Looking to create a temperature rate of rise table for air

In summary, there is no definitive answer for how hot an IT space would get if the AC was lost. However, if you assume there is no forced air flow, the room would reach equilibrium within minutes due to the heat loss from the equipment.
  • #1
Sola
8
3
How did you find PF?: Google

l was asked how hot would our IT space get if we lost all air conditioning. The space is 20' x 15' x 10', We keep set point at 70 F and have 80 kW of load. Assuming this exists in a well insulate container with 20 racks of equipment. Doesn't have to be perfect but a general idea as we compare to various equipment failure thresholds
 
Engineering news on Phys.org
  • #2
Welcome to PF. :smile:

How much airflow is there in and out of the room under those conditions? Are you assuming no forced air at all, so only convection flow? What is the ambient temperature outside of the room and outside of the building? How big are the vents into the bottom of the room and out of the top of the room?

Also, how hot does it need to get in there before some of that load automatically sheds? I assume there are temperature sensors that have some shutdown capability when the racks start overheating?
 
  • Like
Likes russ_watters
  • #3
I am making broad analysis without many specifics,
No air flow,
minor leakage (10%)
There are split systems in the space.
Ambient I choose is 50 F.
The various IT equip will shut off at various temps above 105 F.
My question is "what is the heat RoR" with the 80 continuing to heat the space. How much time in an emergency before we do a graceful shutdown vs hard stop. I am trying to graph this so we can show operators the data
 
  • Like
Likes berkeman
  • #4
BTW as a new user, where would I find posting procedures? TY for the help
 
  • #5
Sola said:
BTW as a new user, where would I find posting procedures? TY for the help
Under INFO at the top of the page you'll find the Rules and About Us pages. But for general posting guidelines, there are only a few:

** Schoolwork-type questions (even for self study) go in the Homework Help forums, and the student is required to show their work before we can help. We can't post solutions for them; we can only help guide them with questions and suggestions so that they figure out their schoolwork problems on their own.

** Technical posts go in the appropriate technical forum (which is why I moved your thread to the ME forum). It's best to post links to what you have been reading to try to figure out your question when starting a new thread. That helps others to see your level of understanding and tailor their responses accordingly.

** In some of the technical forums, there is a "Thread Prefix" A/I/B that is used to indicate the level of discussion that the Original Poster (OP) wants. A is Advanced (graduate school and above), I is Intermediate (undergraduate school level) and B is Beginner (high school level).

** Since we focus on mainstream science here at PF, we will generally require a link to a peer-reviewed journal article to start some of the more advance technical discussions.

That's about it, I think. Feel free to send me a Personal Message (PM, click my avatar and "Start a conversation") if you have any more questions about PF. Enjoy! :smile:
 
  • #6
Sola said:
l was asked how hot would our IT space get if we lost all air conditioning...Doesn't have to be perfect but a general idea as we compare to various equipment failure thresholds
HVAC engineer here. The short answer is infinity. The longer answer is extremely difficult to calculate but suffice to say the room would be uninhabitable and the IT equipment would fail before it got to an equilibrium - in a matter of minutes.

For the room air, you can calculate the rate of rise from mass, heat capacity and heat input. The mass of equipment won't matter immediately so that should get you through the first 5-10 min.

[Edit] Nope, just ran the numbers and it's seconds, not minutes.
 
Last edited:
  • Wow
  • Like
Likes Lnewqban and berkeman
  • #7
TY Russ, Is there a formula or calculator to input the room data. Per above without getting very specific on building envelope for a telco hut. 20 x 15 x 10' CMU exterior, r-19 wall insulation, no windows, metal truss roof with 4" roof rigid roof insulation on a metal corrugated deck. We use split hvac systems. I am learning Newton's laws and looking to build an excel sheet that I can do high level comparisons at different loads. TY for comments.
 
