Synchronous Generator PMG Rotor Damaged

Click For Summary
SUMMARY

The discussion centers on a synchronous generator operating at 1800rpm, 11kV, and 656A, which experienced increased vibrations and tripped after a large balanced three-phase load was applied. Despite normal excitation voltage fluctuations from 23V to 120V, the generator's PMG rotor magnets were found damaged upon inspection. The PMG pole cap fasteners were tightened to less than 20 Nm, below the required 35-37 Nm, which may have contributed to the issue. Participants emphasized the importance of monitoring instrument recordings to diagnose the problem accurately.

PREREQUISITES
  • Understanding of synchronous generator operation and components
  • Knowledge of PMG (Permanent Magnet Generator) systems
  • Familiarity with vibration analysis in electrical machinery
  • Experience with electrical testing and diagnostics
NEXT STEPS
  • Investigate the impact of PMG rotor magnet integrity on generator performance
  • Learn about proper torque specifications for PMG pole cap fasteners
  • Research loss of synchronism events in synchronous generators
  • Explore vibration monitoring techniques for electrical machinery
USEFUL FOR

Electrical engineers, maintenance technicians, and professionals involved in the operation and troubleshooting of synchronous generators will benefit from this discussion.

vish1711
Messages
4
Reaction score
0
TL;DR
Synchronous Generator PMG Rotor Damaged
Generator - 1800rpm, 11kV, 656A. While running Gen, a large load was turned on, and excitation voltage went from 23V to 120V, but that's a normal situation that happens every time and on all Generators. But this time after turning on the large load, vibrations started increasing, and Gen tripped on high vibrations. When inspected PMG rotor magnets were broken inside the gen. We did all the testing and couldn't found anything. Does anyone has experienced a similar thing before?
 
Engineering news on Phys.org
Welcome to PF.
Was it a 3 phase generator? Was the heavy load a balanced 3 phase load?
Did one of the three phases break due to load before the other phases?
 
vish1711 said:
Summary:: Synchronous Generator PMG Rotor Damaged

But this time after turning on the large load, vibrations started increasing,
If the vibrations increased gradually, the problem is probably not with the load. Perhaps one magnet cracked, then another, then another. If the load was unbalanced three phase, the vibrations would be a step, not a ramp.

Do you have recordings of what happened from the instruments?

I am not familiar with synchronous generators that have both permanent magnets and external excitation.
 
anorlunda said:
If the vibrations increased gradually, the problem is probably not with the load. Perhaps one magnet cracked, then another, then another. If the load was unbalanced three phase, the vibrations would be a step, not a ramp.

Do you have recordings of what happened from the instruments?

I am not familiar with synchronous generators that have both permanent magnets and external excitation.
It was balanced three phase load and started with 3 Generators. Other two Generators did handle the load very well. And it's not external excitation system. There is a exciter system within the generator. You are right, it has nothing to do with the load I guess but I can't see any reason of damaging magnets. All electrical and magnetic tests were fine.
 
Baluncore said:
Welcome to PF.
Was it a 3 phase generator? Was the heavy load a balanced 3 phase load?
Did one of the three phases break due to load before the other phases?
Baluncore said:
Welcome to PF.
Was it a 3 phase generator? Was the heavy load a balanced 3 phase load?
Did one of the three phases break due to load before the other phases?
It was balanced three phase load and started with 3 Generators. Other two Generators did handle the load very well. It has nothing to do with the load I guess but I can't see any reason of damaging magnets. All electrical and magnetic tests were fine.
 
vish1711 said:
Summary:: Synchronous Generator PMG Rotor Damaged

Generator - 1800rpm, 11kV, 656A. While running Gen, a large load was turned on, and excitation voltage went from 23V to 120V, but that's a normal situation that happens every time and on all Generators. But this time after turning on the large load, vibrations started increasing, and Gen tripped on high vibrations. When inspected PMG rotor magnets were broken inside the gen. We did all the testing and couldn't found anything. Does anyone has experienced a similar thing before?
PMG Pole cap Fasteners were tighten less than 20 Nm whereas it should be between 35-37 Nm. But still there is no crack on Pole cap but magnet under the pole cap are damaged.
 
How about a loss of synchronism event? After loss of synchronism, as frequency departs from synchronous frequency, you would see extreme and wild swings in power. When the frequency difference became big enough, those swings might be interpreted as vibrations.

I ask again. Do you have records from the instruments?
 

Similar threads

Replies
1
Views
3K
  • · Replies 46 ·
2
Replies
46
Views
6K
  • · Replies 20 ·
Replies
20
Views
3K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 21 ·
Replies
21
Views
9K
  • · Replies 38 ·
2
Replies
38
Views
8K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 7 ·
Replies
7
Views
4K
Replies
4
Views
15K