering thread @Lnewqban linked that the walls are CMU. Is this kind of failure mechanism typical for that construction?
There is some focus on the base of the building and the underground garage.

https://www.msn.com/en-us/news/us/possible-failure-point-emerges-in-miami-building-collapse/ar-AALvJr3
While no definitive conclusions could be drawn from the surveillance video, which was shot from a distance and reveals only one perspective of the disaster, some of the engineers reviewing it last week said it seemed to suggest that the failure began at a specific point near the bottom of the structure — perhaps as far down as the parking garage beneath the building, or on the first few floors.

From what can be seen in the video, part of the structure first slumped, seemingly falling vertically in one giant piece, as if the columns had failed beneath the southern edge of the center of the building, not far from the pool. Like a nightmarish avalanche, the failure quickly spread and brought down the entire center of the building. Seconds later, a large section to the east also toppled.

In the video of the collapse, there is some lateral motion of the building, and columns and their joints don't do well with lateral motion. Once the columns sheared or buckled at the first floor and below, then the upper mass drops with a jolt, the lowest intact floor collapses/pancakes, and there is a progression up the remaining structure until all the floor collapse.

Edit/update from the cited article:
Gregg Schlesinger, a contractor and lawyer in Florida, said that cracks and a kind of crumbling in the concrete known as “spalling,” also identified in the 2018 report, should have been a “red flag” if it seemed serious at the time. If that were the case, he said, engineers should have dug deeper to find out what was causing the deterioration.
 
Last edited:
  • Informative
  • Like
Likes Lnewqban and Twigg
  • #46
Borg said:
The Washington Post had a story on the front page this morning which described a man whose wife was talking on the phone from her balcony when the collapse occurred.
I heard another story of some guy who spoke with his mother who was awakened from noise in the building and she couldn't go back to sleep. She described popping and creaking sounds. I don't know if she was a survivor or one of those missing.

Edit/update:
The night before the Champlain Towers South building collapsed, Pablo Rodriguez recalls his mom telling him she heard a loud creaking noise.
She’s among the 150 people still missing, along with Rodriguez’s grandmother.
https://www.wbur.org/hereandnow/2021/06/29/surfside-condo-missing-family
 
Last edited:
  • Like
Likes russ_watters
  • #47
Apparently, the garage under the Champlain Tower South building had a chronic flooding problem with seawater, especially with high tides, and presumably hurricanes.

https://www.msn.com/en-us/news/world/ex-maintenance-manager-for-surfside-condo-that-collapsed-recalls-saltwater-intrusion/ar-AALvrfH

William Espinosa, who oversaw maintenance of the Champlain Towers South condo building from 1995 to 2000, recalled the building's garage experiencing a concerning amount of seawater during high ocean tides.

"Any time that we had high tides away from the ordinary, any King Tide or anything like that, we would have a lot of saltwater come in through the bottom of the of the foundation," he told CBS 4 Miami, adding they had to use two large pumps to try and remove the rising water.

"But it was so much water, all the time, that the pumps never could keep up with it."

Furthermore, building managers discovered a large hole under the condo after the collapse that may have been caused by saltwater intrusion. Saltwater intrusion can be particularly corrosive to older concrete, as it attacks the pillars and foundation and can slowly erode concrete and cause damage to steel, CBS 4 Miami reported.

"The water would just basically sit there and then it would just seep downward," Espinosa told the news outlet. "It would just go away after a while. And I would think, where does that water go? Because it had to go in through somewhere. I'm talking about a foot, sometimes two feet of water in the bottom of the parking lot, the whole parking lot."

:oops:

I don't understand the statement, "building managers discovered a large hole under the condo after the collapse". I would imagine that first responders discovered a large hole and reported it, but was that the garage, or there is actually a large void under the foundation/garage. The could imply flooding or saltwater intrusion, and based on the observations of the former maintenance manager, they should have investigated 20+ years ago. Did the flooding continue, and was it simply ignored?
 
