Supplied complex power from source vs consumed by load

13 replies · 3K views · last reply
eehelp150
Messages
235
Reaction score
0

Homework Statement


Printed problem text: 2.13. A balanced delta connected load of 15 + j18 Ω per phase is connected at the end of a three-phase line as shown in Figure 12. The line impedance is 1 + j2 Ω per phase. The line is supplied from a three-phase source with a line-to-line voltage of 207.85 V rms. Taking Van as reference, determine the following:

Three-phase circuit schematic: a source with lines a, b and c, each with a series impedance of 1 + j2 Ω, labelled |V_L| = 207.85 V, feeding a delta-connected load with 15 + j18 Ω in each branch, terminals a, b and c.


Homework Equations


S= 3VaIa*

The Attempt at a Solution


After transformation:
Single-phase circuit schematic: source V1 = 120∠0° V at terminal a and n, series impedance 1 + j2 Ω, then load of 5 Ω resistor and j6 Ω inductor, with current Ia marked and V2 across the load.

Ia = 120<0 / (6+8j) = 12<-53.13 A
Total complex power = 3 * Va * Ia* = 3*120<0 * 12<53.13 = 2592W + j3456 VAR
This is the power supplied from source. What would be the power consumed by load?
 
Attachments
  • Textbook problem 2.13: A balanced delta connected load of 15 + j18 ohms per phase is connected at the end of a three-phase line with impedance 1 + j2 ohms per phase, supplied at 207.85 V rms line-to-line, with Van as reference.
    upload_2016-10-27_0-28-36.png
    10.1 KB · Views: 596
eehelp150 said:
What would be the power consumed by load?
You know the load impedance and load current. How will you determine the active and reactive power associated with the load?
 
cnh1995 said:
You know the load impedance and load current. How will you determine the active and reactive power associated with the load?
Load impedance = 5 + j6
Load current = 12<-53.13A
I*I*Z
?
 
eehelp150 said:
Load impedance = 5 + j6
Load current = 12<-53.13A
I*I*Z
?
Yes. Take magnitudes only.
S=I2Z.
 
Last edited:
cnh1995 said:
Yes. Take magnitudes only.
S=I2Z.
So 144 * (5+j6)
?

power of (1+j2)= 144 * (1+2j)
and
(load) = 144*(5+j6)
combined become 864W + j1152VAR

but the total complex power is 2592W + j3456VAR

Is it right for these values to not match?
 
Last edited:
eehelp150 said:
So 144 * (5+j6)
Yes.
eehelp150 said:
Is it right for these values to not match?
Yes. Can you say why?
 
cnh1995 said:
Yes.

Yes. Can you say why?
Is it because it's 1/3 of the "actual" circuit?
Do I need to multiply by 3 to get the total complex power consumed by load?

If no, does this look correct?
720W + j864VAR

Load power factor:
S = sqrt(Q^2+P^2) = 1124VA
PF = P/S = 720/1124 = 0.64 lagging (Q>0)
correct?
 
eehelp150 said:
Is it because it's 1/3 of the "actual" circuit?
Do I need to multiply by 3 to get the total complex power consumed by load?

If no, does this look correct?
720W + j864VAR

Load power factor:
S = sqrt(Q^2+P^2) = 1124VA
PF = P/S = 720/1124 = 0.64 lagging (Q>0)
correct?
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
 
cnh1995 said:
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated (720W + j864VAR) or do I need to multiply that by 3?
 
eehelp150 said:
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated (720W + j864VAR) or do I need to multiply that by 3?
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.
eehelp150 said:
power of (1+j2)= 144 * (1+2j)
and
(load) = 144*(5+j6)
combined become 864W + j1152VAR
Here, while applying S=I2Z, you should consider the magnitude only. If you want to use the phasor form, you should take the conjugate of the current i.e. (IZ)(I*).
 
cnh1995 said:
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated or do I need to multiply that by 3?
cnh1995 said:
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.

Here, while applying S=I2Z, you should consider the magnitude only. If you want to use the phasor form, you should take the conjugate of the current i.e. (IZ)(I*).
So magnitude of (5+j6) = sqrt(61)?
 
eehelp150 said:
Calculate the total complex power consumed by the load and determine the load's power factor
cnh1995 said:
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.
For load power factor, you can use the single phase equivalent network since it is a balanced network.
eehelp150 said:
So magnitude of (5+j6) = sqrt(61)?
Yes.
 
cnh1995 said:
For load power factor, you can use the single phase equivalent network since it is a balanced network.

Yes.
so load would be 3 * 144*sqrt(61)?
How do i get power factor from this?
 
Last edited:
eehelp150 said:
so load would be 3 * 144*sqrt(61)?
How do i get power factor from this?
If the load impedance is R+jX, what would its power factor?