Which Earth Fault Relay Setting Is Correct for a 20 KV Zig-Zag Transformer?

Click For Summary
The discussion centers on determining the correct primary current setting for an Earth fault relay in a 20 KV zig-zag transformer. The initial setting of 8.67 A is based on the transformer's continuous rating, but calculations suggest a higher setting of 12.5 A may be more appropriate due to the unique characteristics of zig-zag transformers. It is noted that zig-zag transformers operate with less voltage per leg, leading to a lower continuous rating of 5 A and a neutral current rating of 15 A. The consensus leans towards selecting 12.5 A for optimal performance during line-to-ground faults. Understanding the differences in transformer types is crucial for accurate fault relay settings.
m.s.j
Messages
212
Reaction score
1
A 20 KV switchgear have equipped with one zig-zag earthing transformer. As you know,
A grounding transformer must handle the unbalanced load on the circuit as well as the duty during line-to-ground faults. If the circuit has a lot of unbalance load, then we must concern the continuous rating of transformer in addition of its short time withstand currents. The continuous rating power of mentioned grounding transformer is 100 KVA.
The primary current setting of related Earth fault relay that installed in neutral point of E.T. is 8 Amp.
This set point current is chosen in base of E.T. continuous rating current and following calculations:

It =100/ (20x1.73) = 2.89 A

In= 3x It = 8.67 A

But the Earth fault current calculation and analyses dictate other primary current setting (12.5 A).

Which one current setting is correct? Which one do you choose?



--------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Engineering news on Phys.org
I would say 8.67 A since you are concerned with the phase to phase loading.
 
Unfortunately, nowadays with our world information transmission system (internet), we usually neglect the basic conceptions and deep thinking about new problems.
With more deep thinking, we can find that the mentioned evident equation (S = 1.73 VI) is not correct for zig-zag earthing transformers.
Indeed, each leg of a grounding transformer carries one-third of the neutral current and has line-to-neutral voltage. So in a grounded wye - delta transformer, the total power rating including all three phases is the neutral current times
The line-to-ground voltage:
S= 1.73 VI
But a zig-zag transformer is more efficient than a grounded wye - delta transformer.
In a zig-zag, each winding has less than the line-to-ground voltage,
by a factor of 1.73, so the bank may be rated lower:
S = 1.73/1.7.3 VI = VI
Therefore, the continuous rating current of E/T is 5 A and rating neutral current is 15A, and we can choose 12.5A as correct Earth fault primary current setting.


--------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Thread 'I thought it was only Amazon that sold unsafe junk'
I grabbed an under cabinet LED light today at a big box store. Nothing special. 18 inches in length and made to plug several lights together. Here is a pic of the power cord: The drawing on the box led me to believe that it would accept a standard IEC cord which surprised me. But it's a variation of it. I didn't try it, but I would assume you could plug a standard IEC cord into this and have a double male cord AKA suicide cord. And to boot, it's likely going to reverse the hot and...

Similar threads

  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 3 ·
Replies
3
Views
10K
  • · Replies 1 ·
Replies
1
Views
3K