  • Like
  • Informative
Likes Twigg and Lnewqban
  • #48
I'm starting to see a coherent story here. The poor drainage made this building a high maintenance property. It likely caused both the subsidence and the damage to the foundation that was seen in 2018. (The failure of the waterproofing sounds like it was an expected event after that much time.) Whoever was responsible repeatedly ignored these action items / costs, preferring stop-gap measures (like pumps) to actually fixing anything. "My other properties don't need all this maintenance, it'll be fine!"

How does the investigative team determine what caused the hole in the foundation? Anyone have experience with this kind of thing?
 
  • Like
Likes russ_watters
  • #49
Twigg said:
How does the investigative team determine what caused the hole in the foundation? Anyone have experience with this kind of thing?
The investigation will have to characterize (topographical mapping) the surface and subsurface. Besides taking core samples of the surrounding formation (i.e., that which did not collapse), they will have to take chemical samples around the void and into surrounding formation. There are also other methods, such as ground-penetrating radar (GPR), which could have been employed on the concrete columns, and a relatively new method, electrical resistivity tomography (ERT), or ground conductivity measurements. And one could use methods employed by mining and petroleum industries to investigate formations, e.g., well-logging techniques.

https://en.wikipedia.org/wiki/Electrical_resistivity_tomography
https://en.wikipedia.org/wiki/Well_logging
 
  • Informative
Likes Twigg
  • #50
Don't want to sound like a "wise guy" but judging from the pictures seems like the building had a structural system made from reinforced concrete cast on site which unlike reinforced concrete elements welded together on site is more structurally stable. A single reinforced concrete column can easily hold its own full height given weight plus the added weight of whatever is attached given it has lateral anchors or stability.
Normally when a building sinks it happens to either the full building or some portion of it.
Still I personally think sinking of few mm a year can't cause a collapse like this, unless it manages to single out many individual columns such that the cracks form around them and they are not laterally anchored anymore which is very unlikely.
What does seem more probable is that the structural elements like columns were weakened over time , also some lateral stability was lost but even this I believe could not case the collapse if not acted by some third force which I might speculate was a sinkhole or some ground fault.
Based on the CCTV video it seems like the collapse started from the middle of the building then went through to the other side and then one of the side which survived the initial collapse but was visibly tilted also went down.

As I said before even with cracks in the concrete rebar being still in place serves some lateral anchoring so I don't think concrete columns could just buckle under their own weight given they have the building structure still around them, also given concrete is best at compression so unless broken otherwise typically doesn't yield.So what I think happened was this. The cracks and rebar rusting over time created structural weakness, in itself not being enough to cause collapse, then some other factor caused a few of the columns in the middle of the building to collapse, this weight was still attached to the rest of the building by rebar so it created a pull force. This I believe is the reason why the portion of the building in the video collapsed a few seconds later than the first portion, you can see that it has visibly tilted.
I have heard that experts in controlled demolition often use this to take down buildings with less explosives. They break a crucial portion of the building and then they let the collapsing inertia to pull on the adjacent building via the rebar laid into the structure, or for steel structures the girders and trusses.
In this way one can blow out the middle of a tower for example and make that the outer portions fall inwards because of the pull and lost lateral stability.
If anything this Florida case seemed almost like a perfect controlled demolition case where the middle went straight down and the side fell inwards on top of the already collapsed middle portion.
 
  • Informative
Likes Twigg
  • #51
Twigg said:
Whoever was responsible repeatedly ignored these action items / costs, preferring stop-gap measures (like pumps) to actually fixing anything. "My other properties don't need all this maintenance, it'll be fine!"
My understanding is this was a condo. The "responsible" people are therefore the individual unit owners. The reported $9 million cost to repair split among the (reported) 160 units would be a $415 per month assessment, for 15 years (at 3%). That looks like a bargain, but only with the benefit of hindsight. In any condo association I've been involved with, such a proposal would meet very strong pushback with little chance of it being passed. Just human nature, IMO.
 
