How Do I Calculate Voltage Drop Without Knowing Current?

  • Thread starter scarecrow75
  • Start date
  • Tags Tags
    Voltage
4 replies · 2K views · last reply
scarecrow75
Messages
3
Reaction score
1
Thread moved from the technical forums, so no HH Template is shown.
Hi all

Wondering if anyone can help. Really don't know where to start

I know Zs = Ze + Z1 + Z2

and Z1 = PCR 8.9 milli-ohms/meter
and Z2 = CPC 14.5 milli-ohms/meter
which equates to 0.0234X milli-ohms/meter over X meters

but where does my volt drop come in if I don't know my current?

Regards
Text problem statement for a single-phase ring final circuit: 230 V, 50 Hz supply, Ze of 0.8 ohm, cable resistances R1 = 8.9 mΩ/m and R2 = 14.5 mΩ/m, volt drop 18 mV/A/m, 32 A BS 88 fuse and 30 mA RCD, asking for maximum ring length.
 
scarecrow75 said:
but where does my volt drop come in if I don't know my current?

If the fuse is 32A the current could be any value <32A ??
 

Homework Statement


230 V, 50 Hz supply (TN)
Ze = 0.8 ohms
Z1 = 8.9 milli-ohms/meter
Z2 = 14.5 milli-ohms/meter
Volt-drop/Amp/meter = 18 mV/A/m

Homework Equations


Zs = Ze + Z1 + Z2
V / Zs = I ?

The Attempt at a Solution


Zs = Ze + Z1 + Z2
Zs = 0.8 + (0.0089 + 0.0145)X......where X is the distance in meters
Zs = 0.8 + 0.0234X

Then
230V / (0.8 + 0.0234X) = I

Not sure if this is correct!
Also is this relevant:
TN system... I know that for final circuits up to 32A disconnection time should not exceed 0.4secs
Voltage Drop, lighting circuits = 3%max and other circuits 5% max
if this is correct then 230V * 0.05 = 11.5V

Not sure if this is right approach

Any help?

Cheers
Text problem statement on a ring final circuit: single-phase 230 V 50 Hz TN supply, Ze = 0.8 ohm, R1 = 8.9 mohm/m, R2 = 14.5 mohm/m, volt drop 18 mV/A/m, 32 A BS 88 fuse, 30 mA RCD, asking maximum ring length in metres [80 m].
 
  • Like
Likes   Reactions: berkeman