Power Factor Correction: Capacitor Bank

  • #31
Hesch said:
It can be mechanically loaded at the same time. The generator at your utility is (negative) mechanically loaded while producing kVAr's.

Thanks! I found a great article describing the use of a synchronous motor in a process plant here in case it helps anyone else:

https://www.site.uottawa.ca/~rhabash/project-synversusinduction.pdf
 
Engineering news on Phys.org
  • #32
Hesch said:
It can be mechanically loaded at the same time. The generator at your utility is (negative) mechanically loaded while producing kVAr's.

Out of curiosity, are there practical systems that have a natural leading power factor & hence cannot be corrected by a capacitor bank?
 
  • #33
rollingstein said:
Out of curiosity, are there practical systems that have a natural leading power factor & hence cannot be corrected by a capacitor bank?

Power transmission lines, especially underground power cables. We correct those with shunt reactors.
 