  • Like
  • Sad
Likes mathwonk, Twigg and russ_watters
  • #52
What I want to add is this. I personally don't think the building was in a critically bad structural condition. Bad yes most likely but not to the point where it can just go down like it did.
Here are my reasons for thinking this. When i watch the video I see the middle portion collapse first and the side portion left still standing for a couple of seconds in a tilted position and collapses only then. The other half of the building still left standing. Think of the lateral pull force created by the collapsing middle portion on the rest of the structure. One side of it survived this force till now, the other side survived it for a few seconds. For this I think the reason is that one side was much thicker (the left standing one) while the other side was much thinner (the one that stood up for a few seconds) The side that survived a few seconds based on the video was a thin outer portion which probably had no more than around 10 columns most likely in two rows.
Given such a structural arrangement and being pulled by a collapsing neighboring section I'd say it did rather well. If it was "that weak" it would have went smoothly down along the middle and you would not see a difference instead a smooth continual domino like collapse.
Also please see this video. (the action is more towards the end)


This building was "enjoying" a winter/summer climate left abandoned for some 25 years. At the moment of demolition it's total age was close to 40. It was a Soviet sanatorium built in the early 80's.
It has a very interesting reinforced concrete pillar/column type base that extends up to around the 3rd floor. On those columns sits the whole upper structure. Beneath them was built a smaller 2 story building.
https://www.google.com/search?q=sanatorija+liva&source=lnms&tbm=isch&sa=X&ved=2ahUKEwiQqKf27LrxAhWqlYsKHX9-A9AQ_AUoAXoECAEQAw&biw=1366&bih=615

Now what I want to illustrate with this is that even after all the columns of this building were half cut to weaken them, not to mention they were out in the open rain and frost for decades , then even after breaking half of them just the structure directly beneath fell down while the rest was left standing. This structure was also assembled from reinforced concrete panels welded together, instead of floor slabs and columns cast as a monolith on site as the Florida building.
I highly doubt the Florida building was in a worse shape than this abandoned sanatorium.
Both were roughly the same size and height. It takes an awful lot of rusting and cracking where that alone can cause a collapse like this, in a reinforced concrete monolith structure.

In the FL case, since the structure seems like a monolith cast reinforced concrete , I'd say that in order to initiate a collapse multiple adjacent columns would need to completely lose vertical loading capability, one is not enough since if only one loses such capability it then "hangs" in the floor slabs connecting it to the adjacent columns. Surely it might be the case that the adjacent columns or floor slabs were so weak that having to bear the load of just one additional column was enough but again I doubt that. My bet is on multiple columns.
What can cause that is an open question in this case.
 
  • Like
Likes Lnewqban
  • #53
From the Miami Herald - https://www.miamiherald.com/news/state/florida/article252340108.html

Could it have been a sinkhole?​

Miami-Dade County Mayor Daniella Levine Cava told reporters Friday morning that there was no confirmed sinkhole beneath the condo building that crumbled.

But the sudden, unexpected nature of the building’s collapse left officials and experts wondering about the possibility.

Jason Borden, the Florida regional director at O&S Associates — which bid unsuccessfully last year to perform the 40-year inspection at Champlain South — said he did an hour-long site visit in January 2020 and “didn’t see anything alarming or out of the ordinary.” The property manager believed the roof should be repaired or replaced, Borden said, and there were some cracks in the ceiling of the parking garage below street-level, as well as in the stucco that coated the building’s concrete walls.

But he didn’t see anything that seemed to put the entire structure at risk.

“My suspicion is that there was something going on there that was not detectable,” Borden said. If a sinkhole were to open up beneath a building, he said, “you don’t know it’s going to happen until it happens.”

Borden said reviews of the underground structural integrity of buildings, including during the 40-year recertification process, are rare, in part because going underground is a “very pricey, very complicated” process. The bulk of a 40-year inspection is visual, he said, and excavations would likely only be done if there were visible evidence of shifting or movement in the foundation.

