Relay Control of Induction Motors

  • Thread starter Thread starter neilparker62
  • Start date Start date
Click For Summary
SUMMARY

The discussion focuses on the relay control circuit for driving forward and reverse terminals of 230 V AC, 0.5 HP induction motors. The circuit employs electrical interlocks to prevent simultaneous activation of both forward and reverse terminals. Key components include SMCJ440CA bidirectional TVS diodes for voltage transient suppression and 500 mA fast-blow fuses rated for 600 V AC. Recommendations emphasize the importance of managing transient voltages to avoid silent failures and potential EMF interference.

PREREQUISITES
  • Understanding of relay control circuits and electrical interlocks
  • Knowledge of transient voltage suppression techniques, including R/C snubber circuits and TVS diodes
  • Familiarity with motor specifications, particularly induction motors
  • Basic principles of circuit protection, including fuse ratings and configurations
NEXT STEPS
  • Research the implementation of R/C snubber circuits for induction motors
  • Study the characteristics and applications of SMCJ440CA TVS diodes
  • Learn about the effects of high current pulses on motor operation and protection strategies
  • Explore methods for enhancing circuit impedance to mitigate transient voltage issues
USEFUL FOR

Electrical engineers, automation specialists, and technicians involved in motor control systems and transient voltage management will benefit from this discussion.

neilparker62
Science Advisor
Homework Helper
Education Advisor
Insights Author
Messages
1,200
Reaction score
708
Would like to check if the following relay control circuit work for driving forward and reverse terminals of a gate motor will work? Relays are connected for 'electrical interlock' meaning it should not be possible for both fwd and rvs terminals to be activated at the same time. Physically that is implemented as a jumper wire between the relay commons. If the fwd n/o is closed, the right hand motor will be connected and vv for the reverse. If both fwd and rvs are somehow activated at the same time, both n/c s will be open and there will be no connection to either terminal.

What is the "conventional wisdom" on dealing with transients from small induction motors such as these ? Are we still using standard R/C snubber circuits or are the bi-directional TVS diodes a better option. Or maybe even both ?

Design notes / recommendations on fuses and TVS diodes below are from Chatgpt.


1746680869129.webp


Design Notes
Motors: 230 V AC, 0.5 HP induction motors.
Motor windings: 10 ohm resistance, 90 mH inductance.
TVS Diodes: SMCJ440CA — bidirectional, 440 V clamping.
Fuses: 500 mA fast-blow, 600 V AC rated — placed in series with each TVS diode.
Purpose: Suppress voltage transients across motor windings during switching by relays.
 
Engineering news on Phys.org
The first thing I noticed is that if you blow one of those fuses, the system will still operate, but the voltage transients will be entirely unsuppressed. You will have a silent failure. On the other hand, this motor looks like it's 1/4HP or less. So those transients are more likely to show up as EMF interference than actual circuit damage.

The second thing is that supposedly, you are trying to protecting other devices that share the same power source as this motor - or perhaps suppress EMF. And you are depending on the impedance/resistance of the power lines to this motor system to make sure that most of the transient power is absorbed through the diodes and not transmitted. This may or may not be good enough. If it isn't, you may want to loop the live power line just before it reaches the switches to provide a bit more impedance.

The third thing: I know you're using break before make from your discussion. But I can't tell whether those extra lines in your schematic are intended to show that.
 
Last edited:
  • Informative
Likes   Reactions: neilparker62
Where is the phase shift capacitor that generates the rotating field?

If you switch from forward to reverse without waiting for the armature to stop, you will generate a high current pulse, and a physical shock to the motor.
 
  • Informative
Likes   Reactions: neilparker62
.Scott said:
The third thing: I know you're using break before make from your discussion. But I can't tell whether those extra lines in your schematic are intended to show that.
If you mean these:

1746721802759.webp


They are the normally closed switched on the relays. Current paths to the respective motors are as shown below. If both relays are activated at the same time , both normally closed switches will be open. So the red and green current paths are mutually exclusive. In effect the relay connections are implementing an XOR gate.

1746722749184.webp
 
Baluncore said:
Where is the phase shift capacitor that generates the rotating field?

If you switch from forward to reverse without waiting for the armature to stop, you will generate a high current pulse, and a physical shock to the motor.
The relays are driven from program logic. A motor opening a gate will be stopped for a period before the reverse motor/winding is activated to close the gate.
 
.Scott said:
The first thing I noticed is that if you blow one of those fuses, the system will still operate, but the voltage transients will be entirely unsuppressed. You will have a silent failure. On the other hand, this motor looks like it's 1/4HP or less. So those transients are more likely to show up as EMF interference than actual circuit damage.

The second thing is that supposedly, you are trying to protecting other devices that share the same power source as this motor - or perhaps suppress EMF. And you are depending on the impedance/resistance of the power lines to this motor system to make sure that most of the transient power is absorbed through the diodes and not transmitted. This may or may not be good enough. If it isn't, you may want to loop the live power line just before it reaches the switches to provide a bit more impedance.
Noted - re silent failure. Thanks for pointing it out. We'll have to figure out how to deal with that situation.

Re protection - no other devices are connected. We are just trying to deal with arcing across the relay contacts caused by high voltage transient spikes when the motors are turned off/on.
 

Similar threads

  • · Replies 25 ·
Replies
25
Views
5K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 10 ·
Replies
10
Views
5K
Replies
3
Views
3K
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 2 ·
Replies
2
Views
3K
Replies
5
Views
29K