What Are Economical Methods to Cool Down Mineral Oil in Server Tanks?

  • Thread starter Thread starter Anon_Miner
  • Start date Start date
  • Tags Tags
    Cool Cooling Oil
Click For Summary
SUMMARY

The forum discussion focuses on economical methods to cool down 250 liters of mineral oil used for immersion cooling of 10 servers, each consuming 2100 W. Key solutions proposed include using an oil-water heat exchanger, a car radiator as a dry cooler, and constructing a PVC cooling tower. The discussion emphasizes the necessity of finding an effective waste heat disposal method, particularly when access to natural water bodies is limited.

PREREQUISITES
  • Understanding of immersion cooling systems
  • Knowledge of heat exchanger principles
  • Familiarity with cooling tower design and operation
  • Basic principles of thermodynamics and heat transfer
NEXT STEPS
  • Research the design and efficiency of oil-water heat exchangers
  • Explore DIY methods for constructing a PVC cooling tower
  • Investigate the use of evaporative coolers for server cooling
  • Learn about the specifications and installation of commercial dry coolers
USEFUL FOR

This discussion is beneficial for data center operators, IT infrastructure engineers, and anyone involved in optimizing cooling solutions for high-performance computing environments.

Anon_Miner
Messages
19
Reaction score
1
TL;DR
Hi kind strangers
I'm asking for different ways to cool down 250 litres of mineral oil in a system.
Hello friendly people of PF

So I have a tank with about 250 litres of mineral oil in it. and computer servers are immersed in it. the oil keeps the servers cool but get's hot in return.

What different (economic) ways are there to cool the oil down? The best way I could think of was Oil-water heat exchanger but i don't know what to do with the produced hot water as I have no use for it.

Further Info: there are 10 servers in the pool. Each server consumes 2100 W. The working temperature for servers is within 10-65 °C.

so can you think of any other ways to optimize cooling down the oil?
or what to do with the hot water produced?

Thanks guys
 
Engineering news on Phys.org
You have to find a place to dump your waste heat. Just like with any airconditioning system: it's got to go somewhere. If you live near the ocean or a river: into the water. Else into the air.

Did your servers come with oil cooling ?
 
  • Like
Likes   Reactions: Anon_Miner
Drop the hot water through a cooling tower and recycle it.
 
  • Like
Likes   Reactions: Chestermiller, Anon_Miner and russ_watters
Cool problem [pun coincidental]
Anon_Miner said:
What different (economic) ways are there to cool the oil down? The best way I could think of was Oil-water heat exchanger but i don't know what to do with the produced hot water as I have no use for it.

Further Info: there are 10 servers in the pool. Each server consumes 2100 W. The working temperature for servers is within 10-65 °C.
You need a cooling tower or dry cooler if you don't have access to a large heat sink (a pool or lake?).

You can make a dry cooler with a car radiator.
 
  • Like
Likes   Reactions: Klystron, berkeman and Anon_Miner
BvU said:
You have to find a place to dump your waste heat. Just like with any airconditioning system: it's got to go somewhere. If you live near the ocean or a river: into the water. Else into the air.

Did your servers come with oil cooling ?
Thanks for your reply

No they didn't come with oil cooling, I used immersion cooling by myself.
Unfortunately I don't live near ocean or river and have to use tap water.

Do you have any suggestions on how to dissipate the heat into the air?
 
russ_watters said:
Cool problem [pun coincidental]

You need a cooling tower or dry cooler if you don't have access to a large heat sink (a pool or lake?).

You can make a dry cooler with a car radiator.
AZFIREBALL said:
Drop the hot water through a cooling tower and recycle it.
Thank you guys for taking the time

Yes I was thinking about using a car radiator since they are smaller and I don't have a lot of space. Hence the cooling tower seems not viable.
 
Anon_Miner said:
Yes I was thinking about using a car radiator since they are smaller and I don't have a lot of space. Hence the cooling tower seems not viable.
I've seen people make cooling towers with PVC pipe and a showerhead, but probably not for 2100W and it's more cumbersome.
 
  • Like
Likes   Reactions: Anon_Miner
russ_watters said:
I've seen people make cooling towers with PVC pipe and a showerhead, but probably not for 2100W and it's more cumbersome.
Yea I think it's the best solution. but do you know any way (other than Oil-water heat exchanger) to cool down the oil?
 
