Homework Statement
A 415V to 11 kV transformer has a rating of 200 kVA. The winding resistance and leakage reactance when referred to the primary are 0.014 Ω and 0.057 Ω respectively.
(a) Determine the % regulation of the transformer at 0.8 power factor lagging.
(b) In designing a particular 415V to 11 kV, 200 kVA transformer, the primary winding resistance is to be 10 mΩ. Find the maximum winding resistance of the secondary winding if the transformer is to have 2% regulation at unity power factor.
Homework Equations
##R's = Rs + \frac{Rp}{n^2} \leftarrow## this is to calculate the resistance reflected from the primary to the secondary winding.
##L's = Ls + \frac{Lp}{n^2} \leftarrow## this is to calculate the reactance reflected from the primary to the secondary winding.
##n^{2} = \frac{415}{11000} = 0.0014233471 \leftarrow## this is the value of ##n^{2}##
The Attempt at a Solution
Firstly, with unity power factor, I believe that I can effectively treat this as 200kW because with a part reactive load we would have a non-unity power factor. Therefore calculations are based upon this assumption.
To calculate the primary (reflected to the secondary) impedance we use ##R's = Rs + \frac{Rp}{n^2}## which using ##\frac{Rp}{n^2}## and thus ##\frac{10 mΩ}{0.00142...}## gives us only the reflected portion of the impedance which is 40.06 (X) - we have not added the Rs
Similarly, the primary (reflected to the secondary) reactance is given by ##L's = Ls + \frac{Lp}{n^2}## which using ##\frac{Lp}{n^2}## and thus ##\frac{0.057Ω}{0.00142...}## gives us only the reflected portion of the reactance which is 7.0256 (R) - we have not added the Ls
As my previous method of calculation appears to be incorrect, I'm not sure what to do now. All I can see is that to achieve a power of 200kW at 11kV, would require a current of 18.181818 Amps. This gives a total impedance across the winding (i.e. the load) of 605 Ohms.
I have the feeling that I'm missing some key relationship between the reflected impedance and the only possible (maximum) value of the secondary winding. I don't know what the load value is, or the secondary winding resistance and reactance, so obviously the necessary data is in the given information.
There have been several topics on this question in this forum, all of which I have tried to learn from, but inevitably they become protracted or focus on a different part of the question. And like those other posters have said, the material supplied is often confusing, incomplete or simply inadequate.
Any help greatly appreciated!