Solving Flow Process Problem: PCB Dissapates 20W

  • Thread starter Thread starter Lancelot59
  • Start date Start date
  • Tags Tags
    Flow Process
Click For Summary
The discussion revolves around calculating the average temperature of air exiting a hollow PCB that dissipates 20W of heat. The initial approach involved simplifying the second law of thermodynamics for a steady-state scenario, focusing on energy balance without kinetic or potential energy effects. The user confirmed that the PCB acts as a vessel imparting heat to the air, and they successfully derived the mass flow rate using the ideal gas law. They also noted the importance of ensuring unit consistency in calculations. Ultimately, the user resolved their confusion and expressed gratitude for the guidance received.
Lancelot59
Messages
640
Reaction score
1
I'm attempting to solve the following problem:

A hollow PCB dissapates 20W into air which enteres at 32 degrees C, 1atm, and a volume flow rate of 800cm3/s. Find the average temperature the air leaves at.

I started by first simplifying the second law energy balance equation:

\frac{dE}{dt}+\Sigma_{out}m^{\cdot}_{e}(h_{e}+ \frac{1}{2} v_{e}^{2}+gz_{e})- \Sigma_{in}m^{\cdot}_{i}(h_{i}+\frac{1}{2}v_{i}^{2}+gz_{i})=Q^{\cdot}-W^{\cdot}

Since this is a steady state problem, energy rate of change is 0, and there are no effects from kinetic or potential energy. There is also no work being done, and the mass flow rates are equal. So I believe this simplifies to:

m^{\cdot}((h_{e})-h_{i})=Q^{\cdot}

From here I'm not sure what I can do to solve the problem. Was this the correct approach to begin with?
 
Physics news on Phys.org
Update: I tried running the ideal gas law using the volume flow rate, and after sorting the units I believe I can get the mass flow rate from that. What to do after that however, I'm not sure.
 
Last edited:
What is a PCB? Can it be considered a vessel of some sort that is imparting the air flow with 20 watts? If it is, you have the correct equation. Q is energy per unit time. If you assume KE changes are negligible and express enthalpy as specific heat times temperature, the solution is at hand. Be sure your units agree when plugging in the numbers.
 
In this instance PCB = Printed Circuit Board. I did manage to sort everything out. Thanks.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
Replies
22
Views
3K
  • · Replies 12 ·
Replies
12
Views
3K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
Replies
22
Views
4K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 5 ·
Replies
5
Views
634