Anon_Miner said:
Yea I think it's the best solution. but do you know any way (other than Oil-water heat exchanger) to cool down the oil?
You could use tap water, but that would get expensive/wasteful.

The radiator/dry cooler is probably easiest, but the PVC cooling tower would be more effective (cooler water) and could be fun. You just might need to bank several together. Also, the PVC cooling tower might be able to be done without a fan.
 
  • Like
Likes   Reactions: Lnewqban and Anon_Miner
  • #10
russ_watters said:
You could use tap water, but that would get expensive/wasteful.

The radiator/dry cooler is probably easiest, but the PVC cooling tower would be more effective (cooler water) and could be fun. You just might need to bank several together. Also, the PVC cooling tower might be able to be done without a fan.
I really appreciate you taking the time

Do you have any blueprints for said cooling tower or any sources I can refer to?
 
  • #11
@Anon_Miner
Mineral transformer oil = 1-Methyl-naphthalene, is circulated through an electrical transformer and external radiator by a thermal siphon. You can use a similar technique.

https://owlcation.com/stem/Cooling-of-transformers

A circulation pump can be used to move the oil if the radiator placement is not suitable for the thermal circulation. A fan can be used to increase the flow of cooling air through a smaller radiator.
 
  • Informative
Likes   Reactions: Anon_Miner
  • #12
  • Like
Likes   Reactions: Joe591 and Anon_Miner
  • #13
Anon_Miner said:
I really appreciate you taking the time

Do you have any blueprints for said cooling tower or any sources I can refer to?
You're welcome!

https://www.overclockers.com/forums/showthread.php/321055-Building-your-First-evaporative-cooling-tower!

A couple of notes:
-Works better in cooler/ drier climates.
-Will humidify the room it is in.
-Taller is better. Or shorter, with a small fan.
-Higher flow through the tower means more cooling (in watts), but warmer water. So you are probably better off with more of them at lower flow (a misting nozzle instead of a shower head). Taking a stab at their effectiveness; 4 at 1 l/m and 10C delta-T.
 
  • Love
  • Like
Likes   Reactions: Anon_Miner and Lnewqban
  • #14
Baluncore said:
transformer
There's a good clue. Your application is very similar to cooling an oil filled transformer. This search shows numerous cooling methods found to be practical. You might even find a used transformer cooling system in a junkyard, and skip designing your own. Design can be fun, but we must recognize the risk of failed designs.
 
  • Like
Likes   Reactions: Anon_Miner and russ_watters
  • #16
Anon_Miner said:
Yea I think it's the best solution.
Can you say what the climate is like where you live? How many stories is the building where you have this server farm, and do you have access to the roof? If you aren't going to mount this radiator and fan on the roof, where are you going to dump all of that hot air?
 
  • Like
Likes   Reactions: Lnewqban, Anon_Miner and russ_watters
  • #17
Also, you might look at re-purposing the exterior fan and housing of a heat pump -- it's a nice compact weatherproof unit that you could use to pull air through your radiator...

1588949580745.png
 
  • Like
  • Informative
Likes   Reactions: Klystron, russ_watters and Anon_Miner
  • #18
berkeman said:
Can you say what the climate is like where you live? How many stories is the building where you have this server farm, and do you have access to the roof? If you aren't going to mount this radiator and fan on the roof, where are you going to dump all of that hot air?
thanks for your reply

The weather is dry and can reach up to 40°C during summer. The building is 4 story and access to the roof is possible but it's not necessary since the hot air will be dumped into open air (through the yard).
 
  • Like
Likes   Reactions: berkeman
  • #19
You are trying to dump 21 kW of power. That's a lot. I'd be surprised if you can get that practically with things like evaporative cooling or repurposed heat pumps.
 
  • Like
Likes   Reactions: Anon_Miner and berkeman
  • #20
Vanadium 50 said:
You are trying to dump 21 kW of power. That's a lot. I'd be surprised if you can get that practically with things like evaporative cooling or repurposed heat pumps.
2.1, not 21...
 
  • #21
Vanadium 50 said:
You are trying to dump 21 kW of power. That's a lot. I'd be surprised if you can get that practically with things like evaporative cooling or repurposed heat pumps.
russ_watters said:
2.1, not 21...
Ten times two equals twenty in my universe. 😉
 
  • Like
Likes   Reactions: Anon_Miner and Vanadium 50
  • #22
russ_watters said:
2.1, not 21...
Bystander said:
Ten times two equals twenty in my universe. 😉
Dang, sorry guys. I even read it a second time before replying and still misread. Somehow I read this as a home project and couldn't get off that track.

