Which Earth Fault Relay Setting Is Correct for a 20 KV Zig-Zag Transformer?

Click For Summary
SUMMARY

The correct Earth fault relay setting for a 20 KV zig-zag transformer is determined to be 12.5 A, based on the continuous rating of the grounding transformer and the analysis of fault currents. The grounding transformer has a continuous rating of 100 KVA, leading to a calculated primary current of 8.67 A. However, due to the unique characteristics of zig-zag transformers, which operate at a lower voltage factor, the appropriate setting is adjusted to 12.5 A for optimal performance during line-to-ground faults.

PREREQUISITES
  • Understanding of zig-zag transformer operation
  • Knowledge of Earth fault relay settings
  • Familiarity with electrical power ratings and calculations
  • Experience with line-to-ground fault analysis
NEXT STEPS
  • Research the principles of zig-zag transformer efficiency
  • Study Earth fault relay settings and their impact on system protection
  • Learn about continuous rating calculations for grounding transformers
  • Explore line-to-ground fault analysis techniques in electrical systems
USEFUL FOR

Electrical engineers, power system designers, and professionals involved in transformer protection and grounding system design will benefit from this discussion.

m.s.j
Messages
212
Reaction score
1
A 20 KV switchgear have equipped with one zig-zag earthing transformer. As you know,
A grounding transformer must handle the unbalanced load on the circuit as well as the duty during line-to-ground faults. If the circuit has a lot of unbalance load, then we must concern the continuous rating of transformer in addition of its short time withstand currents. The continuous rating power of mentioned grounding transformer is 100 KVA.
The primary current setting of related Earth fault relay that installed in neutral point of E.T. is 8 Amp.
This set point current is chosen in base of E.T. continuous rating current and following calculations:

It =100/ (20x1.73) = 2.89 A

In= 3x It = 8.67 A

But the Earth fault current calculation and analyses dictate other primary current setting (12.5 A).

Which one current setting is correct? Which one do you choose?



--------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Engineering news on Phys.org
I would say 8.67 A since you are concerned with the phase to phase loading.
 
Unfortunately, nowadays with our world information transmission system (internet), we usually neglect the basic conceptions and deep thinking about new problems.
With more deep thinking, we can find that the mentioned evident equation (S = 1.73 VI) is not correct for zig-zag earthing transformers.
Indeed, each leg of a grounding transformer carries one-third of the neutral current and has line-to-neutral voltage. So in a grounded wye - delta transformer, the total power rating including all three phases is the neutral current times
The line-to-ground voltage:
S= 1.73 VI
But a zig-zag transformer is more efficient than a grounded wye - delta transformer.
In a zig-zag, each winding has less than the line-to-ground voltage,
by a factor of 1.73, so the bank may be rated lower:
S = 1.73/1.7.3 VI = VI
Therefore, the continuous rating current of E/T is 5 A and rating neutral current is 15A, and we can choose 12.5A as correct Earth fault primary current setting.


--------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 