How long will it take to reach 1000ppm CO2 from 2000ppm

  • Context: High School 
  • Thread starter Thread starter mess
  • Start date Start date
  • Tags Tags
    Co2
Click For Summary
SUMMARY

The discussion centers on calculating the time it will take for CO2 levels to decrease from 2000 ppm to 1000 ppm in a room with specific ventilation conditions. The participants utilize a differential equation approach, specifically V(dC/dt) = f(c_in - c), where V is the room volume, f is the volumetric flow rate, c_in is the inlet CO2 concentration (400 ppm), and c is the instantaneous CO2 concentration. The conversation highlights the importance of ventilation effectiveness and the mixing of air, emphasizing that a well-mixed room achieves a ventilation effectiveness of 1.0, while imperfect mixing can lead to varied concentrations.

PREREQUISITES
  • Understanding of differential equations, specifically in the context of mass balance.
  • Knowledge of CO2 concentration measurements and units (ppm).
  • Familiarity with ventilation concepts, including volumetric flow rates and mixing effectiveness.
  • Basic calculus, particularly the concept of infinitesimal time increments (dt).
NEXT STEPS
  • Study the dilution ventilation equation to understand CO2 concentration dynamics.
  • Learn about ventilation effectiveness and its impact on indoor air quality.
  • Explore numerical methods for solving differential equations, particularly in environmental science.
  • Investigate tools for modeling air quality in enclosed spaces, such as computational fluid dynamics (CFD) software.
USEFUL FOR

This discussion is beneficial for environmental scientists, HVAC engineers, and anyone involved in indoor air quality management, particularly those interested in CO2 dynamics and ventilation strategies.

mess
Messages
59
Reaction score
8
TL;DR
If a fan is pumping in fresh air (400ppm CO2) at 50 CFM into a space that is 500 CF , another fan is pumping out the air of the space at 50cfm, and the space is currently 2000ppm, how long will it take to reach 1000ppm CO2?
would this be a quadradic equation since its dealing with half life? I think in 500/50 = 10 minutes, the fan would have brought 500 CF of fresh air, but the out fan would have been taking out the same amount of air which includes the fresh air, so at 10 minutes, it should have less then half the average CO2 ppm between the two. so it should be less than (2000+400ppm)/2 = 1200 ppm, but how much exactly?
 
Last edited:
  • Like
Likes   Reactions: Delta2
Mathematics news on Phys.org
Normally one fan should lead to the specified air flow already, a second fan might increase it.

Your room is probably more than 1 foot tall, so 500 square feet will correspond to far more than 500 cubic feet of air.

Assuming the air mixes fast relative to the exchange rate: You get an exponential distribution above the baseline of 400 ppm. C(t) = 400ppm + 1600ppm*e-ct. Here c is the air flow divided by the volume.
 
  • Like
Likes   Reactions: russ_watters and mess
In order to write down the ODE that governs this system:
For a time window ##(t,t+dt)## :
  • How much mass of CO2 is added to the room?
  • How much mass of CO2 is removed from the room?
Assume that the density of the CO2 remains constant and equal to ##\rho(t)## during this time window of length ##dt##. So at time ##t+dt## what is the new density of CO2 ##\rho(t+dt)##. If all goes well and you answer correctly my questions you ll be able to find ##d\rho(t)=\rho(t+dt)-\rho(t)## and from that find the differential equation that governs this system.
 
Last edited:
Delta2 said:
In order to write down the ODE that governs this system:
For a time window ##(t,t+dt)## :
  • How much mass of CO2 is added to the room?
  • How much mass of CO2 is removed from the room?
Assume that the density of the CO2 remains constant and equal to ##\rho(t)## during this time window of length ##dt##. So at time ##t+dt## what is the new density of CO2 ##\rho(t+dt)##. If all goes well and you answer correctly my questions you ll be able to find ##d\rho(t)=\rho(t+dt)-\rho(t)## and from that find the differential equation that governs this system.

Thanks for the response! What is dt? is it delta time? and what is p(t)?
Delta2 said:
How much mass of CO2 is added to the room?
A human adds 5000ppm CO2 in one hour. So me being alone will add that to the room

Delta2 said:
How much mass of CO2 is removed from the room?
I don't know, there is no constant rate to this because the fresh air is being mixed in with the inside air, and that mixture is being extracted.
 
Let V be the volume of the room and f be the volumetric flow rate into and out of the room. The rate of CO2 entering the room is ##fc_{in}## where ##c_{in}## is the concentration of CO2 in the inlet stream (400 ppm). If the room is well-mixed, the rate of CO2 exiting the room is fc, where c is the instantaneous concentration of CO2 in the room air at time t. Therefore, the rate of increase of CO2 in the room is ##fc_{in}-fc=f(c_{in}-c)##. And this is also equal to ##V\frac{dc}{dt}##. Thus, from a mass balance on the CO2, we have $$V\frac{dc}{dt}=f(c_{in}-c)$$This is subject to the initial condition c(0)=2000 ppm.
 
  • Like
Likes   Reactions: russ_watters and Delta2
mess said:
Thanks for the response! What is dt? is it delta time? and what is p(t)?
I guess you are not familiar with Calculus in order to be asking this question. Yes ##dt## is an infinitesimal increase in time. And ##\rho(t)## is the instantaneous density of CO2 in the room at the time ##t##.

Anyway @Chestermiller explains quite well how to setup the differential equation that governs this system's behavior at post #5, I guess you can ask him for more details, he is more knowledgeable than me and since he has enter this thread grab the chance to talk with him :D.
 
Last edited:
  • Like
Likes   Reactions: mess
@mess you don't need the differential equation if you just want to calculate the concentration after a certain time; @mfb gave you the equation for it. Otherwise if you want to see the dilution progress you can plug the differential equation into a spreadsheet and graph concentration vs time.

One thing to watch out for is the purge rate depends on the ventilation effectiveness. A perfectly mixed ventilation/room will have a 1.0 ventilation effectiveness. If mixing isn't perfect, it will be lower, and the concentration will be different in different places in the room. And if ventilation is introduced on one side of the room and exhaust is on the other, you will get displacement, and a greater than 1.0 effectiveness.

Some more resources, with different calculations for differently framed problems:
https://en.wikipedia.org/wiki/Dilution_(equation)#Dilution_ventilation_equation
http://faculty.washington.edu/airion/ENVH557/Dilution_Vent_1.pdf
 
  • Like
Likes   Reactions: mess
mfb said:
Your room is probably more than 1 foot tall, so 500 square feet will correspond to far more than 500 cubic feet of air.
It's a van.
 

Similar threads

  • · Replies 11 ·
Replies
11
Views
6K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 8 ·
Replies
8
Views
14K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 12 ·
Replies
12
Views
88K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
17
Views
7K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 4 ·
Replies
4
Views
21K