Restricted Earth Fault Trip due to inrush current

  • Thread starter Sreelathag
  • Start date
  • #1

Main Question or Discussion Point

Hello I need some help. In our 50MVA, 132/33 kV star/star transformer, at the time of charging from HV side, the transformer trips on REF (restricted earth fault) due to magnetizing inrush current.

Rated current: 218.7 Amp
Line CT ratio: 800/400/200/1 Amp
tap selected 400/1 Amp
setting on MJT 36 Numerical relay.
Earth fault = 0.2 In
TMF = 0.15 In
Inrush current in three phases is:
Ia = 0.42
Ib = 0.05
Ic = 0.51

EF current in neutral = 0.58 In
Relay operating time = 0.94 s

Since, inrush dyeing time > 2.5 s, the relay trips.

At TMS 0.3, the relay operating time = 1.89s
At TMS 0.4, the relay operating time = 2.52s

Customer advised to change TMS to 0.4 (2.52s), he does not agree since,

i) It will affect his normal earth fault protection time of 0.94s which is not desirable.
ii) Other similar transformer in the same substation does not give the problem.

The transformer is made with step lap core construction using Hi-B grade material using 1.6 tesla flux density.

Can anyone help me analyze and suggest what to do?

Thanks & Regards
G.Sreelatha
Asst. Manager
Vijai Electricals Limited
Hyderabad.
 

Answers and Replies

  • #2
217
1
Last edited by a moderator:

Related Threads on Restricted Earth Fault Trip due to inrush current

Replies
3
Views
15K
  • Last Post
Replies
21
Views
7K
  • Last Post
Replies
3
Views
3K
  • Last Post
Replies
24
Views
8K
Replies
14
Views
2K
  • Last Post
Replies
3
Views
9K
Replies
12
Views
4K
  • Last Post
2
Replies
31
Views
3K
Replies
15
Views
2K
  • Last Post
Replies
3
Views
7K
Top