  • #8
Sola said:
TY Russ, Is there a formula or calculator to input the room data. Per above without getting very specific on building envelope for a telco hut. 20 x 15 x 10' CMU exterior, r-19 wall insulation, no windows, metal truss roof with 4" roof rigid roof insulation on a metal corrugated deck. We use split hvac systems. I am learning Newton's laws and looking to build an excel sheet that I can do high level comparisons at different loads. TY for comments.
m * Cp * ΔT = Q (heat input)

And pick a rate (E.G. heat rate per minute, ΔT per minute).

You have a fixed mass of air in the room, it has a certain heat capacity and you apply heat at a certain rate, resulting in a rate of temperature change. That enough to run the calculation yourself?

The rate of temperature rise is way too fast for the heat loss through the walls to matter.
 
  • Like
  • Informative
Likes Lnewqban, Dullard and berkeman
  • #9
I just did a similar analysis for a customer who wanted me to build him a bitcoin mining container. 80KW in that space (without ventilation or refrigeration) will get really hot really fast (like: RUN!). 80KW is approx 23 Tons of heat load.
 
  • Like
  • Informative
Likes russ_watters and berkeman
  • #10
russ_watters said:
m * Cp * ΔT = Q (heat input)

And pick a rate (E.G. heat rate per minute, ΔT per minute).

You have a fixed mass of air in the room, it has a certain heat capacity and you apply heat at a certain rate, resulting in a rate of temperature change. That enough to run the calculation yourself?

The rate of temperature rise is way too fast for the heat loss through the walls to matter.
So ?
m= mass (volume of air in the space )3000 cu ft or 229 lbs ?
Cp=total heat capacity of air would I use 1 or .718 (Cv)
Delta T
I think so.. Let me take a shot.
My initial approach was to convert the 80 kW to Btuh (276,300) / 60 (minutes), div by 229 (lbs) = 20 deg F per minute. That seemed really high so here I am
 
  • #11
Additionally I would have a start point of 70 F and average ambient of 50 F, as we have locations across the country
 
  • #12
To figure the equilibrium temperature you need the surface area (I got 1700 ft2) and an estimate of the heat transfer coefficient from interior to ambient. With no forced convection (fans) the free convection coefficient would be limiting (unless the wall insulation is really good).

A typical free convection coefficient would be 1 or 2 Btu/hr-ft2-F. The the temperature drop across the wall would then be 80 to 160F (to transfer your 273,000 Btu/hr). So for 50F ambient, the interior would be 130 to 210F. That's about as rough an estimate as you're likely to get. No leakage, no equip shutoff, ...
 
  • #13
Sola said:
So ?
m= mass (volume of air in the space )3000 cu ft or 229 lbs ?
Cp=total heat capacity of air would I use 1 or .718 (Cv)
Delta T
I think so.. Let me take a shot.
My initial approach was to convert the 80 kW to Btuh (276,300) / 60 (minutes), div by 229 (lbs) = 20 deg F per minute. That seemed really high so here I am
Close, but I think you mixed units there. In English units, the heat capacity is about 0.24 (but you didn't use it?). So the answer is about 84F / min.

So, even worse but you were in the right OOM.
 
  • #14
gmax137 said:
To figure the equilibrium temperature you need the surface area (I got 1700 ft2) and an estimate of the heat transfer coefficient from interior to ambient. With no forced convection (fans) the free convection coefficient would be limiting (unless the wall insulation is really good).

A typical free convection coefficient would be 1 or 2 Btu/hr-ft2-F.
Wall insulation was provided and it's really good: R-19 = U of 0.053 BTU/hr/ft2-F. That's why convective heat transfer is usually ignored for walls for building envelope loads.
 
  • Informative
Likes gmax137
  • #15
Thanks @russ_watters -- I didn't know or didn't remember that the R "value" is the inverse of the U (with U in "imperial" units: Btu/hr ft2 F).
russ_watters said:
The short answer is infinity.
Yes, using that 0.05 Btu/hr ft2 F the equilibrium temperature works out to >3000 F. Showing it is silly to ignore the leakage etc. Rather, best to focus on the rate of rise and the given temperature limits, as you said in your original reply.
 
