We had a thermal oxidizer on the tail end of a sulfur recovery unit have intermittent "flame failure" trips on the burner management system. This was a pretty big deal. Turning off an incinerator while full of bad stuff wasn't something you wanted to do. Management pressure to fix this *right now* was high.
After a while, we found a spider using the air cooling bleed as an entrance to the flame detection port and it could get close enough to the detector for it to fail self-check. Insect screens, redundant flame sensors, etc. were installed to address this and other issues.
I hate to think how much money that one cost. After that, I tended to refer to any arthropods/parts in incinerator, furnace, or other burner instrumentation systems as "debris", which for some reason was more politically correct than "spiders" at that facility.