HV and LV difference on distribution boards

Click For Summary
SUMMARY

The discussion centers on the differences between high voltage (HV) and low voltage (LV) distribution boards, specifically in the context of cooling pumps operating at 3.3kV and 415V. The user, kdcoops, calculates the power requirements using Ohm's Law, determining that the larger pump at 3.3kV requires 60 amps (198,000 watts) while the smaller pump at 415V requires 228 amps (94,620 watts). The conversation emphasizes that using a 415V motor for the larger pump would necessitate a significantly higher current, estimated at 860 amps, thereby requiring larger cables to handle the increased load.

PREREQUISITES
  • Understanding of Ohm's Law and its application in electrical systems
  • Familiarity with electrical power calculations (watts, volts, amps)
  • Knowledge of cable sizing standards and requirements
  • Basic concepts of high voltage (HV) and low voltage (LV) systems
NEXT STEPS
  • Research cable sizing calculations for high current applications
  • Learn about the implications of using high voltage in industrial settings
  • Study the principles of electrical power distribution systems
  • Explore the differences in efficiency and safety between HV and LV systems
USEFUL FOR

Electrical engineers, technicians working with distribution boards, and anyone involved in the design or maintenance of electrical systems in industrial settings.

kdcoops
Messages
3
Reaction score
0
. Hello, I have recently been given a course at work as someone left and they had already paid for it, unfortunately I am a bit green to electrical systems ( I only work in stores but want to learn) And my course helper, our onsite electrical man is off on long term sick!
In my course I have been asked:

" Demonstrate a clear understanding on Ohms Law by showing why different voltages are used on certain distribution boards on site"

Now I have chosen to try and explain why we have two different cooling pumps on site. A large one with a motor at 3.3kv and a smaller one at 415v. Using Ohms Law I have worked out that the larger one which runs at 60amp is 198,000 watts and the small one at 228amps is 94,620watts.

What I am struggling with is, if we used a 415v instead of 3.3kv motor on the bigger pump would we need more amps meaning a lot bigger cables to get the power to run the big pump??

I understand it says on site you don't like to give direct answers and I don't expect that but would appreciate any help what so ever and if you could try and keep it pretty simple.

Kind Regards
kdcoops
 
Physics news on Phys.org
kdcoops said:
What I am struggling with is, if we used a 415v instead of 3.3kv motor on the bigger pump would we need more amps meaning a lot bigger cables to get the power to run the big pump??

What you said is correct. It seems as though you have a good handle on this problem!

if you really want to demonstrate knowledge of ohms law, I would calculate what the exact required current would be if the voltage dropped down to 415 V. then use some reference material too look up exactly what size wire you would need

Keep up the good work!
 
Hi donpacino,
Thanks for the reply, good to know I am on the right track. I have had a go a working out the current needed and came up with 477amps does this sound about right?? Hopefully it is, then I just need to try find out what cable size would be need to carry that.
 
Sorry scratch that last one, now I have had another go I have come up with 860amps! This seems a bit more likely to why we would use a higher voltage?
Thanks Kev
 
This is exactly why very high voltages are used for the national grid.
 

Similar threads

  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
Replies
2
Views
1K
Replies
4
Views
3K
  • · Replies 33 ·
2
Replies
33
Views
4K
  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 9 ·
Replies
9
Views
3K