SE 704 ground fault detector causing nuisance trips on 1900 HP motor startup

  • Thread starter Thread starter dorymill
  • Start date Start date
  • Tags Tags
    Detection Earth
Join the discussion
Registration is free. Start your own thread to ask a follow-up.
1 reply · 2K views
dorymill
Messages
1
Reaction score
0
Anyone ever install SE 704 Earth Detection (ground fault system)?
4160V 3 phase
1900 HP motor
detection level 100 Ma
resistance grounded supply max fault current 1 amp.

Nuisance tripping when starting the motor.
 
Engineering news on Phys.org
what's KVA code on motor?

is starting current within spec of that Startco gizmo's CTs?

Wye connection? remember third harmonic all returns through neutral...CT needs to wrap it too.
any idea of motor windings' capacitance to earth?

examine CT output with a scope during a start, if it's 180 hz you have an interesting situation.

just guesses