  • Like
Likes russ_watters
  • #16
russ_watters said:
Close, but I think you mixed units there. In English units, the heat capacity is about 0.24 (but you didn't use it?). So the answer is about 84F / min.

So, even worse but you were in the right OOM.
Russ,

Thank you, This is a great learning experience.
 
  • Like
Likes berkeman
  • #17
Russ,
Ok now the formula makes sense but I am stunned how much heat is generated and how quick. Still thinking I am missing some variable
 
  • #18
Sola said:
Ok now the formula makes sense but I am stunned how much heat is generated and how quick. Still thinking I am missing some variable
I think you're just expecting another variable to be there that isn't. Watts is watts and 80 kW is a lot of watts. Period. Every watt that the data center uses is converted to heat.

Maybe if you think about it in terms of a unit of heat you recognize. Like a hairdryer for example (on full). This is 55 hairdryers.

Or, I live in a 1500 sq ft townhouse in the northeast of the US and my central heating is generously sized. This data center is 4x the heat output of my house's heater in 1/5 the space. It's enough to run all of the air in the room through the heater, with it's 60F temperature rise, in 30 seconds.
 
Last edited:
  • Like
Likes Lnewqban and anorlunda
  • #19
Sola said:
Russ,
Ok now the formula makes sense but I am stunned how much heat is generated and how quick. Still thinking I am missing some variable
I would say that you can’t have so much generated heat within that space.
In my experience designing cooling for server rooms, it is safer and more practical to measure the actual amount of amps used by all the electronic equipment in the room in normal operation.
When the approach was adding up all the amps shown in the nameplate of each piece of equipment, the AC units resulted grossly oversized.

Another way to approach your problem could be to calculate how much heat your AC equipment is normally moving out of the room while keeping set temperature, based on its performance and capacity at normal working temperatures.
 
Last edited:
  • Like
Likes russ_watters

1. What is a temperature rate of rise table for air?

A temperature rate of rise table for air is a table that shows the change in temperature over a specific period of time. It is used to track the rate at which the temperature of air increases, and can be helpful in understanding the behavior of air in different environments.

2. Why is it important to create a temperature rate of rise table for air?

Creating a temperature rate of rise table for air is important because it allows us to better understand the behavior of air in different environments. This information can be useful in various fields such as meteorology, engineering, and environmental science.

3. How do you create a temperature rate of rise table for air?

To create a temperature rate of rise table for air, you will need to collect data on the temperature of air at different time intervals. This can be done using a thermometer or a data logger. Once you have the data, you can plot it on a graph and calculate the rate of change in temperature over time.

4. What factors can affect the temperature rate of rise for air?

The temperature rate of rise for air can be affected by various factors such as humidity, air pressure, wind speed, and the presence of other gases in the air. These factors can impact the rate at which air heats up or cools down.

5. How can a temperature rate of rise table for air be used in practical applications?

A temperature rate of rise table for air can be used in practical applications such as designing heating and cooling systems, predicting weather patterns, and studying the effects of air pollution. It can also be helpful in understanding the behavior of air in different environments and making informed decisions related to air quality and safety.

Similar threads

  • Mechanical Engineering
Replies
3
Views
959
  • Mechanical Engineering
Replies
3
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
10
Views
1K
  • Introductory Physics Homework Help
Replies
6
Views
1K
  • Engineering and Comp Sci Homework Help
2
Replies
41
Views
4K
  • Introductory Physics Homework Help
Replies
2
Views
648
Replies
3
Views
927
  • Electrical Engineering
Replies
6
Views
17K
  • Calculus and Beyond Homework Help
Replies
1
Views
696
Replies
8
Views
3K
Back
Top