Read more here: https://www.miamiherald.com/news/state/florida/article252340108.html
The 2018 report about cracked concrete and damage to the entrance/exit ramp from the lower portion of the garage gave 'red flags'. I don't think folks looked, for whatever reason. I have seen such behavior in the nuclear and aerospace industries, where folks don't look because they might find a problem, which will require costly remedial action. And sometimes, the result is catastrophic failure including loss of life in some cases.

Salzhauer said one resident of Champlain South told her that, while construction was being done over the past few years on the building next door — 8701 Collins Ave., known as Eighty Seven Park — the Champlain structure was “shaking” and there were “cracks” in the building as a result.

“The tenants in South were complaining a lot because their building was shaking and vibrating when they were digging and blasting at the construction site,” Arbide said.

https://www.miamiherald.com/news/state/florida/article252340108.html
It's a very good article looking at various aspects.

artis said:
This building was "enjoying" a winter/summer climate left abandoned for some 25 years. At the moment of demolition it's total age was close to 40. It was a Soviet sanatorium built in the early 80's.
How close to the ocean or seawater? The Champlain tower is probably about 100 m from the ocean, and a former manager of maintenance indicated periodic flooding by seawater! Investigators will have to look to see if a void opened up under the building, or if the columns simply crumbled due to saltwater corrosion (chemical attack).

In the process industry, there have been stress corrosion cracking of stainless steel piping and vessels due to chlorine attack over 2 or more decades (I remember 25 years in one case), and there are similar failures due to polythionic acids or hydrogen sulfide, or a combination of these elements and compounds. Usually, the higher the temperature the shorter time to failure, depending on the stress level.

I personally have experience with degraded cement/concrete in the foundation of my house where persistent pooling of water due to failed gutters (previous owner failed to maintain) had caused cement and cinder blocks to disintegrate. The inside (basement) surface, which was painted and covered in gypsum board, showed minimal damage until I removed the gypsum board and found rotten wood. The cinder blocks looked intact, but mortar was cracked and powdery in some cases. It wasn't until I dug out the outside of the foundation that I found 2 and 3 courses of cinder block (concrete masonary unit) had disintegrated. I could pull the block apart with my hands. I replaced the damaged blocks, and properly sealed the foundation.

I subsequently found that the floor of the basement had been poured without rebar and improperly made concrete. Parts of the concrete were more sand than cement. In some cases, with pooling water, the cement may have dissolved leaving just the sand. It didn't take much effort to chisel into the floor, and in some cases, I could drag a cold chisel across the floor and scrape a channel into the cement/concrete. I eventually had to chisel out the crack and refill with proper concrete mix. Eventually, hired a company to place a trench drainage system to prevent flooding in the basement. So far, so good.
 
Last edited:
  • Like
Likes Twigg and Lnewqban
  • #54
Surfside official was sent disturbing report. He told board condo was ‘in good shape’
Read more here: https://www.miamiherald.com/news/local/community/miami-dade/miami-beach/article252394393.html

A month after an engineer’s report flagged “major structural damage” at Champlain Towers South, the chief building official for the town of Surfside told residents the condominium was “in very good shape,” according to minutes from a November 2018 board meeting obtained by the Miami Herald.
:oops: :oldsurprised:o_O
Ross Prieto, who left the post last year, had reviewed the engineer’s report, the minutes say. Records show condo board member Mara Chouela forwarded a copy to him two days earlier.

But this past Saturday, Prieto told the Herald he didn’t remember getting the report.“I don’t know anything about it,” he said. “That’s 2018.”

Asked Sunday about the November 2018 board meeting, Prieto declined to comment, citing the advice of an attorney.

That was after details of the November 2018 meeting minutes were first reported Sunday by NPR.
o_O
The owners, or perhaps the board, should have asked for Frank Morabito of Morabito Consultants to provide a statement. Unless they were engineers, and particularly structural engineers, I imagine none of the board members understood the dire situation of the condo. It was not 'in good shape'!
 
