Why Does a Yd1 Transformer Connection Cause a -30 Degree Phase Shift?

Click For Summary
A Yd1 transformer connection results in a -30 degree phase shift due to the alignment of primary and secondary windings to the same phase angle. The phase angle of C1-A1 relative to N-A1 demonstrates this shift. Proper vector alignment is essential; for instance, in a delta configuration, the c1-a1 vector should be vertical, aligning with N-A1. The connection follows a specific arrangement based on the transformer nameplate, maintaining the same phase relationships across windings. For further details on transformer connections, IEC 60076-1 Annex D provides comprehensive explanations.
OliskaP
Messages
38
Reaction score
7
Hi,

I have problems understanding why, for example, a Yd1 connection introduces a -30 degree phase shift, see image below.

How should I think when I want to produce vector groups like that, and derive myself what the phase shift should be?

Thanks..
Yd1.JPG
 
Engineering news on Phys.org
First - just consider the actual phase angle of C1-A1 relative to N-A1 - there will be a 30deg Shift there. So it is not really any magic in the transformer - each winding Primary and Secondary are aligned to the same phase angle.

If you keep the vectors properly aligned - you will see... for example in the bottom Delta configuration, c1-a1 vector should be vertical because it is in the same phase as N-A1 above.
Now using the same Vector angle for N-B1 and N-B2 - connect the "tail" of a1-b1 to the head of the c1-a1, and then the same for b1-c1 - this should close the triangle of the delta.

I proper transformer nameplate will maintain this same arrangement. EXAMPLE
 
  • Like
Likes OliskaP
As windadct said A1_N is same phase as a1_4 , B1_N is same phase as b1_5, C1_N is same phase as c1_6 since the same magnetic flux will pass through both windings.
The connection will be as per attached sketch- for Yd11 : 5 with a1 ,6 with b1 and 4 with c1 and
for Yd1 a1_6, b1_4, c1_5.
The convention states an imaginary neutral point in the intersection of all three medians of the equilateral triangle , and an imaginary voltage to this neutral from each point of triangle. The a1 to neutral n is the first phase and the angle from HV A1_N is the considered angle which divided by 30 degrees gets the symbol of the connection[in Yd11 case 330/30=11].
You may find in IEC 60076-1 Annex D all the connections.
upload_2016-10-13_21-31-35.png

upload_2016-10-13_21-32-10.png
 
  • Like
Likes OliskaP
Very nice explanation, thanks, both of you.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 10 ·
Replies
10
Views
5K
  • · Replies 27 ·
Replies
27
Views
3K
  • · Replies 8 ·
Replies
8
Views
6K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 41 ·
2
Replies
41
Views
7K
Replies
2
Views
8K
  • · Replies 15 ·
Replies
15
Views
4K
Replies
7
Views
3K
Replies
7
Views
12K