Grounding Test: Ordinary Multimeter vs Special Tool?

Click For Summary
SUMMARY

The discussion centers on the effectiveness of using an ordinary multimeter versus a specialized ground test tool for point-to-point resistance testing of grounding systems. It is established that while a multimeter can be used, its leads introduce significant resistance, making it unsuitable for accurate measurements, especially over long distances. A 4-wire "Kelvin" resistance meter is recommended for precise testing, as it eliminates lead resistance issues by using separate leads for current supply and voltage measurement. The widely accepted NETA value for grounding resistance is 0.5 ohm.

PREREQUISITES
  • Understanding of grounding systems and their importance in electrical safety.
  • Familiarity with resistance measurement techniques.
  • Knowledge of NETA standards for grounding resistance.
  • Experience with 4-wire "Kelvin" resistance measurement methodology.
NEXT STEPS
  • Research the specifications and usage of 4-wire "Kelvin" resistance meters.
  • Study the NETA standards for grounding resistance testing.
  • Explore the differences between ordinary multimeters and specialized ground test tools.
  • Review case studies on grounding system testing and compliance with safety regulations.
USEFUL FOR

Electrical engineers, safety inspectors, and technicians involved in grounding system testing and compliance with electrical safety standards will benefit from this discussion.

Royherd27
Messages
11
Reaction score
0
Can the point to point test, (to determine the resistance between the main grounding system and all the major electrical frames, system neutral, etc) be made with an ordinary multimeter or does it need a special ground test tool?
The NETA value of 0.5 ohm is widely accepted?
 
Engineering news on Phys.org
The advantage of an approved tester is that it is consistent with your country's requirements, and doesn't depend on you interpreting the rules and the readings and correctly applying the correct stimulus.
 
Royherd27 said:
Can the point to point test, (to determine the resistance between the main grounding system and all the major electrical frames, system neutral, etc) be made with an ordinary multimeter or does it need a special ground test tool?
The NETA value of 0.5 ohm is widely accepted?

The basic problem with ordinary multimeter is that its leads will add resistance in series. You will need long leads if you are probing between major electrical frames, the lead resistance will probably be orders of magnitude more than the bonding resistance you are trying to measure.

You need a 4 wire "Kelvin" resistance meter (previous posters provided links). Here is how they work:

2 leads supply a constant controlled current source through the ground structure under test (lead resistance not an issue here since it is a current source). The other two leads measure voltage across the current source. The voltage measurement leads draw very low leakage current so lead resistance here is not an issue.
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 83 ·
3
Replies
83
Views
7K
  • · Replies 53 ·
2
Replies
53
Views
7K
  • · Replies 13 ·
Replies
13
Views
6K
  • · Replies 38 ·
2
Replies
38
Views
8K
  • · Replies 7 ·
Replies
7
Views
12K
  • · Replies 105 ·
4
Replies
105
Views
11K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 12 ·
Replies
12
Views
17K
Replies
12
Views
3K