Understanding HVAC Dampers and Flow Rates

  • Context: Undergrad 
  • Thread starter Thread starter poont2
  • Start date Start date
  • Tags Tags
    Flow Hvac
Click For Summary
SUMMARY

This discussion clarifies the function of HVAC dampers in regulating airflow within duct systems. It emphasizes that while dampers can create pressure drops, they should not be used to increase back pressure, as this can reduce overall efficiency. Instead, dampers are intended for balancing airflow across different areas, with the principle that a more open damper enhances efficiency. The continuity equation Q=AV is highlighted, reinforcing that flow rate remains constant despite changes in duct diameter or damper position.

PREREQUISITES
  • Understanding of the continuity equation Q=AV in fluid dynamics
  • Basic knowledge of HVAC systems and components
  • Familiarity with airflow principles and pressure differentials
  • Experience with duct design and air distribution methods
NEXT STEPS
  • Research the impact of pressure drops on HVAC system efficiency
  • Learn about duct sizing and its effect on airflow and velocity
  • Explore methods for balancing airflow in HVAC systems
  • Investigate the historical context of high-pressure air distribution systems
USEFUL FOR

HVAC engineers, service technicians, and anyone involved in the design or maintenance of air distribution systems will benefit from this discussion.

poont2
Messages
11
Reaction score
0
Hello guys,

I recently got an internship at a engineering consultant firm doing HVAC work. I am kinda confuse on one thing. How does HVAC dampers work? I have always learned in school the continuity equation Q=AV=AV ,

Q = the volumetric flow rate
A = the cross sectional area of flow
V = the mean velocity

So how do you regulate flow in a duct system using damper when the flow is going to be the same even if you put a damper to block the air space, wouldn't it just make the flow kinda turbulent while the flow rate stay the same? wouldn't the velocity just increase at the damper and decrease after it passes the damper? I am kinda confuse, only way i can think of is it give more pressure making the air handling unit put out less air?

For example, if a pump is connected to A and B pipe. Where A pipe is 1" and B pipe is 5", of course the velocity is going to be larger on the smaller pipe, but the flow rate (Q) would be the same on both pipe rite?

Thanks for your help!
 
Physics news on Phys.org
Which has the higher flow rate in your wash basin? When the valve is open or closed?
 
poont2 said:
...only way i can think of is it give more pressure making the air handling unit put out less air?
That's the answer. The key is the pressure drop across the damper making it harder for the fan to move air.
 
A common misconception about HVAC air flow is that you need "back pressure" to make it work. Service techs will often close air dampers just to build pressure because they've been taught that pressure differential is the key to air flow. But efficiency demands mass flow which is reduced with back pressure. In the 70's a lot of homes were built with "high pressure" air distribution systems. This was accomplished by drastically reducing duct diameters. Unfortunately the resultant volume reduction resulted in poor heat distribution and efficiency. So, the less restriction the better and dampers should only be used to balance different areas always keeping in mind that the more open the damper the greater the efficiency.
 
I still don't get it. could you please illustrate more
 

Similar threads

  • · Replies 17 ·
Replies
17
Views
3K
  • · Replies 10 ·
Replies
10
Views
4K
  • · Replies 22 ·
Replies
22
Views
3K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 19 ·
Replies
19
Views
3K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
Replies
0
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 11 ·
Replies
11
Views
3K