Power loss in transmission lines problem

Click For Summary

Homework Help Overview

The problem involves calculating power loss in transmission lines when delivering electricity at different voltages. It focuses on a scenario where a power station delivers 890 kW at 12 kV and examines the impact of increasing the voltage to 50 kV on power loss due to resistance in the wires.

Discussion Character

  • Conceptual clarification, Assumption checking, Mathematical reasoning

Approaches and Questions Raised

  • Participants discuss the application of Ohm's Law and the relationship between voltage, current, and power loss. Questions arise regarding why Ohm's Law cannot be directly applied to find current in this context, and the necessity of using power equations instead. Some participants explore the implications of voltage drop across the transmission line and the definitions of terminals in AC systems.

Discussion Status

The discussion is ongoing, with participants providing insights into the relationship between voltage and current, as well as the implications for power loss. Some have expressed improved understanding of the concepts involved, while others continue to seek clarification on specific aspects of the problem.

Contextual Notes

There is a focus on the assumptions made regarding the load and the nature of the transmission line. Participants note the importance of understanding voltage drops and the definitions of terminals in the context of AC transmission systems.

IniquiTrance
Messages
185
Reaction score
0

Homework Statement



A power station delivers 890 kW of power at 12 kV to a factory through wires with total resistance 5.0 \Omega.

How much less power is wasted if the electricity is delivered at 50 kV rather than 12 kV?


Homework Equations



eq-1) P = IV
eq-2) P = I2R

Ohm's Law: V = IR

The Attempt at a Solution



I know the problem can be solved by solving for the current value in each case from eq-1, and plugging it into eq-2 to calculate power loss.

My real question is why can't we apply Ohm's law to calculate I, and then plug it into eq-2? Why must we use eq-1 to get the current? Doesn't Ohm's law apply for all ohmic conductors, and since we have both the resistance and voltage of and across the conductor, can't we get the current that way?

Thanks!
 
Last edited:
Physics news on Phys.org
If you apply Ohm's Law to the line resistance, you would need to know the voltage drop in the line.

If you apply it to the load plus the line, you would have to use the combined resistance of line and load. You could use the power formula to find the load resistance, then use Ohm's Law to find the current.
 
Delphi51 said:
If you apply Ohm's Law to the line resistance, you would need to know the voltage drop in the line.

If you apply it to the load plus the line, you would have to use the combined resistance of line and load. You could use the power formula to find the load resistance, then use Ohm's Law to find the current.

Thanks for the reply!

So when you have a 12kV transmission line, what is the 12 kV drop across? The negative terminal is obviously at the powerplant, the positive, after passing through the load, back at the powerplant?
 
A power station delivers 890 kW of power at 12 kV to a factory
The wording is careful, as it should be, to make it clear that the potential at the load is 12 Kv. It will have to be larger at the source to make up for the loss in the line resistance.

Virtually all transmission lines are AC, so there is no negative or positive terminal.
 
IniquiTrance said:
so when you have a 12kV transmission line, what is the 12 kV drop across?
It's between the output of the power line and ground - and in an ideal world is the same as the difference between the input to the powerline and ground.

This confuses everybody who first sees this question - do a search here and you will see dozens of threads on it!
 
Thank you!

I have a much better understanding of the concept now.
 
IniquiTrance said:
Thanks for the reply!

So when you have a 12kV transmission line, what is the 12 kV drop across? The negative terminal is obviously at the powerplant, the positive, after passing through the load, back at the powerplant?
The voltage is the potential difference with no load. It does not matter what the load is. The question does not ask how much power is lost. It just asks for the relative power loss at these two different line voltages. All you have to know is that for a given load, if the 12Kv line has current I the 50Kv line the current will be 12I/50. The power loss across the line will be I^2R where R is 5 ohms so you can easily calculate the relative line losses.

AM
 
Last edited:
KW KV R I=KW/KV Loss=I*I*R Loss reduction
890 12 5 74.17 27503.47
890 50 5 17.8 1584.2 25919.27
PF=1
 
KW KV R I=KW/KV Loss=I*I*R Loss reduction
890 12 5 74.17 27503.47
890 50 5 17.8 1584.2 25919.27
PF=1


890 kw 12kv current= 890/12=74.17 Amp assuption pf=1, loss= I*I*R=27503 W
890kw, 50kv, current=890/50=17.8 amp, loss= 1584.2 w,
loss reduction= 25919.27 w,
As the voltage increases, current decreases for same power. current decreases loss also decreases. current has a squred relation with loss.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 9 ·
Replies
9
Views
2K
Replies
6
Views
2K
  • · Replies 20 ·
Replies
20
Views
12K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 16 ·
Replies
16
Views
2K
  • · Replies 7 ·
Replies
7
Views
8K
  • · Replies 12 ·
Replies
12
Views
3K
  • · Replies 14 ·
Replies
14
Views
4K