Supplied complex power from source vs consumed by load

AI Thread Summary
The discussion focuses on calculating the total complex power consumed by a load in a three-phase system, emphasizing the need to multiply per-phase values by three to obtain total power. The initial calculations yield a total complex power of 2592W + j3456VAR from the source, while the load's calculated power is 720W + j864VAR, which requires adjustment for the three-phase context. Participants clarify that discrepancies arise due to power associated with line impedance, which must be accounted for in the total power analysis. The load power factor is computed as 0.64 lagging, based on the total active and reactive power. Ultimately, the correct approach involves using the per-phase calculations and adjusting for the three-phase system to determine accurate power values and factors.
eehelp150
Messages
235
Reaction score
0

Homework Statement


upload_2016-10-27_0-28-37.png

upload_2016-10-27_0-28-49.png


Homework Equations


S= 3VaIa*

The Attempt at a Solution


After transformation:
upload_2016-10-27_0-30-5.png

Ia = 120<0 / (6+8j) = 12<-53.13 A
Total complex power = 3 * Va * Ia* = 3*120<0 * 12<53.13 = 2592W + j3456 VAR
This is the power supplied from source. What would be the power consumed by load?
 

Attachments

  • upload_2016-10-27_0-28-36.png
    upload_2016-10-27_0-28-36.png
    10.1 KB · Views: 544
Physics news on Phys.org
eehelp150 said:
What would be the power consumed by load?
You know the load impedance and load current. How will you determine the active and reactive power associated with the load?
 
cnh1995 said:
You know the load impedance and load current. How will you determine the active and reactive power associated with the load?
Load impedance = 5 + j6
Load current = 12<-53.13A
I*I*Z
?
 
eehelp150 said:
Load impedance = 5 + j6
Load current = 12<-53.13A
I*I*Z
?
Yes. Take magnitudes only.
S=I2Z.
 
Last edited:
cnh1995 said:
Yes. Take magnitudes only.
S=I2Z.
So 144 * (5+j6)
?

power of (1+j2)= 144 * (1+2j)
and
(load) = 144*(5+j6)
combined become 864W + j1152VAR

but the total complex power is 2592W + j3456VAR

Is it right for these values to not match?
 
Last edited:
eehelp150 said:
So 144 * (5+j6)
Yes.
eehelp150 said:
Is it right for these values to not match?
Yes. Can you say why?
 
cnh1995 said:
Yes.

Yes. Can you say why?
Is it because it's 1/3 of the "actual" circuit?
Do I need to multiply by 3 to get the total complex power consumed by load?

If no, does this look correct?
720W + j864VAR

Load power factor:
S = sqrt(Q^2+P^2) = 1124VA
PF = P/S = 720/1124 = 0.64 lagging (Q>0)
correct?
 
eehelp150 said:
Is it because it's 1/3 of the "actual" circuit?
Do I need to multiply by 3 to get the total complex power consumed by load?

If no, does this look correct?
720W + j864VAR

Load power factor:
S = sqrt(Q^2+P^2) = 1124VA
PF = P/S = 720/1124 = 0.64 lagging (Q>0)
correct?
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
 
cnh1995 said:
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated (720W + j864VAR) or do I need to multiply that by 3?
 
  • #10
eehelp150 said:
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated (720W + j864VAR) or do I need to multiply that by 3?
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.
eehelp150 said:
power of (1+j2)= 144 * (1+2j)
and
(load) = 144*(5+j6)
combined become 864W + j1152VAR
Here, while applying S=I2Z, you should consider the magnitude only. If you want to use the phasor form, you should take the conjugate of the current i.e. (IZ)(I*).
 
  • #11
cnh1995 said:
Well, you calculated the total power for three phases. So, you should multiply the load power by 3. But they are not equal because out of total input power, some power is associated with the line impedance 1+j2 ohm. Remaining power is fed to the load.
If the prompt is:
Calculate the total complex power consumed by the load and determine the load's power factor

Do I use what I calculated or do I need to multiply that by 3?
cnh1995 said:
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.

Here, while applying S=I2Z, you should consider the magnitude only. If you want to use the phasor form, you should take the conjugate of the current i.e. (IZ)(I*).
So magnitude of (5+j6) = sqrt(61)?
 
  • #12
eehelp150 said:
Calculate the total complex power consumed by the load and determine the load's power factor
cnh1995 said:
You should multiply by 3. You have transformed the circuit into its per phase equivalent. Total power will be thrice the per phase power.
For load power factor, you can use the single phase equivalent network since it is a balanced network.
eehelp150 said:
So magnitude of (5+j6) = sqrt(61)?
Yes.
 
  • #13
cnh1995 said:
For load power factor, you can use the single phase equivalent network since it is a balanced network.

Yes.
so load would be 3 * 144*sqrt(61)?
How do i get power factor from this?
 
Last edited:
  • #14
eehelp150 said:
so load would be 3 * 144*sqrt(61)?
How do i get power factor from this?
If the load impedance is R+jX, what would its power factor?
 