AI Thread Summary
The relay control circuit for driving the forward and reverse terminals of a gate motor is designed to prevent simultaneous activation through electrical interlock, using normally closed switches to ensure mutual exclusivity. Concerns were raised about handling voltage transients from small induction motors, with discussions on the effectiveness of R/C snubber circuits versus bi-directional TVS diodes for transient suppression. It was noted that if a fuse blows, the system continues to operate but without transient suppression, leading to potential silent failures. The design also considers the need to manage arcing across relay contacts due to high voltage spikes when switching the motors on and off. Overall, the focus is on ensuring reliable operation while minimizing electrical interference and protecting the system from transient damage.
neilparker62
Science Advisor
Homework Helper
Insights Author
Messages
1,191
Reaction score
683
Would like to check if the following relay control circuit work for driving forward and reverse terminals of a gate motor will work? Relays are connected for 'electrical interlock' meaning it should not be possible for both fwd and rvs terminals to be activated at the same time. Physically that is implemented as a jumper wire between the relay commons. If the fwd n/o is closed, the right hand motor will be connected and vv for the reverse. If both fwd and rvs are somehow activated at the same time, both n/c s will be open and there will be no connection to either terminal.

What is the "conventional wisdom" on dealing with transients from small induction motors such as these ? Are we still using standard R/C snubber circuits or are the bi-directional TVS diodes a better option. Or maybe even both ?

Design notes / recommendations on fuses and TVS diodes below are from Chatgpt.


1746680869129.webp


Design Notes
Motors: 230 V AC, 0.5 HP induction motors.
Motor windings: 10 ohm resistance, 90 mH inductance.
TVS Diodes: SMCJ440CA — bidirectional, 440 V clamping.
Fuses: 500 mA fast-blow, 600 V AC rated — placed in series with each TVS diode.
Purpose: Suppress voltage transients across motor windings during switching by relays.
 
Engineering news on Phys.org
The first thing I noticed is that if you blow one of those fuses, the system will still operate, but the voltage transients will be entirely unsuppressed. You will have a silent failure. On the other hand, this motor looks like it's 1/4HP or less. So those transients are more likely to show up as EMF interference than actual circuit damage.

The second thing is that supposedly, you are trying to protecting other devices that share the same power source as this motor - or perhaps suppress EMF. And you are depending on the impedance/resistance of the power lines to this motor system to make sure that most of the transient power is absorbed through the diodes and not transmitted. This may or may not be good enough. If it isn't, you may want to loop the live power line just before it reaches the switches to provide a bit more impedance.

The third thing: I know you're using break before make from your discussion. But I can't tell whether those extra lines in your schematic are intended to show that.
 
Last edited:
  • Informative
Likes neilparker62
Where is the phase shift capacitor that generates the rotating field?

If you switch from forward to reverse without waiting for the armature to stop, you will generate a high current pulse, and a physical shock to the motor.
 
  • Informative
Likes neilparker62
.Scott said:
The third thing: I know you're using break before make from your discussion. But I can't tell whether those extra lines in your schematic are intended to show that.
If you mean these:

1746721802759.webp


They are the normally closed switched on the relays. Current paths to the respective motors are as shown below. If both relays are activated at the same time , both normally closed switches will be open. So the red and green current paths are mutually exclusive. In effect the relay connections are implementing an XOR gate.

1746722749184.webp
 
Baluncore said:
Where is the phase shift capacitor that generates the rotating field?

If you switch from forward to reverse without waiting for the armature to stop, you will generate a high current pulse, and a physical shock to the motor.
The relays are driven from program logic. A motor opening a gate will be stopped for a period before the reverse motor/winding is activated to close the gate.
 
.Scott said:
The first thing I noticed is that if you blow one of those fuses, the system will still operate, but the voltage transients will be entirely unsuppressed. You will have a silent failure. On the other hand, this motor looks like it's 1/4HP or less. So those transients are more likely to show up as EMF interference than actual circuit damage.

The second thing is that supposedly, you are trying to protecting other devices that share the same power source as this motor - or perhaps suppress EMF. And you are depending on the impedance/resistance of the power lines to this motor system to make sure that most of the transient power is absorbed through the diodes and not transmitted. This may or may not be good enough. If it isn't, you may want to loop the live power line just before it reaches the switches to provide a bit more impedance.
Noted - re silent failure. Thanks for pointing it out. We'll have to figure out how to deal with that situation.

Re protection - no other devices are connected. We are just trying to deal with arcing across the relay contacts caused by high voltage transient spikes when the motors are turned off/on.
 
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top