How does voltage in wires affect conduit and nearby materials?

Click For Summary
SUMMARY

The discussion centers on the effects of voltage in wires on conduit and nearby materials, specifically addressing two scenarios: the heating of conductors in separate conduits for a 3-phase motor and the safety concerns of high DC voltage (60kV) wiring. It is established that running conductors in separate conduits can induce eddy currents in the conduit, leading to overheating. Additionally, maintaining a distance from metal is crucial to prevent arc-over and shock hazards, as per the National Electric Code guidelines.

PREREQUISITES
  • Understanding of 3-phase motor operation and wiring
  • Familiarity with eddy currents and their effects on materials
  • Knowledge of high voltage safety practices
  • Awareness of the National Electric Code (NEC) regulations
NEXT STEPS
  • Research the principles of eddy currents and their implications in electrical installations
  • Study the National Electric Code (NEC) requirements for conduit and wiring configurations
  • Learn about high voltage safety measures and installation best practices
  • Explore the effects of magnetic fields on conductive materials in electrical systems
USEFUL FOR

Electrical engineers, safety inspectors, and technicians involved in high voltage installations and conduit design will benefit from this discussion.

quikpik
Messages
2
Reaction score
0
Two questions here. From real-world problems, I was hoping someone smarter than me could explain the physics behind some issues I was told about. It's been a long time since I looked at an engineering or physics book, so please bear with me.

1) For a 3-phase motor, I was told that someone had the idea to run each conductor in its own conduit. He thought it was a good idea until the wires started to heat up and melt. Let's assume that the wires were sized for the correct full load amps of the motor. I was told that when the 3 conductors are run in the same conduit, that voltage/current offset each other. When they were run independently, it must've induced some sort of a charge in the conduit causing it to heat up? Is this possible, or is this story made up?

2) If I have a power supply, very high DC voltage (~60kV) with very low current (15mA), do you have to keep the wiring away from all metal? This is more of an engineering installation question, so maybe this isn't appropriate here. I was of the belief that as long as things were non-ferrous, everything would be fine, perhaps even putting the cables in aluminum conduit. I was told this was bad practice. For such an installation, no metal (even non-ferrous) should be within a foot of the cable, due to the possibility of the cable inducing a charge on nearby ungrounded metal. If someone were to then touch that metal, they're liable to get a shock. Is this backed by science?

Thanks for any explanations. It's been a long time since I even had to think about Maxwell or Faraday.
 
Engineering news on Phys.org
quikpik said:
Two questions here. From real-world problems, I was hoping someone smarter than me could explain the physics behind some issues I was told about. It's been a long time since I looked at an engineering or physics book, so please bear with me.

1) For a 3-phase motor, I was told that someone had the idea to run each conductor in its own conduit. He thought it was a good idea until the wires started to heat up and melt. Let's assume that the wires were sized for the correct full load amps of the motor. I was told that when the 3 conductors are run in the same conduit, that voltage/current offset each other. When they were run independently, it must've induced some sort of a charge in the conduit causing it to heat up? Is this possible, or is this story made up?

2) If I have a power supply, very high DC voltage (~60kV) with very low current (15mA), do you have to keep the wiring away from all metal? This is more of an engineering installation question, so maybe this isn't appropriate here. I was of the belief that as long as things were non-ferrous, everything would be fine, perhaps even putting the cables in aluminum conduit. I was told this was bad practice. For such an installation, no metal (even non-ferrous) should be within a foot of the cable, due to the possibility of the cable inducing a charge on nearby ungrounded metal. If someone were to then touch that metal, they're liable to get a shock. Is this backed by science?

Thanks for any explanations. It's been a long time since I even had to think about Maxwell or Faraday.

Welcome to the PF.

1) When the wires are run together in the same conduit, there is no net B-field (the currents cancel). When run alone, it may be that the eddy currents induced in the conduit heat it up too much.

2) The spacing issue is to avoid arc-over from the HV conductors to other conductors.
 
Steel conduit experiencing inductive heating is certainly not made up. See the attached section of the National Electric Code.
 

Attachments

  • 99nec300-20.png
    99nec300-20.png
    35.2 KB · Views: 737
He thought it was a good idea until the wires started to heat up and melt.

he's not the first, by a long shot.

http://media.nowpublic.net/images//97/7/977a0e06c35f94412e56c9d32e1704f5.jpg

Those red magnetic lines heat iron . But it takes substantial current, like to a motor or something, to make it dangerously hot.

if the iron encircles the return conductor too then the two magnetic fields will cancel.
That's why that paragraph in electrical code says run them all together.

If you have a clamp-around ammeter , clamp it around both wires of a lampcord and observe zero reading. Then split the cord and clamp around either conductor observe you read lamp current.

Then repair or replace the lampcord.

old jim
 
Last edited by a moderator:
That's actually a very simple, practical test. I wish I had thought to try that earlier.

As for my second question, would arc-over be an issue since my plan would have been to run the HV cable in aluminum conduit? The cable itself would also be insulated, of course. The shock hazard posed extended to metal fasteners as well, which might be in the vicinity of where the conduit is routed.

I have no problem using all non-metallic conduit, fasteners, etc, I'd just like to convince myself of why it'd be needed.
 

Similar threads

  • · Replies 18 ·
Replies
18
Views
5K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 16 ·
Replies
16
Views
3K
  • · Replies 21 ·
Replies
21
Views
7K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 24 ·
Replies
24
Views
5K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 19 ·
Replies
19
Views
4K
Replies
9
Views
2K