Steam Condenser Not Working: Pressure & Temperature Issues

Click For Summary
SUMMARY

The steam condenser is underperforming, with a condensate drain temperature of 38 deg C instead of the expected 50 deg C, and a pressure of 0.25 bar abs rather than 0.2 bar. This indicates potential issues with steam flow rates and the presence of non-condensable gases. A heat balance comparison with other condensers is essential to identify discrepancies, particularly in upstream drains and air ingress. Additionally, the design of the condenser, including the use of trays for condensate routing, plays a critical role in heat transfer efficiency.

PREREQUISITES
  • Understanding of steam condenser operation and thermodynamics
  • Familiarity with pressure and temperature measurement in steam systems
  • Knowledge of heat balance calculations in thermal systems
  • Experience with troubleshooting steam systems and identifying non-condensable gases
NEXT STEPS
  • Conduct a heat balance analysis on the steam condenser and compare it with other units
  • Investigate upstream drain flow rates and their impact on condenser performance
  • Examine air ingress levels and their effects on heat transfer efficiency
  • Review the design and functionality of trays within the condenser for optimal condensate routing
USEFUL FOR

Engineers, maintenance personnel, and operators involved in steam system management, particularly those focused on optimizing steam condenser performance and troubleshooting related issues.

Nirmsing1411
Messages
1
Reaction score
0
The condensate drain from a steam condenser is expected to be about 50 deg C. It's only 38 deg C or so. There's a mix of steam and non condensable gases coming into the condenser. Its pressure seems slightly higher, being about 0.25 bar abs instead of 0.2 bar. What does it indicate? Also, no significant difference in cooling water flow and the inlet outlet temps, compared to other healthy units under similar load conditions.
 
Engineering news on Phys.org
You should do a heat balance on this condenser and one of the others and compare the numbers. It sounds wrong that you have these differences but zero difference in the cooling water flow or temperatures.

You don't really give enough information, but it sounds like the flow rate (pounds per second) of moisture and/or steam into that condenser is different than the other condensers. Presumably, they should be the same. Look for differences in the upstream drains between this condenser and the others.

Are these condensers catching exhaust from steam turbines? If so, also check for differences in reheat spray, and for abnormal sealing steam flows.
 
Nirmsing1411 said:
The condensate drain from a steam condenser is expected to be about 50 deg C. It's only 38 deg C or so. There's a mix of steam and non condensable gases coming into the condenser. Its pressure seems slightly higher, being about 0.25 bar abs instead of 0.2 bar. What does it indicate? Also, no significant difference in cooling water flow and the inlet outlet temps, compared to other healthy units under similar load conditions.

How's the air ingress on those other units?

In a condenser, steam flowing toward the tubes should reheat the water dripping from them back up to nearly saturation.
Too much air interferes with that.
Our condenser had trays interspersed in the tube bundle to catch the condensate and route it out of the tubes on an inclined plane, providing lots of surface area for heat transfer from incoming steam. That brings condensate back closer to saturation temperature.

upload_2017-6-20_0-47-4.png

image courtesy of these guys
http://www.hts.org.uk/downloads/TroubleshootingSteamSurfaceCondensers.pdf

Cooling water temperature rise shouldn't be much different between your condensers,,, .
Compare :
the enthalpy change between saturated vapor and saturated liquid
to
the enthalpy change between saturated vapor and your twelve degrees subcooled liquid.
Divide one by the other, i wager you get pretty close to 1.That's my guess.

Is the air ejector howling ? What tests can you run ?

@Nirmsing1411 have you gone away ?
 
Last edited:

Similar threads

Replies
1
Views
2K
Replies
5
Views
4K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 2 ·
Replies
2
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
8
Views
5K
  • · Replies 6 ·
Replies
6
Views
5K
  • · Replies 8 ·
Replies
8
Views
6K
Replies
6
Views
7K