High leg delta/high leg heating up and tripping the breaker

  • Thread starter Thread starter Crazyhorse2882
  • Start date Start date
  • Tags Tags
    Heating
Click For Summary

Discussion Overview

The discussion revolves around a service call by an electrician regarding a 175 amp 3-phase breaker that repeatedly tripped while feeding an AC unit with multiple compressors and blowers. Participants explore potential causes for the overheating of one phase, specifically the high leg, and discuss troubleshooting steps and theories related to electrical faults, load balancing, and connection integrity.

Discussion Character

  • Technical explanation
  • Exploratory
  • Debate/contested

Main Points Raised

  • One participant noted that the high leg was very hot and suggested it might be due to the motors being wired for a wye connection in a delta service.
  • Another participant proposed that a loose or corroded connector could cause local resistive heating, leading to the breaker tripping.
  • It was mentioned that ants could infest a breaker, blocking airflow and causing overheating.
  • A participant identified a high resistance ground fault as the problem, found a nick in the wire inside a flex connector, and noted burn marks on reducing washers used with the connector.
  • Some participants discussed the importance of checking phase-to-phase and phase-to-ground voltages, suggesting that an imbalance in utility line voltage could lead to excessive current draw from the motors.
  • There was speculation about whether the fault was intermittent, causing the breaker to trip after a period of heating up.
  • One participant shared that after resolving the issue, the currents were balanced at around 115 amps for each leg.

Areas of Agreement / Disagreement

Participants generally agree that the issue was related to a ground fault, but there are multiple competing views regarding the exact nature of the fault and the contributing factors, such as connection integrity and load balancing. The discussion remains unresolved on some technical aspects.

Contextual Notes

Participants noted the absence of a meg ohmmeter for testing wires, which may have limited troubleshooting options. There was also mention of the potential for intermittent faults and the effects of local heating on breaker operation.

Who May Find This Useful

Electricians, electrical engineers, and those interested in troubleshooting electrical systems may find this discussion relevant, particularly regarding issues related to phase imbalance and fault detection in 3-phase systems.

Crazyhorse2882
Messages
20
Reaction score
0
Ok I have a question that hopefully someone can answer. I'm an electrician and I recently had a service call where a hotel had a 175 amp 3 phase breaker feeding an ac unit with 4 compressors and 2 blowers that kept tripping. I first checked all the compressors and blowers to see if they were grounded or open and all were good. I then turned on the unit and all 4 compressors ran for about an hour and then the breaker tripped. Once it tripped I felt the 3 phases and phase C which happens to be the high leg was very hot so that leg is the culprit which tripped the breaker. I amp probed all three phases while they were running and it was a little off balance. The C phase was drawing around 120 amps, B phase 115 amps and A phase 105 amps. The compressors are 7.5 hp and draw approximately 22 amps each at 240 Volts. Does anyone have any idea why this one leg could be getting hot and tripping the breaker? Could it be that the motors are wired for wye connection and the delta service is the problem? Any suggestions would be helpful. Thank you in advance
 
Engineering news on Phys.org
You found one of the lines to the circuit breaker was heating up? With the breaker rated at 175A, then presumably each line would be rated for something like 250A continuous current?

This is not a new installation, so it has been working happily for years? So you can conclude a fault has recently developed? I take it you didn't find or fix the fault?

I'm wondering whether that cable has a loose or corroded connector, and this is causing local resistive heating. Can you feel whether the cable in that line is heated all along its length on both sides of the breaker?

I don't know whether it's possible for a breaker to be tripped by having one of its terminals subjected to local heating?
 
The supply is a delta high leg 3 phase. The high leg is 208 phase to ground, the other two phase are 120 to ground and it's 240 phase to phase. The load was a little off balance. A phase was drawing 105 amps, B phase 115 amps and C phase 120 amps
 
The supply is 120/240
 
NascentOxygen said:
I don't know whether it's possible for a breaker to be tripped by having one of its terminals subjected to local heating?

yes looseness can cause heat at the connection that'll travel along the conductor both directions, into the breaker and away from it via the wire, so your advice about feeling the wire was good
when ants move in and build a nest inside the breaker it blocks airflow and an infested breaker can overheat
 
I found the problem, it was a high resistance ground fault. I found a nick in the wire just inside the flex connector. Thanks for your help anyways
 
Wow ! Good find.

Nothing burned up ?
 
Thanks for the reminder. Step two to troubleshooting an electrical problem would be to think about it from a circuit analysis view, and maybe post a question to a EE forum.

Step one to troubleshooting an electrical problem should be a very thorough visual inspection.

Look before you think sounds overstated but ...
 
The ground fault was just inside of a flex connector that I had no way if seeing. The company I work for didn't have a meg ohmmeter to check the wires so they insisted on changing the breaker to a fused disconnect which I thought was fooling because I knew that the breaker was not the problem. So when I pulled the old breaker box off the wall I then pulled the wire out of the flex and visually inspected it and I found the ground fault. There were some burn marks on the inside of some reducing washers that were being used with the flex connecter
 
  • #10
Foolish not fooling
 
  • #11
I would also have checked the Phase-to-Phase and Phase-to-Ground voltages - in your case it may have shown the phase with the fault to have a lower voltage, but ALSO if the utility's line voltage was out of balance, the 3 phase induction motors would draw excessive current.
 
  • #12
Crazyhorse2882 said:
There were some burn marks on the inside of some reducing washers that were being used with the flex connecter
i'd guess it was intermittent fault that tripped the breaker before welding itself into a permanent fault ? Else something should have got really hot...?
 
  • #13
The voltage was fine but each leg had a little difference in current, not much though. It would run for an hour and then trip. So the only possibility that I can see is that the fault wasn't in direct contact with the can but was so close that just a tiny bit of fault current was leaking through and it took an hour to heat up the leg to the point of tripping the breaker. I called a friend of mine who's also an electrician and he called it a "high resistance" ground fault. Meaning that there was enough resistance between the leg and the can so that it didn't trip immediately but in time it would heat up and trip the breaker. In this case it was taking an hour almost to the minute every time
 
  • #14
Crazyhorse2882 said:
... I knew that the breaker was not the problem. So when I pulled the old breaker box off the wall I then pulled the wire out of the flex and visually inspected it ...
Now that's being a "dedicated troubleshooter". :bow:
 
  • #15
How'd the currents look afterward?
I'm still wondering where all that excess energy went for an hour.

But - you saw what it looked like and i didnt.

Glad it's running smooth for ya' now.

old jim
 
  • #16
My last measurement showed each leg around 115 amps. Everything was balanced. I'm guessing the excess energy was in the form of heat in the one leg that was heating up.
 

Similar threads

  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 7 ·
Replies
7
Views
8K
  • · Replies 38 ·
2
Replies
38
Views
8K
  • · Replies 17 ·
Replies
17
Views
12K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 1 ·
Replies
1
Views
4K
  • · Replies 6 ·
Replies
6
Views
4K
  • · Replies 5 ·
Replies
5
Views
4K