Synchronous Generator Homework: Finding Required Field Current and Input Torque

Click For Summary

Discussion Overview

The discussion revolves around a homework problem related to synchronous generators, specifically focusing on calculating the required field current and input torque while operating at a rated voltage of 13.8kV. Participants explore the implications of rated voltage on field current and the effects of load on terminal voltage.

Discussion Character

  • Homework-related
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant suggests that the required field current at rated voltage is 225 Amps, questioning if this is correct.
  • Another participant argues that the excitation will be higher than 225A due to voltage sag when a load is connected, proposing the use of synchronous impedance to find the required field current.
  • There is a discussion about whether the rated voltage refers to line-to-line voltage or line-to-neutral voltage, with some participants expressing uncertainty about the implications of this distinction.
  • One participant mentions calculating the current from the load and finding the generator voltage, leading to a field current estimate of approximately 300 amps.
  • Concerns are raised about the complexity of the material and the desire for clear solutions rather than just problem statements.

Areas of Agreement / Disagreement

Participants express differing views on the interpretation of rated voltage and its impact on field current calculations. There is no consensus on the correct approach or final values, as multiple competing perspectives are presented.

Contextual Notes

Participants reference different methods for calculating field current, including interpolation-extrapolation techniques and the effects of armature reaction on terminal voltage. There is acknowledgment of potential errors in calculations and the complexity of three-phase systems.

Who May Find This Useful

Students and practitioners working on synchronous generator problems, particularly those dealing with field current calculations and the effects of load on generator performance.

Brianrofl
Messages
21
Reaction score
0

Homework Statement



t.PNG

The Attempt at a Solution



First up, part a.

The first one is really simple. The generator is working at its rated voltage of 13.8kV, right? So, would the required field current not be just 225 Amps?

Next, part b.
20160404_194024.jpg


To sort of explain what's going on, I first found the saturated reactance of the generator by using the data from the table (for 175 field amps). Then, I draw out a per-phase circuit using 13.8kV for the voltage source, the reactance Xs, and the load in Y-connection. I used 13.8kV because the instructions say the generator operates at rated voltage, correct? [Divide by sqrt 3 to convert to line-to-neutral voltage].

Using that, the current is found easily.

20160404_194045.jpg


Which then translates into finding the input torque rather easily.

I'd appreciate any input. I think I know how to solve this problem but it seemed too easy, and there are just so many things you can make mistakes on doing 3 phase systems that I just want to make sure.

Thanks.
 
Physics news on Phys.org
Brianrofl said:
The first one is really simple. The generator is working at its rated voltage of 13.8kV, right? So, would the required field current not be just 225 Amps?
I believe the excitation will be higher. For 225A field current, "open circuit" voltage is 13.8kV. This voltage will sag once you connect the load, due to the synchronous impedance. From the OC and SC data given, you can calculate synchronous impedance Zs and use E=Vterminal+I*Zs.
You can calculate current I from the load. For the value of E(generated emf), you can find the field current required by interpolation-extrapolation technique using Voc vs field current table.
 
Last edited:
  • Like
Likes   Reactions: Brianrofl
Ok, I'll work it out again and see what I get. Are there any issues with my part b?
 
Brianrofl said:
Ok, I'll work it out again and see what I get. Are there any issues with my part b?
Your approach looks right to me. I haven't verified the calculations, but I'm sure they are correct.
 
cnh1995 said:
Your approach looks right to me. I haven't verified the calculations, but I'm sure they are correct.

I'm really getting hung up on one thing. In the problem, he states: "while operating with the rated voltage." Wouldn't that just mean that the generator voltage is the 13.8kV line-to-line?

I'm referencing a lecture problem where when solving for the field current, you're given the voltage at the load and the power at the load. Using those two values, you can solve for the current, and then find the voltage dropped at the synchronous impedance. You then add the load voltage to this impedance voltage and find the voltage Ea supplied by the generator. In my homework problem's case, wouldn't my voltage Ea just be 13.8kV line-to-line?

I did try putting the voltage given (13.8kV) across the load, then calculated current, then found the generator voltage from there, which gave me a field current of ~300 amps.

So many nit picky things in this material, and I really hate turning in problems for credit. I'd so much rather just be given a solution and figure out how to do it.
 
Brianrofl said:
Wouldn't that just mean that the generator voltage is the 13.8kV line-to-line?
It is terminal voltage of the generator. When you connect a load, this voltage reduces due to armature reaction. To bring it back to the rated value, field excitation is raised.
 
cnh1995 said:
It is terminal voltage of the generator. When you connect a load, this voltage reduces due to armature reaction. To bring it back to the rated value, field excitation is raised.

Like this?

20160404_231946.jpg


Where I find my new value of Ea at which the voltage across the terminals is still 13.8kV?
 
Brianrofl said:
Like this?

View attachment 98562

Where I find my new value of Ea at which the voltage across the terminals is still 13.8kV?
Yes.
 

Similar threads

  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 37 ·
2
Replies
37
Views
8K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
Replies
4
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
1
Views
3K
Replies
34
Views
4K
Replies
6
Views
4K