Phase and Line current in 3 phase circuits

5 replies · 2K views · last reply
Cocoleia
Messages
293
Reaction score
4

Homework Statement


Circuit diagram of a balanced three-phase supply feeding a delta-connected motor load through a cable with series impedance ZTL in each phase line, with load impedance ZL in each delta branch.

I need to first find phase current in the load and line current from the supply

Homework Equations

The Attempt at a Solution


Handwritten notes converting a delta-connected three-phase load to an equivalent star, with a one-phase equivalent circuit below showing a 240 V source and impedance ZTL + Z/3, followed by the line current calculation IL = 7460 / (√3 × 240 × 0.85) = 211.13 A.

I thought it would be easier to work with a star because then the Ztl would be in series with it... I am not sure how to find the current but my best guess was using this power equation. For the second current, I am not sure how to proceed.
 
Attachments
  • Circuit diagram of a balanced three-phase supply feeding a delta-connected motor load through a cable with series impedance ZTL in each phase line, with load impedance ZL in each delta branch.
    upload_2017-10-30_13-2-55.png
    85.1 KB · Views: 890
  • Handwritten notes converting a delta-connected three-phase load to an equivalent star, with a one-phase equivalent circuit below showing a 240 V source and impedance ZTL + Z/3, followed by the line current calculation IL = 7460 / (√3 × 240 × 0.85) = 211.13 A.
    upload_2017-10-30_13-9-8.png
    92.9 KB · Views: 794
You don't need to convert it in star. Keep it as it is and find the line current from the power equation.

Your attempt is unclear.
What is the active power input to the motor?
 
cnh1995 said:
You don't need to convert it in star. Keep it as it is and find the line current from the power equation.

Your attempt is unclear.
What is the active power input to the motor?
Can I use the same power equation that I had used ?

I guess the power input is 74600 W
 
Cocoleia said:
Can I use the same power equation that I had used
Yes.
Cocoleia said:
I guess the power input is 74600 W
What about efficiency?
 
cnh1995 said:
Yes.

What about efficiency?
If it is only 90% then only 67140 W. I use this as P.

WIll V be 240/sqrt(3)
 
Cocoleia said:
If it is only 90% then only 67140 W. I use this as P.
How can the input be less than the output? Use the efficiency correctly.
Cocoleia said:
WIll V be 240/sqrt(3)
No.