  • Like
  • Sad
Likes Twigg, Lnewqban and gmax137
  • #55
Another "red flag" a day or two before the collapse?

From Miami Herald via Yahoo - https://news.yahoo.com/two-days-condo-collapse-pool-202849974.html
There was nothing unusual about the lobby and pool area at Champlain Towers South condo, which looked clean and well maintained to a commercial pool contractor who visited the building last Tuesday, just 36 hours before half of the building unexpectedly collapsed. Then, he saw the basement-level garage.
One has to wonder, if someone saw something alarming, then what is the responsibility to report it? Maybe it wasn't in his workscope, but geez . . . It seems the building has been deteriorating in front of everyone who went through the garage, but somehow no one thought to raise the alarm.

Mohammad Ehsani, an engineer and concrete restoration expert who invented QuakeWrap technology, a way to reinforce old concrete columns, reviewed the contractor’s photos from the pool equipment room.

“You can see extensive corrosion of the rebars at the bottom of the beam. That is very serious,” Ehsani said, commenting it was the worst damage he had seen documented in the building so far. The equipment room runs along the southern wall of the building — an area that did not collapse.

“If the condition of the beam in the pool guy’s photo is something that was also happening under the building, that is a really major concern,” Ehsani said. In that case, it “absolutely” could have contributed to the collapse.

However, he cautioned against rushing to conclude that all beams in the building showed similar levels of damage to those exposed to chemicals from the pool. The 2018 report that documented “severe” structural damage to concrete in the garage under the pool deck did not include photos of anything nearly as alarming as what the pool contractor documented, Ehsani said.
It seems that the corrosion observed recently was perhaps worse than three years ago. If that area was affected, then what other areas (columns) were affected?
 
  • Like
Likes Lnewqban
  • #57
Vanadium 50 said:
The engineer's report is available. The issues that have been brought up are there. What isn't there is a sense of threat or urgency.
Having been peripherally involved in the construction industry in the past, I decided to read the Engineering Report.

To me it read as 'This building is falling apart, you better fix it!'

Obviously he was right. 😢
 
  • #58
@Astronuc the old Soviet sanatorium I was referring to was actually built in a local once famous small city which is basically located in the midst of a swamp. The area is very good for people's health having mineral water springs and lots of natural remedies that were used for health and disease treatment and rehabilitation.

But as for a reinforced concrete structure it is a bad environment , the sea was some 8 miles from the building so maybe the salt levels were not that high but the moisture from the surrounding swampy forests was all year round. I remember that once the building got abandoned after the dissolution of the USSR I went there to climb it as a kid because it was high and had a nice view. I mean it was sometimes so wet in there that you could see stalactite structures emerging from concrete walls not to mention the fact that whenever it rained i could see rivers of water flowing down from the upper floors through shafts and even through seems in the panels that formed the floor slabs.

Not to mention one other factor which is of big importance. Florida never has temperatures below zero or freezing from what I think. This sanatorium in my country is in a climate where we have hot summers and cold winters, so each year all that water froze up and you could see that it performed like a small explosive because as we all know here on PF water expands when freezing so if it's within a concrete column or panel or a brick it expands with great force and just tears the thing in half and makes cracks.

All of this happened for around 25 years year round.
See the links for pictures to see the base columns I am talking about
https://www.praeitieszvalgas.lt/sanatorija-liva-kemeri-latvija/
https://mapio.net/pic/p-9121735/When they took this thing down some 5 years ago they came up with a cheap and clever method because of the base columns were exposed they used a thick chain and two excavators to see-saw each column but before they could do that they needed to take about half the column out manually to ease the burden and time needed. A dangerous job as the guy in the cabin of the demolition excavator had to be very near the column as he was doing it.

Still after all columns were half cut and then they started to cut them one by one and yet still each time only the portion of the building fell that was directly above the completely cut columns. The rest stayed up.

