Need some help -- Power Factor Correction for a Motor

Click For Summary
SUMMARY

The discussion focuses on power factor correction for a 12.5 kW motor operating at 440 V and 50 Hz, which has an efficiency of 85% and an initial power factor of 0.86 lagging. To meet the utility requirement of a power factor of 0.96 lagging, a capacitor must be added. The calculations reveal that the motor current is 42.85 A, the new supply current with the capacitor is 38.39 A, and the capacitor current is 11.12 A. The required capacitance to achieve the desired power factor is 80.44 μF, and the VAR rating of the capacitor is 4.89 kVAR.

PREREQUISITES
  • Understanding of power factor and its significance in electrical systems
  • Knowledge of AC circuit analysis, including phasor representation
  • Familiarity with capacitive reactance and its calculation
  • Basic proficiency in using trigonometric functions for electrical calculations
NEXT STEPS
  • Research the principles of power factor correction using capacitors
  • Learn about the calculation of reactive power (VAR) in AC circuits
  • Study the effects of motor efficiency on power consumption and performance
  • Explore the implications of power factor on energy costs and utility regulations
USEFUL FOR

Electrical engineers, motor control specialists, and anyone involved in optimizing motor performance and compliance with utility power factor requirements.

Kasim
Messages
23
Reaction score
0
< Mentor Note -- thread moved to HH from the technical engineering forums, so no HH Template is shown >[/color]

Hi there. I am wondering if someone can help me.. Below is a question and answer, I need help with IV . Where does the 0.51 and 0.28 come from? I've tried cos and sin and thitha but doesn't give me correct number
 

Attachments

  • image.jpg
    image.jpg
    34.3 KB · Views: 558
  • image.jpg
    image.jpg
    30.3 KB · Views: 577
Last edited by a moderator:
Engineering news on Phys.org
Seriously? You ask people for help by posting a tiny unreadable image of something
 
Cant you enlarge it by opening the actual picture? Sorry but I am new here..
 
Kasim said:
Cant you enlarge it by opening the actual picture? Sorry but I am new here..
The "enlargement" is tiny

The issue is not about this forum it's about the size of the image you posted.
 
A 12.5 kW motor is to be powered from a 440 V, 50 Hz supply. Data from

factory testing indicates the motor has an operating efficiency of 85% and

that the power factor is 0.86 lagging. The power utility feeding the factory

requires that the motor’s power factor is 0.96 lagging or better.(i) Explain how the addition of a capacitor to the motor would give the required power factor.

(ii) Determine the motor current in the original configuration.

(iii) Determine the supply current with the capacitor in place.

(iv) Determine the current flowing in the capacitor.

(v) Calculate the value of the capacitance which must be added to give the

desired performance

(vi) Determine the ‘VAr’ rating of the additional component.
 
(ii) Efficiency of motor = Power output/power input,

ð 0.85 = 12500/power input

ð power input = 14706 WPower input = VImcosФ = (440)(I)(0.86)

ð I am = 14706/(440)(0.78) =

ð I am = 42.85 A

The motor current I am is 42.85 A(iii) The current in the parallel capacitor leads the supply voltage by 90°.

The phasor sum of the original current I am and the capacitor current Ic must be such that the supply current Is lags by 0.96 or better.Resistive component of motor current = I am cosФ = (42.85)(0.86) = 36.85 AResistive component of new supply current = Is cosФ’ = Is (0.96) = 0.96 Is AAs resistive component of current does not change => 36.85 = 0.96 Is

=> New supply current, Is = 38.39 A(iv) Reactive component of motor current = I am sinФ = (42.85)(0.51) = 21.87 AReactive component of new supply current = Is sinФ’ = (38.39)(0.28) = 10.75 AAs reactive component of current in capacitor is balance of current => Ic = 21.87 – 10.75

=> Capacitor current, Ic = 11.12 A(v) Capacitor current, Ic = V/Xc => Xc = V/Icð 1/(2πfC) = V/Ic

ð C = Ic /(2πfV) = 11.12/(2π(50)(440))

ð C = 1.26 x 10-4 = 80.44 μF
(vi) The var rating of the capacitor = VIc = (440)(11.12) = 4.89 kvar
 
Old PF is cosФ = 0.86 = arccos(0.86) = 30.68° so the sin of 30.68° degrees is sin (30.68°) = 0.51
Since the new PF must be equal to cosФ = 0.96 = arccos(0.96) = 16.26° so the sin of 16.26° is 0.28.
 
Last edited:
Thank you
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 55 ·
2
Replies
55
Views
9K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 2 ·
Replies
2
Views
3K
Replies
11
Views
4K
Replies
11
Views
2K
  • · Replies 32 ·
2
Replies
32
Views
7K
  • · Replies 2 ·
Replies
2
Views
1K
Replies
61
Views
9K
  • · Replies 15 ·
Replies
15
Views
4K