Single machine-Infinite bar (SMIB)

  • Thread starter Thread starter DianeS
  • Start date Start date
Click For Summary

Discussion Overview

The discussion revolves around obtaining the external reactance for a Single Machine-Infinite Bar (SMIB) model in the context of small-signal studies. Participants explore methods for determining this reactance, particularly through power flow simulation software, and discuss the implications of different short circuit types on Thevenin equivalent calculations.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant seeks to determine the external reactance connected to the infinite bar and questions whether it can be obtained through power flow simulation software.
  • Another participant shares that the external reactance depends on the number of operational lines and connected units, recalling a per-unit value of approximately 0.013.
  • A participant mentions using DigSilent for simulations and suggests that running a three-phase short circuit can yield Thevenin equivalent values for positive sequence impedance.
  • There is a discussion about the types of short circuits that can be used to find the Thevenin equivalent, with one participant questioning whether a three-phase or one-phase short circuit is more appropriate.
  • Concerns are raised about whether it is sufficient to find only the positive sequence impedance when using a three-phase short circuit for the SMIB equivalent.
  • Another participant expresses uncertainty about which short circuit current to use for calculating the Thevenin impedance, highlighting the distinction between one-phase and three-phase scenarios.

Areas of Agreement / Disagreement

Participants express varying opinions on the appropriate methods for determining Thevenin equivalent values and the types of short circuits to use, indicating that multiple competing views remain and the discussion is unresolved.

Contextual Notes

Participants note that the external reactance values may vary based on system configurations and operational conditions. There is also mention of the negligible resistance in large systems, suggesting a focus on reactance in analyses.

Who May Find This Useful

This discussion may be of interest to electrical engineers, power system analysts, and students engaged in power system modeling and analysis.

DianeS
Messages
3
Reaction score
0
Greetings ladies and gentleman.
Well I'm trying to do some small-signal studies, and I'm familiar with the deMello-Concordia linearized model. As far as i know all the constants used in that model (K1-K6) depend on the system, and so they change as the system changes too. I have a large system with several synchronous machines and i want to obtain the SMIB model for one of those machines. So how do i obtain the external reactance connected to the infinite bar, representing the transmission line? I know this reactance corresponds to the Thevenin equivalent, but is there a way to obtain this value by using a power flow simulation software?

Or is it a good approach to assume this value to be zero?
Thanks a bunch
 
Engineering news on Phys.org
""So how do i obtain the external reactance connected to the infinite bar, representing the transmission line? I know this reactance corresponds to the Thevenin equivalent, but is there a way to obtain this value by using a power flow simulation software?""

what an interesting question.

I wish i had an answer for you.
In the utility where i worked we had a whole department dedicated to calculating just such things, and we just asked them. But the number depends on how many lines are in operation and how many units are connected.

I seem to recall they gave us per-unit numbers like 0.013 so i wouldn't use zero. It was however a lot less than the stepup transformer impedance.

Here's a link i found with some formulas, perhas you could approximate a reasonable line to get your simulation running then tweak it with real numbers from your utility's system people.

www.powerworld.com/Document%20Library/version.../TransCalcHelp.pdf[/URL]

"Power System Analysis" by Charles M Gross is a practical textbook.
Dr Gross was my instructor for some undergrad courses and he has a God-given talent for clear explanations. I saw his book in the bookcases of many engineers in that department i mentioned, they all spoke highly of it -- so ask among your colleagues, if you find a copy i think it'll have some practical examples worked out that are quite similar to your question.

Sorry I'm not an expert.

old jim
 
Last edited by a moderator:
Well thank you Jim! I've been using DigSilent for this purpose, and i guess i'll just have to trust in it. By simulating a three phase short circuit, i can obtain the values for R and X, which i asume are Thevenin equivalent for positive sequence.
 
for what little this is worth --

our big steam turbine plant had natural frequency against system of ~ 1 hz
largely due to 17% main tansformer
i think that is typical

it also had main shaft resonance of 7 hz
so that was a frequency to avoid like the plague in anything connected to it.

we overdamped voltage regulator to calm system troubles (2/3 hz divergent oscillations) that were solved initially by power system stabilizers , finally by stouter transmission lines.

wish i could be more help.

good luck with your studies -
that is a field i watched "through the fence" like Charly in 'Flowers for Algernon'.

old jim
 
Well thanks Jim, i appreciate your help.
I'm now trying to find out which type of short circuit i should use to find the thevenin equivalent, because I've found that you can find a 3-phase or1-phase Thevenin equivalent and I'm not so sure if this is true.

By running a 1-phase short circuit i would find impedances in all 3 sequences. Is it enough to find only the positive sequence impedance by running a 3-phase short circuit in my software for the SMIB equivalent??

I'm also aware that for big systems Rthev is negligible so i can only consider Xthev in y analysis, and that this value is the inverse of the imaginary part of the short circuit current. But again which short circuit current? 1-phase or 3-phase?

Thanks again. Would like to get more people involved too. Don't be shy :P
 
""Is it enough to find only the positive sequence impedance by running a 3-phase short circuit in my software for the SMIB equivalent??
""

I wish i could answer that question.
My intuition says use the three phase
the power system guys i used to observe in 1980's were excited about new relay schemes that could interrupt one phase at a time for single line faults

so i would think your small signal studies would be focused on balanced three phase.
but that is a guess.

our power system oscillations were during steady state operation not fault induced.
came from interactions of rotating inertia, system impedance and voltage regulators.


Is there a genuine power system engineer in the house ?


Dr Gross - are you out there?
old jim hardy - UMR '69, your student for AC machinery
 

Similar threads

  • · Replies 3 ·
Replies
3
Views
6K
  • · Replies 3 ·
Replies
3
Views
16K
  • · Replies 13 ·
Replies
13
Views
4K
  • · Replies 35 ·
2
Replies
35
Views
11K
  • · Replies 2 ·
Replies
2
Views
613
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 5 ·
Replies
5
Views
7K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 13 ·
Replies
13
Views
10K