Discussion Overview
The discussion revolves around a service call by an electrician regarding a 175 amp 3-phase breaker that repeatedly tripped while feeding an AC unit with multiple compressors and blowers. Participants explore potential causes for the overheating of one phase, specifically the high leg, and discuss troubleshooting steps and theories related to electrical faults, load balancing, and connection integrity.
Discussion Character
- Technical explanation
- Exploratory
- Debate/contested
Main Points Raised
- One participant noted that the high leg was very hot and suggested it might be due to the motors being wired for a wye connection in a delta service.
- Another participant proposed that a loose or corroded connector could cause local resistive heating, leading to the breaker tripping.
- It was mentioned that ants could infest a breaker, blocking airflow and causing overheating.
- A participant identified a high resistance ground fault as the problem, found a nick in the wire inside a flex connector, and noted burn marks on reducing washers used with the connector.
- Some participants discussed the importance of checking phase-to-phase and phase-to-ground voltages, suggesting that an imbalance in utility line voltage could lead to excessive current draw from the motors.
- There was speculation about whether the fault was intermittent, causing the breaker to trip after a period of heating up.
- One participant shared that after resolving the issue, the currents were balanced at around 115 amps for each leg.
Areas of Agreement / Disagreement
Participants generally agree that the issue was related to a ground fault, but there are multiple competing views regarding the exact nature of the fault and the contributing factors, such as connection integrity and load balancing. The discussion remains unresolved on some technical aspects.
Contextual Notes
Participants noted the absence of a meg ohmmeter for testing wires, which may have limited troubleshooting options. There was also mention of the potential for intermittent faults and the effects of local heating on breaker operation.
Who May Find This Useful
Electricians, electrical engineers, and those interested in troubleshooting electrical systems may find this discussion relevant, particularly regarding issues related to phase imbalance and fault detection in 3-phase systems.