Why is S_{RATED}=I_{RATED}V_{RATED} Insufficient for Synchronous Generators?

Join the discussion
Registration is free. Start your own thread to ask a follow-up.
2 replies · 2K views
sandy.bridge
Messages
797
Reaction score
1
Hey all,

If we are given a synchronous generator with the following nameplate values 10MVA, 13.8kV, 2 pole, 60 Hz

why is it not sufficient to go
[tex]S_{RATED}=I_{RATED}V_{RATED}[/tex]

as we did for transformers?

My reason for asking is because I am trying to determine the voltage regulation of a particular generator. However, if I determine the full load current using the above formula, I get an absurd result.
 
Last edited:
Engineering news on Phys.org
Is the generator a 3 phase machine? If so, the apparent power = √3 Voltageline ⋅ Currentline.
13.8kv is a line voltage.
 
How silly of me. Honestly, this entire time my issue was that I did not divide S by three. Thanks!