Yep, I agree it's too big for a home built solution. A commercial grade dry-cooler or cooling tower is required.
 
  • Like
Likes   Reactions: Anon_Miner
  • #23
@russ_watters -- How do you convert from 21kW to the "ton" or "seer" ratings of heat pumps? Is there a way to show the OP just how big the cooler would have to be?
 
  • Like
Likes   Reactions: Anon_Miner
  • #24
russ_watters said:
even read it a second time before replying and still misread.
Been there, done that, got the t-shirt(s), worn 'em out, washed the car,...
berkeman said:
21kW to the "ton"
"Ton" is order of one horse.(?)
 
  • #25
A ton of air conditioning is a nominal 12,000 Btu/h. It is defined as the rate of heat transfer that results in the freezing or melting of 907 kg (1 short ton = 2,000 lb); of pure ice at 0°C in 24 hours.
12,000 Btu/h. = 12.660672 MJ/hr = 200 Btu/min = 3.517 kW
 
  • Like
  • Informative
Likes   Reactions: Rx7man, BvU, Anon_Miner and 1 other person
  • #26
Baluncore said:
12,000 Btu/h. = 12.660672 MJ/hr = 200 Btu/min = 3.517 kW
So 21kW is about 7 ton? A 10 ton commercial heat pump is only a few thousand dollars (not including installation)...

https://hvacdirect.com/daikin-10-ton-12-6-ieer-light-commercial-heat-pump-packaged-unit-dch120xxx3vxxx.html

1588956070903.png
 
  • Informative
  • Like
Likes   Reactions: Klystron and Anon_Miner
  • #27
berkeman said:
@russ_watters -- How do you convert from 21kW to the "ton" or "seer" ratings of heat pumps? Is there a way to show the OP just how big the cooler would have to be?
Nice save, thanks.

3.41 BTU per watt, 12,000 btu per ton = 6 Tons. For an air conditioner, that's as big as residential units get. For a dry cooler it depends on the exact weather and coolant temperature limits, but you are probably looking at something of about this size:

avi_cooler_7132-crop.jpg
 
  • Informative
  • Wow
Likes   Reactions: Anon_Miner and berkeman
  • #28
Can't help but wonder:
The servers were apparently designed to be air-cooled. Why not build a ducted box and use filtered forced-air cooling? You can discharge the hot air outside, and probably won't need to cool the incoming air (with high enough air flow).
 
  • Like
Likes   Reactions: Klystron and Anon_Miner
  • #29
Dullard said:
Can't help but wonder:
The servers were apparently designed to be air-cooled. Why not build a ducted box and use filtered forced-air cooling? You can discharge the hot air outside, and probably won't need to cool the incoming air (with high enough air flow).
Yes, they are designed to be air-cooled. They've got very high speed fans to cool them.
But the downside to mentioned fans, They are very loud and make a lot of noise even just for one server. Now imagine 10 of them working simultaneously! It's deafening.

That was the reason I converted to oil cooling. I removed the fans and submerged them in Mineral oil to reduce the noise drastically. Although it came at a high expense but that was the only way I saw to "mute" the servers.

If you have any advice on how to reduce the noise drastically without submerging them; I would really appreciate it if you shared. (for the future server farms).

Thanks!
 
  • #30
I'm dating myself, but:

In the good old days, large computer installations were often installed on a false floor with a single large blower / AC pressurizing the under-floor space. Ducts were directed from that space up into the individual enclosures - the pressure difference caused the cool air to flow through the equipment.

You could build a version of that, and use a single large blower (located outside) instead of using the local fans. It's important to get the air where you need it - I'd thoroughly test with a single server before I did anything at scale. You may need to do some 'micro-ducting.'
 
  • Informative
Likes   Reactions: Anon_Miner

Similar threads

  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 3 ·
Replies
3
Views
4K
Replies
77
Views
23K
Replies
2
Views
2K
Replies
10
Views
3K
Replies
3
Views
4K
Replies
3
Views
18K
  • · Replies 9 ·
Replies
9
Views
15K
  • · Replies 5 ·
Replies
5
Views
4K