Maximum current for 600V 16 AWG wire at 230V
  • Thread starter HomeExperiement
    Limits Wires
7 replies · 4K views · last reply
HomeExperiement
Hi!
I have wires that have printed 600V 16 AWG on it. I found this table: http://www.basicsofelectricalengineering.com/2017/07/basics-of-wire-gauge-and-awg-system.html . As I understood then long wires can be used to transmit 3.7 amps and short ones 22 amps? Also does it depend on voltages? Like if I have 230 Volts instead of 600 will the maximum amps still be 22 or will it go up when volts go down?
In my case I have short cable (20 cm at most). So that means that I can hook it electrical appliance that takes 230V*22A = 5060W of power?
Just asking to know if I understood it correctly or not.
You read correctly. But here there is a lot of comment on the huge difference between 'chassis' and 'transmission' admittable current. And a reference to a 'better' table - they quote 15 A, which seems more sensible to me.
For 5 kW I'd recommend a thicker wire, even for a short connection.
Ditto. They might as well go with 12 AWG in my opinion.
Tthe 3.7A rating for 'long' wires is to limit the voltage drop along the wire. Since the total wire resistance increase with length, a given current will cause a larger voltage drop in a long wire than a short one. For these cases, often the current rating is set for no more than a 5% voltage drop at the far end.
For 'short' wire runs the current rating is based on the maximum allowed temperature of the insulation, and whether the wire is out in the open, in a conduit, or in a multi-conductor cable. (Well, it also depends on the surrounding temperature, you don't want the wire hot enough that the wire itself oxidizes or corrodes due to the high temperature. :o:)
No. The voltage rating depends only on the insulation.
Cheers,
Tom
It had 120C written for temperature. Asked this because on my lamp I have 28W bulb limit and then the same manufacturer sells more expensive lamp that looks the same outside that has 85W limit. Since they visually look both same (same materials, etc) then the argument that other deals with the heat better somehow is ruled out. And that's why I looked what's inside to figure out of 36W LED or 40W LED is also ok with it. I personally find it interesting that lamp that is rated for 28W has such wires in it. Is there any logical reason behind it (like running it for long time needs some extra durability maybe?) or is it just that the factory took what was the cheapest to get?
What wires inside? Can you post pictures?
Use the UPLOAD button too post them.
Already put it together again. It was bit time consuming to open it so I wouldn't do it unless needed. The text was small and hard to read so photos wouldn't have much value.
Power dissipated in the cable and temperature reached is also relevant at times. The current ratings are based on where the cable actually runs (in free air or under roof insulation etc. ). We have all seen the figures on mains extension reels for permissible current when wound and when unwound.