When will an airflow cause whistling?

  • Thread starter Thread starter TSN79
  • Start date Start date
  • Tags Tags
    Airflow Cause
AI Thread Summary
Airflow can cause whistling sounds when passing through slits or gaps, influenced by air velocity, geometry, and the angle of incidence. Generally, keeping air velocities below 5000 feet per minute in dust collection systems helps minimize noise. Whistling results from oscillations in the shear layer at the orifice, with the amplitude and frequency of these oscillations determining audibility. Aeroacoustic simulations are recommended for precise analysis, as there is no straightforward approach to predict whistling. Observing the acoustic properties of similar devices can provide insights into potential whistling issues.
TSN79
Messages
422
Reaction score
0
Is there any good approach to determining if an amount of air passing through a given slit or gap will cause a whistling sound? I'm unsure with what shapes whistling might become an issue, and also at what air velocities.
 
Engineering news on Phys.org
I don't know. But generally in dust collection (which is allowed to be loud) we try to stay below 5000 fpm through ducts as above that you tend to get lots of noise. Through an open orifice, I have no idea off the top of my head. It also depends on the angle of incidence between the air path and the orifice (think of a flute or soda bottle)
 
Last edited:
There isn't a good approach of which I am aware. To really figure it out you will likely need some aeroacoustic simulations. It's going to depend on the geometry of the orifice, slit, or gap, the geometry of the vessel through which the air is flowing, and the details of that air flow. The whistling is caused by the oscillating of the shear layer that forms at the orifice. The amplitude and frequency of those oscillations as well as whether or not the surroundings are capable of resonating with that frequency are going to determine how audible any whistle is going to be. Depending on the geometry in question, there are going to be a few rules of thumb to help roughly determine the frequency, but that won't give you much information about whether it is going to be audible.
 
My suggestion would be to flip through some terminal air device catalogues, find some devices similar to what you are picturing, and see what their acoustic properties are.

Try: www.titus-hvac.com
 
It isn't restricted to commercial stuff. I've had cannulas (nasal prongs) for my oxygen equipment that whistled so loudly in my nose that I couldn't go to sleep. It seemed to be at their whim: sometimes they did and sometimes they didn't. When they did, I would bend and twist and beat them until they got down to a level that I could eventually ignore.
 
The effect is called Helmoltz resonance
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...