Transformer Voltage in case of Short-Circuiting

Click For Summary
SUMMARY

The discussion centers on the behavior of a distribution transformer during a short-circuit event between high voltage (HV) and low voltage (LV) lines. The primary winding operates at 14.4 KV, while the secondary winding is rated at 120 V. When short-circuited, the voltage across the secondary windings does not exceed 120 V due to core saturation and the grounding effect, which prevents the secondary voltage from rising to the primary voltage level. This situation can lead to damage in LV equipment before the HV fuse activates, particularly when LV cables are positioned beneath HV lines.

PREREQUISITES
  • Understanding of transformer operation principles
  • Knowledge of high voltage (HV) and low voltage (LV) systems
  • Familiarity with grounding techniques in electrical systems
  • Awareness of electrical safety protocols during short-circuit conditions
NEXT STEPS
  • Research transformer saturation effects and their impact on voltage regulation
  • Study the implications of grounding in HV and LV systems
  • Learn about protective devices and their response to short-circuit conditions
  • Explore case studies on equipment damage due to HV-LV short circuits
USEFUL FOR

Electrical engineers, power system designers, safety inspectors, and anyone involved in the maintenance and operation of transformer systems will benefit from this discussion.

QwertyXP
Messages
66
Reaction score
0
Consider a distribution transformer: The primary winding (HV) has a nominal voltage of 14.4 KV, whereas secondary (LV) has a nominal voltage of 120 V. One terminal from each of the primary and secondary windings is solidly grounded. A HV line (14.4 KV) is connected to the primary.

Now, if the HV line is short-circuited with the LV line, what will the voltage be across the secondary windings?

According to the book I have, the voltage will not be much larger than 120V. I find this very surprising. After the HV and LV lines are short-circuited, the potential difference across secondary should also have been 14.4KV, not a bit larger or smaller!
 
Engineering news on Phys.org
I think I have the answer already. The book was probably only referring to normal situations. The voltage between a terminal and ground can be slightly higher than 120V because of the resistance of ground wire.
 
When the primary to secondary circuit short is made, the transformer will have what is effectively several turns shorted that will saturate the core. This will remove voltage control on the secondary so the voltage on the secondary circuit will rise close to the HV and destroy LV equipment connected to the secondary circuit. The HV fuse will then open, but only after LV equipment has been damaged.

This happens when LV cables are on the same poles below the HV distribution cables. When a cable breaks and drops onto the LV wires you need a good insurance policy. You can tell when this has happened with a 3 phase MEN system because one third of the houses in the street have damaged equipment. Those were the houses that were powered by the LV phase that shorted.
 
  • Like
Likes 1 person
Thank you Baluncore!
 
Most likely this can only be answered by an "old timer". I am making measurements on an uA709 op amp (metal can). I would like to calculate the frequency rolloff curves (I can measure them). I assume the compensation is via the miller effect. To do the calculations I would need to know the gain of the transistors and the effective resistance seen at the compensation terminals, not including the values I put there. Anyone know those values?

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
Replies
2
Views
678
Replies
8
Views
2K
Replies
2
Views
2K
  • · Replies 4 ·
Replies
4
Views
5K
  • · Replies 27 ·
Replies
27
Views
3K
Replies
14
Views
3K
  • · Replies 1 ·
Replies
1
Views
5K
Replies
64
Views
8K
Replies
12
Views
2K