Now it might be that the Soviets had used more concrete and rebar than necessary for this building as for many others because they had a planned economy and the builders did not care for the cost of material. The columns of that sanatorium were massive for it's 12 stories of height, from pictures it seems about twice the size of the Fl building ones , I remember it took about 3-4 people to join hands to completely surround a single column.
Still given what I described here I would doubt the Florida building being in a worse shape overall than this example.
 
  • Like
Likes Lnewqban
  • #59
Now since we are talking about rusting rebar and salt effects on the structural integrity of reinforced concrete structures I want to show an interesting example.
I live in a country with winters and long autumns and springs so we have had all kinds of weather from -30 celsius in which no one can start a diesel to +35 in summer when asphalt becomes rubber like.
In winters we use a salt-sand mix for road safety so it's also sprayed on bridges where it mixes with water and seeps through every smallest crack and seem possible.
As you can imagine this is a nightmare for the bridges structural integrity, not only is it fully open to year round weather conditions without any heating (unlike a building) it has to endure concentrated salt-water mix being poured on it for months at a time.
Here we had a local bridge that is being renovated now after some 50 years of use without any major renovation. The reason they shut the bridge down because they realized that the concrete columns and particularly the rebar within them was so rusted that the concrete was becoming split open.
See the pictures to understand the condition better
486284__5cb5b6bdd8b1e.jpg

486284__5cb5b6b89c1d2.jpg


https://www.lsm.lv/galerijas/31010/augusta-deglava-parvads-riga/?idx=6
See the link for additional pictures that might make you scared.

But given the extensive structural damage this bridge had and it's 50+ year history without any repairs it still did not collapse even though it had semi truck and bus traffic over it constantly.
There are many structures in similar climatic conditions like this in a shape even worse than this and a collapse is very rare for any of them.

As we know normally in the developed parts of the world whenever something is built it has some safety reserves put into it , rusting rebar is typically not enough and should not be enough to cause a complete structural collapse of a building/structure.As for the FL building , the floor slabs seem rather thin from the pictures , i'd say thinner than what I normally have seen in objects around here but then again it's a cast structure and an apartment blocks so the floor slabs are not meant to carry heavy loads and are probably enough for what they were made for.

Still I hold on to my own bet here that a collapse like this can only occur if multiple adjacent or otherwise structurally connected columns fail at the same time but for that to happen simply from rusting and degrading over time seems highly unlikely. I mean it surely impacted the structural integrity but not necessarily was the sole cause of the collapse.

If the rumors that residents heard cracking and popping sounds hours before the collapse are true then that would indicate that a major structural failure had happened hours before and overstressed the additional load bearing members or that a cause currently unknown was causing the whole structure or a large part of it to be overstressed beyond it's design limits. One such cause could be a sudden shift in the ground beneath part of the building whereby a number of columns lose their anchoring and are left hanging in their respective floor slabs dragging them to exert load beyond design limit to additional columns and slabs.

I remember a local case in my country where a big store collapsed. The store had a typical hangar like building with metal roof trusses atop which concrete panels were put. They wanted to create a garden on the roof so they put soil there but they somehow forgot to account for the additional weight of the soil during rain. So rain came and the soil got wet at one point in the day of the collapse residents heard cracking sounds and fire alarms went off (because of the pressure in fire water pipes was decreasing because the pipes were bending together with the roof)
The result was a sudden and abrupt roof collapse and 54 people killed.

The lesson here is simple. Even a intact structure without degradation can suddenly collapse due to large overpressure or exceeding of design parameters.
My bet is that structural deficiency is not enough to cause the FL building to collapse, it needed an additional catalyst to start the "reaction"
 
  • Like
Likes mathwonk and Lnewqban
  • #60
If that reflects the average level of competence or diligence of local contractors, I wonder how many other buildings in Miami Beach are 'in good shape.' I highly doubt Champlain is the only building around with botched drainage or flooding problems.
 