Hi Windadct, thanks for your reply. The situation is like this. We have a normal 3 phase installation with 3 single phase Kwh meters. All are connected correctly IE line and load tails are correctly oriented at the meter connections. The meters all turn in the correct direction when normal single phase or 3 phase loads are connected. However, when a single phase 415 volt load is connected (supplied by 2 of the 3 meters) one of the meters will stop and turn in reverse until that particular load is switched off at which time, the reversing meter will resume turning in the right direction. I was wondering if the cause might be due to the power factor correcting capacitor across the 2 phases perhaps. NB this also occurs with single phase 480volt loads where power is supplied by a single phase (centre tap) transformer where the output is 2 actives and one neutral.
I hope that this makes it a little clearer.