Is My Pramac GSL30 Generator Dead? Testing and Identifying Coil Connections

Click For Summary
SUMMARY

The Pramac GSL30 generator (30kVA) is experiencing no output due to disconnected wires and an unplugged AVR. The alternator features a 12-wire stator corresponding to six coils, configured in a series star for 415V ph-ph and 240V ph-n output. Testing with a Megger at 500V revealed some coils with resistance greater than 3Gohm, while others measured below 10k. The consensus is that moisture in the insulation may be the issue, and further inspection and drying methods are recommended before declaring the alternator dead.

PREREQUISITES
  • Understanding of Pramac GSL30 generator specifications
  • Familiarity with alternator wiring configurations
  • Experience using a Megger for insulation resistance testing
  • Knowledge of moisture-related electrical issues
NEXT STEPS
  • Research methods for drying electric motor windings
  • Learn about troubleshooting AVR issues in generators
  • Investigate the use of insulation resistance testing tools
  • Study the impact of moisture on electrical components
USEFUL FOR

Electricians, generator technicians, and maintenance personnel involved in troubleshooting and repairing generator systems, particularly those dealing with moisture-related electrical failures.

Guineafowl
Messages
876
Reaction score
409
A mate of mine has bought a Pramac GSL30 generator (30kVA) ‘as seen’, and of course there is no output.

Inside the connection box of the Stamford alternator unit, someone has been fiddling - the output wires have been disconnected and taped, and the AVR has also been unplugged.

Now, it’s a 12-wire stator, corresponding to six coils. It was hooked up as a series star, giving 415V ph-ph and 240V ph-n. This is the configuration we want.

I’ve isolated the 12 wires, and identified how they relate to each coil. Using a Megger at 500V, I’ve found that some coils are >3Gohm apart, while others are less than 10k. Have I done enough to call the alternator dead?
 
Engineering news on Phys.org
Guineafowl said:
Using a Megger at 500V, I’ve found that some coils are >3Gohm apart, while others are less than 10k. Have I done enough to call the alternator dead?

I wouldn't call it dead yet.
Sounds to me like moisture in the insulation .

In the plant we 'dried' electric motors to get their resistance readings up to snuff..
Sometimes by covering them and placing big incandescent light bulbs underneath
sometimes by connecting a welder and applying somewhat less than full load current(there's no cooling airflow when it's stationary so feel the windings often)
sometimes simply by energizing the built in "heater" resistors.
We'd plot resistance readings every hour or so.

Brush out any carbon dust and grime. A soap and distilled water wash is strong but permissible medicine , follow by a good long heated dry.

Guineafowl said:
I’ve isolated the 12 wires, and identified how they relate to each coil.
I find a Boy Scout compass and small DC source (D-cell battery or wall-wart) handy for that check but it's easier with the rotor out..

Good Luck !
 
  • Like
Likes Fisherman199, dlgoff, Averagesupernova and 1 other person
jim hardy said:
I wouldn't call it dead yet.
Sounds to me like moisture in the insulation .

In the plant we 'dried' electric motors to get their resistance readings up to snuff..
Sometimes by covering them and placing big incandescent light bulbs underneath
sometimes by connecting a welder and applying somewhat less than full load current(there's no cooling airflow when it's stationary so feel the windings often)
sometimes simply by energizing the built in "heater" resistors.
We'd plot resistance readings every hour or so.

Brush out any carbon dust and grime. A soap and distilled water wash is strong but permissible medicine , follow by a good long heated dry.I find a Boy Scout compass and small DC source (D-cell battery or wall-wart) handy for that check but it's easier with the rotor out..

Good Luck !
Brilliant.

Its most likely use was as a standby generator, so it could have sat for a while, condensating.

Looks like I’ll have to pull it from the engine and have a look inside. Pics to follow.

Many thanks, Jim.
 
  • Like
Likes jim hardy
jim hardy said:
I find a Boy Scout compass and small DC source (D-cell battery or wall-wart) handy for that check but it's easier with the rotor out..

Thankfully I discovered a diagram of the wire connections under the top plate (after I’d cleverly worked out the configuration).
 
Guineafowl said:
Thankfully I discovered a diagram of the wire connections under the top plate (after I’d cleverly worked out the configuration).
Sounds like the wire markers were still there. That's Good Luck - whoever disconnected it didn't cut them off .
 
Most likely this can only be answered by an "old timer". I am making measurements on an uA709 op amp (metal can). I would like to calculate the frequency rolloff curves (I can measure them). I assume the compensation is via the miller effect. To do the calculations I would need to know the gain of the transistors and the effective resistance seen at the compensation terminals, not including the values I put there. Anyone know those values?

Similar threads

Replies
9
Views
2K
  • · Replies 38 ·
2
Replies
38
Views
7K
Replies
24
Views
5K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 7 ·
Replies
7
Views
9K
  • · Replies 44 ·
2
Replies
44
Views
21K
  • · Replies 3 ·
Replies
3
Views
22K
  • · Replies 16 ·
Replies
16
Views
7K