What Are the Functional Differences Between AC22A and AC23A Isolator Operations?

  • Thread starter Thread starter nisham
  • Start date Start date
Click For Summary
SUMMARY

The discussion clarifies the functional differences between AC22A and AC23A isolator operations, emphasizing that AC23A is designed for switching highly inductive loads, while AC22A is suitable for mixed resistive and inductive loads. Key distinctions include differences in contact size, material, and arc quenching mechanisms. The power factor for AC22 is 65%, whereas for AC23, it is 35%, indicating that AC23 can handle more severe duties at reduced current ratings. Manufacturers may assign multiple AC duty ratings to devices, affecting their current ratings based on the application.

PREREQUISITES
  • Understanding of electrical isolator operations and ratings
  • Familiarity with inductive and resistive load characteristics
  • Knowledge of arc quenching techniques in electrical contacts
  • Basic principles of power factor in electrical systems
NEXT STEPS
  • Research the construction and materials used in AC23A isolators
  • Explore the theoretical principles behind different AC duty ratings
  • Learn about arc welding resistance in electrical contacts
  • Investigate the impact of power factor on isolator performance
USEFUL FOR

Electrical engineers, technicians working with isolators, and professionals involved in the design and application of electrical switching devices will benefit from this discussion.

nisham
Messages
2
Reaction score
0
Dears,

Can anyone brief what is the operation functionality of AC23A operation of isolators & what is the difference between AC22A & AC23A operation.
 
Engineering news on Phys.org
It would seem it's just a difference in ratings, AC23 being robust enough for more highly inductive loads.

http://www.hevacomphelp.com/ELEC/1pdf/MCP/0001.PDF
DEFINITIONS OF UTILIZATION
CATEGORY
AC20A Connecting and disconnecting
under no load condition.
AC21A Switching of resistive loads
including moderate overloads.
AC22A Switching of mixed resistive
and inductive loads including
moderate overloads.
AC23A Switching of motor, or other



Was that the question?
There'll be differences in contact size & material, and in the arc quenching apparatus.

This link gives power factor of 65% for AC22, 35% for AC23
http://www.gil-lec.co.uk/custom/upload/pdfs/circuit%20protection/Hager_Isolators_Switches.pdf

and suggests that a given switch may be used for more severe duty at reduced current
Manufacturers may assign more than one AC duty rating to their
devices. For example an AC22 switch can be given a lower
current rating when assigned to AC23 duty. Manufacturers may
also assign a maximum kW power rating for motors or a kVAr
reactive power rating for capacitors.


If you're looking for construction details , i'd take apart a few from different manufacturers to see how they get around one another's patents.
 
Last edited:
Thank you, even i have the same information as you have told. i would like to know what makes the AC23A duty to give a different current rating than other duty. Also what is the theoretical reason behind introducing such different duties in isolators.
 
nisham said:
Thank you, even i have the same information as you have told. i would like to know what makes the AC23A duty to give a different current rating than other duty. Also what is the theoretical reahttp://www.gil-lec.co.uk/custom/upload/pdfs/circuit%20protection/Hager_Isolators_Switches.pdfson behind introducing such different duties in isolators.


again, http://www.gil-lec.co.uk/custom/upload/pdfs/circuit%20protection/Hager_Isolators_Switches.pdf
Common types of defined switching category:
• 20 Connecting & disconnecting under no load.
• 21 Switching of resistive loads.
• 22 Switching of mixed resistive & inductive loads.
• 23 Switching of highly inductive loads.

Have you ever played with inductors and noticed how the make an arc when you interrupt current?

That is rough service for a contact - it must be made from something that resists arc welding.

e = l di/dt
 
Last edited by a moderator:
Most likely this can only be answered by an "old timer". I am making measurements on an uA709 op amp (metal can). I would like to calculate the frequency rolloff curves (I can measure them). I assume the compensation is via the miller effect. To do the calculations I would need to know the gain of the transistors and the effective resistance seen at the compensation terminals, not including the values I put there. Anyone know those values?

Similar threads

  • · Replies 8 ·
Replies
8
Views
2K
Replies
4
Views
1K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 5 ·
Replies
5
Views
2K
Replies
1
Views
2K
Replies
24
Views
2K
Replies
3
Views
1K
  • · Replies 15 ·
Replies
15
Views
3K
  • · Replies 12 ·
Replies
12
Views
2K