My IEC Contactor Coil keeps overheating

  • Thread starter Thread starter epcole
  • Start date Start date
  • Tags Tags
    Coil Contactor
epcole
Messages
5
Reaction score
0
I have a 3ph IEC contactor with 120v coil voltage. For some reason, the coil starts heating up like crazy when I run it. I have 121v on L1, 120v on L2 and 121v on L3. I re-connected all the wiring to make sure there were no loose connections but still it keeps heating up when I energize the coil. What could be causing this?
 
Engineering news on Phys.org
How is the coil connected in the contactor? Is there a transformer using two of the phases to get the 120 volts? If you are connecting the coil across two of the phases directly, you'll need a 230 volt coil.
 
Have you measured the voltage across the coil itself? One voltmeter probe on each terminal of the coil.
 