SUMMARY
The discussion centers on a synchronous generator operating at 1800rpm, 11kV, and 656A, which experienced increased vibrations and tripped after a large balanced three-phase load was applied. Despite normal excitation voltage fluctuations from 23V to 120V, the generator's PMG rotor magnets were found damaged upon inspection. The PMG pole cap fasteners were tightened to less than 20 Nm, below the required 35-37 Nm, which may have contributed to the issue. Participants emphasized the importance of monitoring instrument recordings to diagnose the problem accurately.
PREREQUISITES
- Understanding of synchronous generator operation and components
- Knowledge of PMG (Permanent Magnet Generator) systems
- Familiarity with vibration analysis in electrical machinery
- Experience with electrical testing and diagnostics
NEXT STEPS
- Investigate the impact of PMG rotor magnet integrity on generator performance
- Learn about proper torque specifications for PMG pole cap fasteners
- Research loss of synchronism events in synchronous generators
- Explore vibration monitoring techniques for electrical machinery
USEFUL FOR
Electrical engineers, maintenance technicians, and professionals involved in the operation and troubleshooting of synchronous generators will benefit from this discussion.