Substation main xformer earthing?

Click For Summary
SUMMARY

The discussion focuses on the earthing connection of the fourth terminal on the low side of a substation transformer, which is typically the neutral point connected to protective earth. Participants confirm that this connection is essential for protecting insulators from overvoltage. The grounding setup includes a grid of flat copper straps earthed through deep holes, with the fourth terminal connected to this grid. Additionally, the transformer housing is bonded to the earth grid via a separate conductor, and the operating mode of the neutral conductor should be specified as either TN-C or TN-S.

PREREQUISITES
  • Understanding of substation transformer configurations
  • Knowledge of grounding systems in electrical engineering
  • Familiarity with TN-C and TN-S earthing systems
  • Basic principles of electrical safety and overvoltage protection
NEXT STEPS
  • Research the specifics of transformer grounding and bonding techniques
  • Explore the differences between TN-C and TN-S earthing systems
  • Study the design and implementation of earthing grids in substations
  • Investigate the role of protective earth in electrical installations
USEFUL FOR

Electrical engineers, substation designers, game developers modeling realistic electrical systems, and anyone interested in the technical aspects of transformer earthing and grounding.

Ryoko
Messages
145
Reaction score
10
I'm modeling a substation for a game. I would like it to be generally technically correct. Currently, I'm modeling the main xformer and I noticed they have 4 terminals on the low side. I can guess these are for phases A/B/C plus a neutral. My question is where would this 4th terminal normally be connected in a substation setting?
 
Engineering news on Phys.org
Ryoko said:
My question is where would this 4th terminal normally be connected in a substation setting?
I would expect it to be the neutral, at the centre of the three-phase star, connected to protective earth. It is there to protect the insulators from overvoltage.

It might depend on the country and national standard.
 
  • Like
Likes   Reactions: Ivan Nikiforov
berkeman said:
I saw those articles. But unfortunately it was more theoretical than practical. I guess what I'm asking if I walked into a substation, what would that 4th connection look like? Is it just strapped to an earthing connection in the ground or tied to the xformer case?
 
Hmm, is this article any better?

1738606601084.jpeg

https://eepower.com/technical-artic...tion-grounding-parts-of-the-grounding-system/
 
  • Like
Likes   Reactions: Ivan Nikiforov
Ryoko said:
Is it just strapped to an earthing connection in the ground or tied to the xformer case?
The floor of the sub-station will have a grid of flat copper straps on the surface, earthed through deep holes in the ground. The 4th connection, as an earthed neutral, will be connected to that grid with a strap. The chassis of the transformer will be separately bonded to the earth grid.
 
  • Like
Likes   Reactions: Ivan Nikiforov and berkeman
Ryoko said:
I saw those articles. But unfortunately it was more theoretical than practical. I guess what I'm asking if I walked into a substation, what would that 4th connection look like? Is it just strapped to an earthing connection in the ground or tied to the xformer case?
1738608651112.png

Hello! The ground wire is shown with a red arrow. This connection must be made at the transformer terminal at the neutral connection point. The transformer housing is connected to the ground loop by a separate conductor. When designing, please specify the operating mode of the neutral conductor - TN-C or TN-S.
 
  • Informative
  • Like
Likes   Reactions: berkeman and DaveE
Ivan Nikiforov said:
View attachment 356772
Hello! The ground wire is shown with a red arrow. This connection must be made at the transformer terminal at the neutral connection point. The transformer housing is connected to the ground loop by a separate conductor. When designing, please specify the operating mode of the neutral conductor - TN-C or TN-S.
Not actually designing anything. I just want the model to be reasonably accurate. Though admittedly 99.9% of people playing a game looking at it would never see anything wrong even when it is totally messed up. I've played games with power distribution as part of the modeled environment and it drives me nuts just how horribly wrong it is most of the time. But the art guys like it.
 
  • Like
Likes   Reactions: Ivan Nikiforov

Similar threads

Replies
4
Views
3K
Replies
12
Views
736
  • · Replies 32 ·
2
Replies
32
Views
4K
Replies
31
Views
5K
  • · Replies 83 ·
3
Replies
83
Views
7K
  • · Replies 13 ·
Replies
13
Views
6K
  • · Replies 16 ·
Replies
16
Views
40K
  • · Replies 6 ·
Replies
6
Views
13K
Replies
14
Views
3K
  • · Replies 9 ·
Replies
9
Views
2K